Rewards Points: 12,474
I would not wire nor have a pool that did not have all of the electrical consumption equipment protected by GFCI's. (Bonding grid needs to be there too, )
MechanicalDVR and lighterup like this.
Giving up on unbiased truth.
The Following 2 Users Say Thank You to hardworkingstiff For This Useful Post:
donaldelectrician (06-07-2016), MechanicalDVR (06-04-2016)
Old 06-05-2016, 06:33 PM   #22
Fish On!
lighterup's Avatar
Rewards Points: 965
Originally Posted by InPhase277 View Post
He said in the OP that the grid connected to the heater and pump motor, as it should be.
The way we install the bonding grid ( for equipotential plane) bonds everything
about the pool together and back to the "grounding bar" , not the neutral bus ,
at the sub panel we would install in the pool house.
I'm not debating that the pool pumps are part of this , I'm questioning how it
is seperated from the neutral bar when the sub panel is not only fed with the
wrong feeder , but has no fourth (non current carrying conductor) for grounding / bonding. Savy?
Old 06-05-2016, 07:22 PM   #23
RePhase277's Avatar
Rewards Points: 3,164
It isn't electrically separated because the pumps presumably have an EGC that goes back to the neutral-bonded subpanel. But the equipotential grid doesn't work because it is grounded. It works because it equalize voltage gradients across its area. So yes, the grid is electrically connected to the neutral through the pump EGC, but it isn't required to be. And I think it may introduce more hazard running it to the bar rather than the pump itself. Putting it on the pump keeps it as close as possible to the most likely point of energization.
MTW likes this.
The Following User Says Thank You to RePhase277 For This Useful Post:
lighterup (06-05-2016)
Old 06-05-2016, 10:15 PM   #24
MTW
Megistered Rember
MTW's Avatar
Rewards Points: 6,287
Originally Posted by Dennis Alwon View Post
Then why not gfci every circuit in a home? I understand being ahead of the code but I assume there is a reason the heater doesn't have to be gfci protected. That may change as the pool pump didn't require gfci either when it was direct wired.
I don't know the NEC reasoning. What I do know is there have been many high profile pool electrocutions and shocks and that's reason enough to go overboard with GFCI protection.
Old 06-05-2016, 10:30 PM   #25
Rewards Points: 3,346
GFI protection will not protect when stray currents occur off property and are returning to the origin along a path that takes them in, under, thru the pool area. I don't know stats on how many deaths you can attribute to that, but from reading Mike Holts posts it has to be at least a ''few''.
I still think that requiring a two part armature which has a carbon / fiber rod instead of a metal one between it and the impeller would help reduce a whole lot of injury and death from electric shocks in pools.
Vintage Sounds and AcidTrip like this.
Old 06-06-2016, 12:25 AM   #26
A Little Short's Avatar
Rewards Points: 124
The equipotential bond & grid do not need to go back to the panel. The EGC and equipotential bonding are two different things.
As was mentioned, it will tie into the system grounding through the EGC from the pump motor.
Old 06-06-2016, 07:08 AM   #27
motherplucker
chicken steve's Avatar
Rewards Points: 5,208
The theory is local ground contact enhances gfi capabilities , thus the last code cycle's focus on the EQ plane around a pool.
This is usually made back to the motor terminal or wet niche in #8 solid , assuming them the chief culprit as well as proximal.
Yet as others have stated, possibilities exist where pool accessories , pool heaters ,or other electrical hazards could be every bit as lethal , including what may be a parallel neutral path
That said, a '17 change is rumored to allow a EQ pool plane to serve as a GEC
Yes that is correct, i sad GEC
Stick that in yer theory pipe & smoke it! ~CS~
chicken steve is online now   Reply With Quote
Old 06-07-2016, 10:59 PM   #28
Rewards Points: 1,539
Agreed Macmikeman .... It seems the most effective and simple ways to prevent
a number of electrical problems with pools are not implemented ...
WHY ?
Don
donaldelectrician is offline   Reply With Quote
Old 06-08-2016, 07:28 AM   #29
They go Nuts on Pool Electrocution ...
I think Macmikeman should Patent his Idea... or someone else will...
GFCI will fail over time , non conductive shaft will not ...
Do you hear me Mike ? Great fail safe idea .
Think retirement with a check ... But move on it quick .
A Public forum don't ya know ...
Don
Old 06-08-2016, 11:15 AM   #30
Rewards Points: 124
Proper equipotential bonding will help as much as anything.
Old 06-08-2016, 02:45 PM   #31
Rewards Points: 1,580
I found that the original Electrician installed ground rods at the pool house as a source of ground Two local electrical inspectors say it's wrong and that it should have been 4 wire cable.
What's your opinion?
Greg
Old 06-08-2016, 02:47 PM   #32
Fish On!
lighterup's Avatar
Rewards Points: 965
If you read my previous posts , I've been saying that the feeder is all
wrong. Didn't they notice that SEU was used?
Pool electrocution cabletie General Electrical Discussion 46 06-04-2016 01:26 PM
Pool bonding grid Nolasaints NEC Code Forum 1 05-20-2016 04:58 PM
Pool Receptacle mjjg92 General Electrical Discussion 4 05-16-2016 10:31 PM
Pool Electrocutions donaldelectrician General Electrical Discussion 60 04-10-2016 10:24 AM
Homeowner being a pain the @#$ sub panel/in ground pool DannyC327 General Electrical Discussion 25 04-02-2016 10:57 PM