Cat5e in EMT,do I need to ground emt? - Page 2 - Electrician Talk - Professional Electrical Contractors Forum
Like Tree20Likes
Old 02-08-2017, 11:51 AM   #21
Byte's Avatar
Rewards Points: 930
Originally Posted by oliquir View Post
in the cec anything under 50vac or dc doesnt need grounding/bonding.
I think he is talking about the EMT, not the circuit. Here is from CEC:
10-304 Other conductor enclosures
(1) Metal enclosures for conductors, other than those referred to in Rule 10-300 *(services), shall be bonded to ground, except
(a) in runs of less than 7.5 m that are free from probable contact with ground, grounded metal, metal lath, or conductive thermal insulation, and that, where within reach from grounded surfaces, are guarded against contact by persons; and
(b) runs used for physical protective sleeving of less than 1.5 m in length, where the installation method is such that it is improbable that they will become energized.
So it may be required to be bonded to ground.
B-Nabs likes this.
Byte is offline   Reply With Quote
Old 02-08-2017, 05:44 PM   #22
Semper Fidelis
Suncoast Power's Avatar
Rewards Points: 4,716
I came up not pulling a ground wire in any EMT.
Now these young guys want to waste a roll of green wire every chance they get.
active1 and TGGT like this.
Old 02-08-2017, 07:22 PM   #23
Donuts > Fried Eggs
Big John's Avatar
Rewards Points: 296
Depends what it is: EMT carrying power on non-conductive structure? I'm pulling a ground. Seen too much damaged pipe to want to risk that.
Semi-Ret Electrician and Byte like this.
Old 02-08-2017, 08:28 PM   #24
RePhase277's Avatar
Rewards Points: 4,020
Many times I won't put a green wire in a pipe feeding overhead lights, because you would have to be trying to get shocked in order for fixture grounding to be necessary. I too have seen enough broken conduit fittings/joints that pulling a bonding wire to receptacles and utilization equipment has become second nature to me.
Old 02-08-2017, 08:43 PM   #25
Semper Fidelis
Steel setscrew solve lots of those problems
Old 02-08-2017, 09:18 PM   #26
RePhase277's Avatar
No doubt. Most separated conduit joints are either broken zinc cast fittings or compression fittings.
Old 02-11-2017, 11:29 AM   #27
Cl906um's Avatar
Rewards Points: 1,152
Is there any lightning protection on this structure. If so, I would bond it. If not I would look to see if it is a suspect area for strikes. You are probably putting these cameras at some of the higher points of this building..
Old 02-11-2017, 12:15 PM   #28
Byte's Avatar
Rewards Points: 930
My experience has been to bond certain isolated sections of metallic conduits to ground.
Can never have enough bonding points.
interesting question: what if there is no bonding between ground and neutral? mike883 General Electrical Discussion 35 05-29-2016 02:18 PM
Ground fault, ship dwong General Electrical Discussion 0 05-22-2016 01:44 PM
installer cut off ground on SER cable cubgirl Residential Electrical Forum 43 05-21-2016 08:12 PM
Phantom Voltage? touchtester Residential Electrical Forum 9 04-25-2016 09:20 PM
Ungrounded Delta 480 Station Service with ground reference App4DaWin General Electrical Discussion 30 04-14-2016 12:12 PM