Today's SPOT THE VIOLATIONS! - Electrician Talk - Professional Electrical Contractors Forum
Like Tree12Likes
Old 05-06-2016, 04:31 PM   #1
I own stock in FotoMat!
Rewards Points: 6,520
Default Today's SPOT THE VIOLATIONS!
We haven't done this is quite a while, so let's bring it back: SPOT THE VIOLATION!
3 shots of a panel I got into today:
Full-size images can be found here:
https://www.dropbox.com/s/sheg440wor...0full.zip?dl=0
Other than fugugly and dirty, what violations do you see?
Old 05-06-2016, 04:34 PM   #2
Rewards Points: 8,162
It's half a bubble off. Should have levelled it. Other than that it looks okay.
Oh, and somebody lost the cover. Minor.
emtnut likes this.
Old 05-06-2016, 04:35 PM   #3
Rewards Points: 340
No straps to be seen, that looks like a water line festooned around it, white wires on breakers, I am sure there is more I am missing
Sent from my SM-G900R4 using Tapatalk
Anathera is online now   Reply With Quote
Old 05-06-2016, 04:37 PM   #4
Originally Posted by Anathera View Post
.....white wires on breakers,..........
Those are actually exceedingly pale blue conductors. I had to look at them closely myself.
Old 05-06-2016, 04:59 PM   #5
Band Member
emtnut's Avatar
Rewards Points: 7,436
I guess the incoming neutral was just a tad short
Is that a frayed ground wire at the service conductor conduit ?
360max and telsa like this.
I swear to Drunk ... I'm NOT God
Dennis Alwon (05-06-2016)
Old 05-06-2016, 05:03 PM   #6
Rewards Points: 414
I like the way they used a #10 Black wire- I think- to splice on to it.
Old 05-06-2016, 05:04 PM   #7
Rewards Points: 13,684
Originally Posted by emtnut;2777785[B
]I guess the incoming neutral was just a tad shor[/B]t
AGREED.
VERY odd.
Old 05-06-2016, 05:05 PM   #8
The GEC figures to be seriously over amped.
I'm shocked.
And figure they'd be shocked -- too.
Old 05-06-2016, 05:07 PM   #9
Band Member
emtnut's Avatar
I think that's a gas line !
Old 05-06-2016, 05:21 PM   #10
It's actually 12.
Old 05-06-2016, 05:22 PM   #11
Poly water line for the ice maker. Saddle valve on CPVC.
Old 05-06-2016, 05:37 PM   #12
Band Member
emtnut's Avatar
Is 'every' circuit a MWBC ?
Old 05-06-2016, 05:50 PM   #13
Rewards Points: 2,189
All of the above, plus contamination on the bottom. Is/was the missing cover labeled? Unused openings sealed?
Old 05-06-2016, 05:55 PM   #14
I have to take the cover off to see the innards. So there's no 'missing' cover.
Old 05-06-2016, 06:24 PM   #15
Yeah, I kinda figured that, but considering the severe lack of "workman like manner" I just figured nothing was labeled, and all the cover K.O.'s were......uh, K.O.ed.
Old 05-06-2016, 07:06 PM   #16
Rewards Points: 836
If it is a service, shouldn't the conduit with the service conductors have a bond bushing and jumper?
emtnut likes this.
Old 05-06-2016, 07:52 PM   #17
That's one more!
Actually, there's no missing KOs in the cover. And surprisingly, all 4 factory screws are present!
Old 05-06-2016, 08:05 PM   #18
That's the problem. You took the cover off. I hope you learned your lesson .
joebanana likes this.
Old 05-06-2016, 08:14 PM   #19
If I didn't take the cover off, I won't be able to retask the dryer circuit and add a bath circuit.
Old 05-06-2016, 08:26 PM   #20
Just grinding your gears, 480 .
Can you spot the lineman? Borgi Linework 14 07-12-2016 02:36 AM
Not much electrical work on today's job. Kaffeene General Electrical Discussion 1 02-04-2016 08:45 PM