Old 04-27-2009, 04:55 PM   #1
Default 30 Ton Air Handler
Ok help me out here. We wired up a 30 Ton Air handler but did not put a motor disconnect for the Supply Fan motor within site of the machine. We did this because of there really wasn't anyplace in the room where we had proper working space requirements. (Head room, 3 ft in front) This machine is surrounded by catwalks none of which I consider safe if something went wrong. We installed the disconnect in the room next door which is a mechnical room with evaporative cooling towers where we had the proper working space, head room, and lighting. The disconnect has permanent means for locking out.
The Inspector says a disconnect is required with in site of.
Rick
r_merc is offline   Reply With Quote
Old 04-27-2009, 05:35 PM   #2
BDB
What is your question? If it is: Is the Inspector right, then the answer is yes.
Proud Father of a US Army Solider
BDB is offline   Reply With Quote
Old 04-27-2009, 06:16 PM   #3
seo
Do you comply with section 430.102 exceptions? If so you will have to discuss the issue with your AHJ. He or she will have the final say.
seo is offline   Reply With Quote
Old 04-27-2009, 07:19 PM   #4
Default 430.102
I think I have follew that section. I have a call into the inspector so I will talk with him tomorrow.
Old 04-27-2009, 08:08 PM   #5
Unlimited Lic.Electrician
william1978's Avatar
Where in NC do you live or work?
Old 04-27-2009, 10:12 PM   #6
The clearances mentioned do not apply to an AHU disconnect, unless you're going to work in it while it's energized.
Old 04-28-2009, 06:57 AM   #7
Default Fuses
The disconnecting means is actually a VFD with a built in fused disconnect and bypass. The potential for working on the VFD while energized is a possibility.
Old 04-28-2009, 06:59 AM   #8
"A" inside wireman
randomkiller's Avatar
For the price of a three phase non fused disconnect, just add one, not a big deal. The VFD could stay where it is.