Is a Disconnect required ahead of the VFD? - Electrician Talk - Professional Electrical Contractors Forum
Like Tree9Likes
  • 3 Post By Wirenuting
  • 1 Post By Wirenuting
  • 1 Post By ponyboy
  • 2 Post By backstay
  • 1 Post By MechanicalDVR
  • 1 Post By frenchelectrican
Old 06-08-2016, 09:39 PM   #1
Default Is a Disconnect required ahead of the VFD?
I have seen several 480v Air Handlers in a commercial ceiling that a VFD but no Disconnect ahead of the VFD. The VFD has an on/off switch but it was explained to me that a disconnect switch is not required because the On/off switch in the VFD kills the power to the whole unit and VFD itself. They are fed by a dedicated 480v circuit.
Is this correct or do I need a disconnect switch?
Hdinj is offline   Reply With Quote
Old 06-08-2016, 09:42 PM   #2
Deplorable-Electrician
Rewards Points: 28,002
In years of HVAC control work in NJ I have never seen an air handler without a disconnect with in site.
Old 06-08-2016, 09:48 PM   #3
I agree that is why I thought it was strange when I was told the VFD is the disconnect. Is case that the on/off switch in the VFD would be acceptable as the disconnect?
Old 06-08-2016, 10:01 PM   #4
ponyboy's Avatar
Rewards Points: 707
Have you seen 430.102(b)
Old 06-08-2016, 10:02 PM   #5
I doubt it, or you would see it often. That could save some serious dollars on s many multi unit projects.
Old 06-08-2016, 10:33 PM   #6
Any opinion on the following code?
430.128 Disconnecting Means.
The disconnecting means shall be permitted to be in the incoming line to the conversion equipment and shall have a rating not less than 115 percent of the rated input current of the conversion unit.
Old 06-09-2016, 07:27 AM   #7
Coffee drinking member
Wirenuting's Avatar
Rewards Points: 2,540
A control "switch" is not considered a "means of disconnect".
While your working on that fan, can I open the door to that freq drive and using a screwdriver, push the bypass contactor in?
Remember, there are bigger idiots out there then just me.
MechanicalDVR, TGGT and Majewski like this.
Old 06-09-2016, 07:32 AM   #8
ponyboy's Avatar
Rewards Points: 707
I'm imagining something like this and I'm thinking no other disconnect required
Old 06-09-2016, 07:40 AM   #9
Can that actually be locked out? Most airhandlers have more than just a blower motor load nowadays.
Old 06-09-2016, 07:46 AM   #10
Wirenuting's Avatar
I haven't seen that brand yet. But they all have a handle that can be locked.
Now the trick is to get the cover off to work on the drive. LoL
All the air handlers here have a drive for each motor. Supply side and return air side. Exhausts are separate. It's easier to automate the buildings temperature control.
Old 06-09-2016, 07:57 AM   #11
ponyboy's Avatar
Rewards Points: 707
What I'm used to with rtus is a the drives all being inside the unit and an integrated disconnect on the outside of the unit that shuts everything down. I've installed lots of drives like the one I posted for chiller packages that have multiple water exchangers
Old 06-09-2016, 08:19 AM   #12
NRA Member
backstay's Avatar
Rewards Points: 1,396
The Code only says disconnect, but the ones I've seen, there is a piece that pulls out of the handle to install a lock in the off position.
MechanicalDVR and Wirenuting like this.
backstay is online now   Reply With Quote
Old 08-02-2016, 03:01 PM   #13
Rewards Points: 1,520
the one in the picture is a real disconnect (cuts power to the vfd) and not an on/off control switch
oliquir is online now   Reply With Quote
Old 09-07-2016, 09:42 AM   #14
Rewards Points: 1,248
I know I may bring up a old topic but again let me remind you guys if you going to put a disconnect switch between the VFD and the motor .,,
You going need a aux switch concats to send a signal to the main VFD to keep from enerigzed the load side.,,
and check the VFD manufacter instruction about useing aux concats to islolated the connection.
Old 09-07-2016, 09:50 AM   #15
I'd think that an RTU or similar piece of equipment that contains 1, 2, 3, or more VFDs would have a common disconnect for the whole unit and not have any need for a disco just for a single VFD inside. I've spent serious time inside huge air handlers that have control vestibules and can't recall any with individual discos for a single VFD.
frenchelectrican likes this.
Old 09-07-2016, 10:08 AM   #16
Ya it is simuiair to my area too in my country.,, and it super rare to see individual disconnections devices like that .,,
Spa Disconnect and fuse question DuskIndustries General Electrical Discussion 9 06-18-2016 08:28 AM
Solar disconnect cc2kj General Electrical Discussion 10 03-20-2016 10:19 PM
Disconnect Switch Noob Question! martindag General Electrical Discussion 8 03-07-2016 06:35 PM
Neutral required to be ran to generator? lynes.nathan Canadian Electrical Code Forum 7 03-01-2016 09:10 PM
115 VAC disconnect - should I break both hot & neutral? Paul Kraemer General Electrical Discussion 11 01-22-2016 10:21 PM