Actually 9 but I forgot to change the title. Ooops
Code Hunting (The not so elusive prey)
Well it doesn't take long to find more violations where I work. This time I'm going to do something more productive with it though. Like listing the violations and codes so the correct way is known to everyone.
Lets get started!
P9290244.JPG
Ontario Electrical Safety Code [24th Edition 2009]
12-3024
Unused Openings in Boxes, Cabinets and Fittings
( 12 deficiencies - #7,9,11,12,15,16,17,18,19,20,21,22)
Unused openings in boxes, cabinets, and fittings shall be effectively closed by plugs or plates affording protection substantially equivelant to that of the wall of the box, cabinet, or fitting.
P9290239.JPG
P9290233.JPG
P9290236.JPG
12-1404
Supports
(6 deficiencies - #2,3,4,5,23)
Electrical Metalic Tubing shall be installed as a complete system and shall be securely fastened in place within 1 meter of each outlet box, junction box, cabinet, coupling, or fitting and the spacing between supports shall be in accordance with those specified in rule 12-1010
12-1010
Maximum Spacing of Conduit Supports
(1) All ridged metal conduit of one size shall be securely attached to hangers or to a solid surface with the maximum spacings of the points of support not greater than
(a) 1.5m for 16 and 21 trade size conduit;
(b) 2m for 27 and 35 trade size conduit; and
(c) 3m for 41 trade size conduit or larger.
P9290238.JPG
12-2102
Method of Installation of Wireways
(1 deficiency - #1)
(3) Dead-ends of wireways shall be closed by fittings
P9290242.JPG
12-3012
Boxes, Cabinets, and Fitting Supports
(1 deficiency - #10)
(1) boxes, cabinets, and fittings shall be fastened securely in place.
12-3002
Outlet Box Covers
(1 deficiency - #24)
Cover plates installed on flush-mounted boxes and surface-mounted outlets boxes shall be a type for which each is designed.
P9290241.JPG
2-108
Quality of Work [
For clarity this is the doors jammed together]
(1 deficiency - # 14)
The mechanical arrangement and execution of the work in connection with any electrical installation shall be acceptable.
14-408
Indication of Control Device Positions
(2 deficiencies - # 8,13)
Manually operable control devices shall indicate the "ON" and "OFF" positions, unless the application of the devices makes this requirement unnecesary.
2-300
General requirements for maintenance and operation
(2 deficiencies - #8,13)
[
Safety mechanism to keep door closed while energized damaged]
(1) All operating electrical equipment shall be kept in safe and proper working condition.
So there you have it. 26 deficiencies right there. I imagine you hard working intelligent electricians with no jobs now are seriously mad the idiots who get paid to do this.
Sad how un-fair things are. One day I hope this insanity turns around.