Old 01-13-2007, 05:50 PM   #1
Moderator
 
Join Date: Jan 2007
Location: Beautiful Cumberland Valley, in PA
Posts: 6,889
Default Working space violation, etc.

I hate to see new work with code violations. It gripes me even more to have other trades cause my compliant work to be in violation. Below is a picture of a service I built, only to have the HVAC man come in later years and put units right smack in the working space of the metering equipment. You can also barely make out the exposed bright orange #10 NM cable going to the handyman added AC disco on the right.

MDShunk is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectrcianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 01-13-2007, 07:38 PM   #2
Moderator
 
Join Date: Jan 2007
Location: NY State
Posts: 3,350
Default

That whole thing is just criminal.
Speedy Petey is offline   Reply With Quote
Old 01-17-2007, 10:40 AM   #3
Member
 
Join Date: Jan 2007
Location: central Missouri
Posts: 98
Default

At times I have considered having HVAC guys drawn and quartered, but people tell me that is a little harsh.
3phase is offline   Reply With Quote
Old 01-22-2007, 12:52 AM   #4
K&R
Senior Member
 
K&R's Avatar
 
Join Date: Jan 2007
Posts: 132
Default

Would it be wrong to report him for the violations? I been contemplating this question alot myself. I was brought up never to be a "rat" but as I am getting older the term dosent mean as much.
K&R is offline   Reply With Quote
Old 01-22-2007, 12:58 AM   #5
Moderator
 
Join Date: Jan 2007
Location: Beautiful Cumberland Valley, in PA
Posts: 6,889
Default

Quote:
Originally Posted by K&R View Post
Would it be wrong to report him for the violations? I been contemplating this question alot myself. I was brought up never to be a "rat" but as I am getting older the term dosent mean as much.
I don't know. I struggle with the same question. Legally, no it wouldn't be wrong. Morally... that's another issuse. Pride plays into it a lot, I guess. As long as there's plenty of work for me, I'm not going to put up a fuss. Word gets out. If I ever have to scrap for work at some point in the future, I might be one mean dude in that regard. If I was out of work, I would not be beyond following people who just bought rolls of romex at home depot to see what they're doing with it. At the moment, I'm plenty busy, so I'll leave enforcement to somebody else. There have been two instances in the past in which the work being done or recently completed was so blatently and immediately hazardous that I fell compelled to turn it in. I guess we all have a line someplace in our head that shouldn't be crossed.

By the way, nice to have you here Ken.
MDShunk is offline   Reply With Quote
Old 01-22-2007, 01:35 AM   #6
K&R
Senior Member
 
K&R's Avatar
 
Join Date: Jan 2007
Posts: 132
Default

Thank's MD Im glad to be on here. I have read dozens of your posts and I asked you dozens of questions and have to say that in my time online or in the field you are one of the most knowledgeable electricians I have had the pleasure of talking to.

I guess where I am located at has alot to do with my question. I have seen some of the worst work done since relocating here 6 years ago then in my entire life. I would bet I could come up with 8-10 pics of code violations on every service call I go on or send my guys on. Some serious and some not so serious. I have seen unlicensed home improvment people do whole kitchens with 14-2 and not a single GFCI. I have watched licensed GC's (most respected GC's in the area)make flying splices in crawl spaces next to the shower drains to add a switch. I know of 1 licensed electrician that installs 1 feeder to a rooms center light (octagon box) and then does what I call (spider webs) out of that to power every thing in the entire room. We only have 1 inspector to cover the entire 622 sq. miles of our county. I have a problem turning them in. I guess as you say it's a moral issue. At the same time sooner or later someone will burn and die in one of these areas.
K&R is offline   Reply With Quote
Old 01-22-2007, 02:58 PM   #7
Member
 
lbwireman's Avatar
 
Join Date: Jan 2007
Location: Long Beach, CA
Posts: 36
Default

Marc, is that Seal Tite I see exiting the bottom of those 2 meter bases?
lbwireman is offline   Reply With Quote
Old 01-22-2007, 03:00 PM   #8
Member
 
lbwireman's Avatar
 
Join Date: Jan 2007
Location: Long Beach, CA
Posts: 36
Default

A little. Traditionally, they hung 'em 'bout halfway dead first. Then drew 'em an' quartered 'em.
Se
lbwireman is offline   Reply With Quote
Old 01-22-2007, 05:00 PM   #9
Senior Member
 
JohnJ0906's Avatar
 
Join Date: Jan 2007
Location: Baltimore, MD, USA
Posts: 3,490
Default

Whats trully annoying is that it wasn't nessasary at all to block the meters! Place that unit "in front of" the other, both facing to the right for access, and its golden.
JohnJ0906 is offline   Reply With Quote
Old 01-22-2007, 05:25 PM   #10
Moderator
 
Join Date: Jan 2007
Location: Beautiful Cumberland Valley, in PA
Posts: 6,889
Default

Quote:
Originally Posted by lbwireman View Post
Marc, is that Seal Tite I see exiting the bottom of those 2 meter bases?
What you're looking at there is 4/0 aluminium SE cable. It is traditional to do services in my area is SE cable, and PVC or RMC is an upsell. SE cable exposed is not considered "exposed to physical damage" by the inspection agency unless it's located right along a sidewalk, alleyway, parking lot, or similar.

Last edited by MDShunk; 01-22-2007 at 11:54 PM. Reason: type-o
MDShunk is offline   Reply With Quote
Old 02-03-2007, 07:29 AM   #11
Senior Member
 
Pierre Belarge's Avatar
 
Join Date: Feb 2007
Location: Westchester County, NY
Posts: 194
Default Yes, lets someone know

Construction has grown in a furious pace in the last 2 decades or so. With that, there are many new installers/companies. There are also too many of them who are not aware of, or do not care of the requirements. As a contractor, you may be torn between "snitching" or keeping a contact with the customer. The way around this is to contact your inspector and let him/her deal with this.

As an inspector, what I have started doing in the last 6 months to combat this very issue is during the rough inspection, I contact the builder. I explain to him what the parameters of the location issues are and let him duke it out with the electrician and the HVAC guy. So far that seems to work pretty well.
Pierre Belarge is offline   Reply With Quote
Old 02-03-2007, 12:42 PM   #12
NEC Educator & Consultant
 
TheElectricalGuru's Avatar
 
Join Date: Jan 2007
Location: Harrisonburg,Va
Posts: 66
Send a message via AIM to TheElectricalGuru
Default

No Comment............

PS. Not directed at you Marc...I was gonna tease ya about supports on the SE Cable and SOMEONE took upon themselves to remove my post..SO I dont generally chat on overly controlled boards so....Enjoy and Best of LUCK !
__________________
Paul W. Abernathy,CME,RMS,CMI
Master Electrician/Electrical Educator/NEC Consultant
ICC & IAEI Certified Electrical Inspector/Plans Examiner
www.TheElectricalGuru.com

Last edited by TheElectricalGuru; 02-03-2007 at 01:16 PM. Reason: ......You can remove my account Nathan !
TheElectricalGuru is offline   Reply With Quote
Old 02-03-2007, 01:23 PM   #13
Moderator
 
Join Date: Jan 2007
Location: Beautiful Cumberland Valley, in PA
Posts: 6,889
Default

Quote:
Originally Posted by TheElectricalGuru View Post
..I was gonna tease ya about supports on the SE Cable
Those straps are "upside down", in my opinion also. I always put the screw below the cable or conduit, as I feel it makes for a more secure and longer lived install. I didn't install those straps personally. I was in the basement when they were being bolted on. It wasn't worth ordering it to be re-done differently, in my opinion. Doing odds and ends, like installing anchors and straps is a good thing for a helper to do. My oldest son, on that particular summer day. For SE cable risers, I've had guys alternate each strap to every-other side of the cable on the way up. I understand why this is done sometimes, but it looks "busy" to me, and I don't do it myself. I really don't hold it against a guy who does.
MDShunk is offline   Reply With Quote
Old 02-03-2007, 03:17 PM   #14
NEC Educator & Consultant
 
TheElectricalGuru's Avatar
 
Join Date: Jan 2007
Location: Harrisonburg,Va
Posts: 66
Send a message via AIM to TheElectricalGuru
Default

lol..no my teasing was about having them supported at least 12" from the meter enclosure...lol...anyway was only teasing ya but someone obviously took it as more than that...lol....that photo has been edited since...lol...so ignore the teasing..
__________________
Paul W. Abernathy,CME,RMS,CMI
Master Electrician/Electrical Educator/NEC Consultant
ICC & IAEI Certified Electrical Inspector/Plans Examiner
www.TheElectricalGuru.com
TheElectricalGuru is offline   Reply With Quote
Old 02-03-2007, 06:35 PM   #15
Senior Member
 
Joe Momma's Avatar
 
Join Date: Jan 2007
Location: Salt Lake City
Posts: 617
Default

Quote:
Originally Posted by JohnJ0906 View Post
Whats trully annoying is that it wasn't nessasary at all to block the meters! Place that unit "in front of" the other, both facing to the right for access, and its golden.
The morons wouldn't have blocked the window that way either
__________________
Joe Momma was here
Joe Momma is offline   Reply With Quote
Old 02-10-2007, 10:46 PM   #16
Member
 
Join Date: Feb 2007
Location: so. cal
Posts: 31
Default

"I know of 1 licensed electrician that installs 1 feeder to a rooms center light (octagon box) and then does what I call (spider webs) out of that to power every thing in the entire room"


What's wrong with that.
sckeeth is offline   Reply With Quote
Old 02-10-2007, 11:58 PM   #17
Moderator
 
Join Date: Jan 2007
Location: Beautiful Cumberland Valley, in PA
Posts: 6,889
Default

Quote:
Originally Posted by sckeeth View Post
"I know of 1 licensed electrician that installs 1 feeder to a rooms center light (octagon box) and then does what I call (spider webs) out of that to power every thing in the entire room"


What's wrong with that.
Nothing, as long as the box fill rules are observed. That is an older style of wiring, mostly done in the 60's and 70's. Not normally practiced today, but nothing wrong with it as long as you mind your box fill rules. When rooms are wired in EMT, it's still a normal method.

Not sure how this applies to this thread, though.
MDShunk is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
List the violation Podagrower Code Violation Discussion 15 12-02-2008 06:10 PM
space heater oldschool General Electrical Discussion 5 10-31-2008 05:37 PM
110.27(B) violation JohnJ0906 Services and Service Equipment 6 07-06-2008 07:43 PM
NM-B in crawl space itsunclebill NEC Code Forum 9 03-06-2008 10:12 PM
Working space... this might be legal MDShunk NEC Code Forum 10 02-25-2007 10:25 PM