01-28-2007, 11:52 AM
Transformers and unit substations.
02-06-2007, 04:52 PM
Hmm.. mouse may penetrate a box through upper slot?  .
02-06-2007, 06:13 PM
That's very true, but that mouse won't last very long. Neither will a snake.
02-06-2007, 06:33 PM
I don't see a problem with the bottom install.
I don't see a GEC, but that may be the angle.
We don't use flex for transformers(or much at all), usually hard pipe or gutters. But they did use ground bushings so it all looks okay to me.
What kVA are those big suckers?
Joe Momma was here
02-06-2007, 06:35 PM
Oh, your talking about how they used the rigid coupling aren't you?
Joe Momma was here
02-06-2007, 06:49 PM
Looks like a GEC (at least it looks green) Exiting conduit at the bottom of the panel. I cant see where it goes after the bonding bushing at the transformer, though.
John from Baltimore
"One day at a Time"
02-06-2007, 07:07 PM
That would be commonly known as an EGC, because it's the conductor grounding the equipment.
Joe Momma was here
02-06-2007, 07:19 PM
Got my abreviations confused on that one!
John from Baltimore
"One day at a Time"
02-06-2007, 08:35 PM
DJFVT
It looks like it might get a little hot in the there!
NEC 450.9
02-07-2007, 05:04 PM
No, I was talking about the apparent lack of working space (width) in front of the panel.
02-07-2007, 07:39 PM
Kind of hard to tell from the angle the picture was taken. It might be 30", but it does look less.
John from Baltimore
"One day at a Time"
04-15-2007, 11:27 AM
what about only one wire on X0 should be a ground bond there.
04-15-2007, 12:20 PM
NEC 450.9
Would a room this small need an exhaust fan above the transformer?
04-15-2007, 06:37 PM
Joe;
While it is not code, here if one were to use conduit or a gutter, everyone and his brother would have a fit and the inspector would most likely turn it down. Till you prove to him it was legal per the NEC.
Different areas, different practices.
04-15-2007, 10:53 PM
Originally Posted by brian john
Joe;
You'll have to explain what you're talking about Brian because I haven't the slightest clue from your post.
Joe Momma was here
04-16-2007, 02:51 AM
Joe: Sorry for the confusion:
In Washington DC, every transformer installation utilizes flex, even though this is not a requirement of the NEC. The few jobs where contractors installed EMT straight to the transformer have been ridiculed by other contractors and inspectors I have asked inspectors about this issue and they say (or believe) this is an NEC violation. Why we do this here and everyone has such strong feeling about this issue I DO NOT KNOW. In other parts of the country this practice is not followed.
04-16-2007, 08:42 PM
I've seen transformers flexed around here, but have never flexed one.
I can't remember anything in 450 saying Pipe is no permitted.
We always frown on flex around here, it does have its uses(equipment that moves, but mainly for saving time) but looks bad and says the installer is not very good with pipe.
Joe Momma was here
04-16-2007, 08:59 PM
#18
Joe:
The issue here is not the installers ability to install pipe, even on jobs where the installers are the best pipe men around Flex is still utilized. My point was I am not sure why it is so instilled in the installation practices in this area. Inspectors and installers.
04-16-2007, 10:12 PM
#19
Everywhere I've worked here in MI, We flex our transformers.
Never questioned it. I guess I thought it was required.
04-16-2007, 10:13 PM
#20
I've only ever had to change-out but a few transformers, but I appreciated the fact that the final connection was done with flex. Made the swap a lot easier.