Grounding and bonding a transformer
I have a question about grounding and bonding;
A client has a 120/208 volt service, and he purchased a 480 volt component saw. These saws have anywhere from four to sixteen motors on board, but generally the four or five saw motors are 5 to 7.5 HP, with one saw rated at 10 HP.
To resolve the problem a standard 3 phase transformer was purchased with a Y secondary, and a Delta primary. This transformer was connected backwards with the 208 supplying input to the Y configuration without a neutral. The 480 was taken off from the Delta configuration to supply the safety switch for the machine.
This was wired by the truss plants maintenance staff, however they contacted me regarding the grounding and bonding.
The advice that I gave was to bond the X0 terminal to the transformer frame, and then to carry it to a ground rod, and also to the machine.
Re-thinking this advice, I feel I was mistaken. As the 208 feed is bonded at the service, the XO should NOT have been bonded to the transformer frame.
However the derived system would require that the transformer frame, and the machine to be connected to a ground rod to provide a path for fault current should a fault present itself, so that the supply fuses would open.
The question is, what is the correct way to bond this machine so that it is safe?