4 Wire bus duct used without neutral - Electrician Talk - Professional Electrical Contractors Forum
Like Tree2Likes
  • 1 Post By dawgs
  • 1 Post By ponyboy
Old 05-13-2016, 02:41 AM   #1
Default 4 Wire bus duct used without neutral
I have a customer that wants to reuse some 4-wire bus duct and install it on and existing 3 wire feeder without the neutral. None of their equipment that will feed from the bus duct requires the neutral but it just doesn't seem right to me to hook it up without the neutral. System voltage is 480/277V, 3 phase, 4 wire but all connected equipment is 480V 3 phase without the neutral.
Does installing the bus duct without the neutral violate any code?
thermoelectric is offline   Reply With Quote
Old 05-13-2016, 03:11 AM   #2
Rewards Points: 15,860
But, based on parsing your OP, the client IS installing 4 conductor bus duct.
You seem to imply either this run will be feed by a 3-conductor tap -- using THWN-2 or some such.
Alternately, you seem to imply that the client already has 3-conductor bus duct installed and heated up -- and wants to extend that run with 4-conductor bus duct.
Which is it ?
Old 05-13-2016, 09:02 AM   #3
dawgs's Avatar
Rewards Points: 1,008
If I installed it, I would put stickers at each door opening saying 3-phase 3-wire systems only.
Big John likes this.
dawgs is offline   Reply With Quote
The Following 3 Users Say Thank You to dawgs For This Useful Post:
LuckyLuke (05-16-2016), thermoelectric (05-13-2016)
Old 05-13-2016, 10:41 AM   #4
The feeder is a 3"conduit with 3-500mcm cu and a #2 insulated ground. The feeder is run from a 400 amp 3 Phase 4 wire bus plug about 200' away.
Old 05-16-2016, 12:32 PM   #5
Bump
Old 05-16-2016, 12:58 PM   #6
ponyboy's Avatar
Rewards Points: 709
I've ran more 4 wire busway on a delta feed than I can remember. There is no issue. We also buy 480/277 rated NF panelboards and feed them straight delta from our busways , again, no issue. If you're determined to be concerned about it put some signage up at the busway termination box and the gear feeding it and maybe every 10' along the length of the run if you're feeling ambitious. The only issue I see is its's wasteful but if it's recycled then who cares
DesignerMan likes this.
Old 05-16-2016, 01:15 PM   #7
Deplorable-Electrician
Rewards Points: 2,444
Seen this type install many times. Some labelled and most not.
Old 05-16-2016, 01:55 PM   #8
Rewards Points: 3,046
Missed
"The thought is in the question, the information is in the answer." -Nehemiah Hawkins
Old 05-16-2016, 02:00 PM   #9
Rewards Points: 1,542
standard here on 600v system, most of the time no neutral, 347v stuff is not very popular
Old 05-16-2016, 02:11 PM   #10
LuckyLuke's Avatar
Rewards Points: 1,172
Work on these like this a few times, we always labeled them but never an issue.
LuckyLuke is online now   Reply With Quote
Old 05-16-2016, 04:43 PM   #11
Thanks everyone for input. I'll just install it and label it 3P3W No Neutral. Thanks Again
Old 12-12-2016, 08:07 PM   #12
Rewards Points: 52
It probably violates the manufacturers instructions which violates code.
TRurak is offline   Reply With Quote
Old 12-12-2016, 09:41 PM   #13
Watt Pusher
B-Nabs's Avatar
Rewards Points: 440
Probably violated that code 6 months ago and walked away with a nice cheque for his trouble.
Old 12-13-2016, 10:03 AM   #14
Sparks fly from my finger
Jhellwig's Avatar
Rewards Points: 4,279
Not using a conductor is not a code violation.
Obey your Master.
Old 12-13-2016, 07:43 PM   #15
ponyboy's Avatar
Rewards Points: 709
Umm no
Old 12-18-2016, 09:30 AM   #16
Cl906um's Avatar
Rewards Points: 1,154
The only place a neutral is required on a wye is in the service.
Tags
bus duct, busway, neut
Conductor Electek inc General Electrical Discussion 25 05-04-2016 11:02 PM
Wire Strippers for #18 stranded 2 conductor !Tom Tools, Equipment and New Products 22 05-04-2016 08:22 PM
Neutral required to be ran to generator? lynes.nathan Canadian Electrical Code Forum 7 03-01-2016 09:10 PM
115 VAC disconnect - should I break both hot & neutral? Paul Kraemer General Electrical Discussion 11 01-22-2016 10:21 PM
8ga Aluminum Oven Wire vs 8ga Copper Wire? savatreatabvr General Electrical Discussion 17 01-13-2016 07:57 AM