can you put more then one wire under a termination screw, if not where can I find it in the 2011 nec
reyamkram is offline   Reply With Quote
Old 04-08-2017, 05:11 PM   #2
Deplorable-Electrician
Rewards Points: 25,510
Depends, a termination screw on what?
Old 04-08-2017, 05:19 PM   #3
Click Here
Rewards Points: 1,502
110.3(B) Installation and Use. Listed or labeled equipment
shall be installed and used in accordance with any instructions
included in the listing or labeling.
Old 04-08-2017, 05:48 PM   #4
Rewards Points: 596
The last part of 110.14(A)....."Terminals for more than one conductor and terminals used to connect aluminum shall be so identified".
telsa (04-10-2017)
Old 04-08-2017, 05:52 PM   #5
Click Here
I never saw that, thanks.
micromind likes this.
Old 04-08-2017, 08:13 PM   #6
Rewards Points: 13,742
Half the time... think Stak-ons.
You need to get MUCH more specific.
MechanicalDVR (04-08-2017)
Old 04-08-2017, 10:11 PM   #7
Professional Nit Picker
manchestersparky's Avatar
Rewards Points: 1,624
2011 , 2014, & 2017 NEC -> 408.41
Grounded Conductor Terminations. Each grounded conductor shall terminate within the panelboard in an individual terminal that is not also used for another conductor
Anything Worth Doing ....
Is Worth Doing Right
Old 04-10-2017, 01:10 PM   #8
Rewards Points: 2,424
Well, that's for GROUNDED conductors, and even then, you left out the exception that followed:
Exception: Grounded conductors of circuits with parallel
conductors shall be permitted to terminate in a single terminal
if the terminal is identified for connection of more
than one conductor.
Which rolls us back to 110.14.
Bottom line, "saddle clamp" type connectors are often listed for two conductors, because you will see that the clamp has spaces on either side of the screw.
Simple screws and single hole type terminals are almost NEVER rated for more than one wire.
glen1971 likes this.
Old 04-10-2017, 01:52 PM   #9
Click Here
...except in every panel known to man. They almost always allow 2 EGC's in the neutral/ground bars which have that simple screw and single hole type terminal.
Old 04-10-2017, 03:05 PM   #10
Rewards Points: 262
Yep. If it's service equipment, neutrals and grounds go in the same hole when I do it. I think Eaton BR noodle bar holes are rated for 3 or 4 conductors.
matt1124 is online now   Reply With Quote
Old 04-10-2017, 03:07 PM   #11
Click Here
You can't put neutrals into a hole with another conductor, only grounds. As for how many grounds, I thought it was limited to 2, but I am not sure.
Old 04-10-2017, 03:22 PM   #12
Rewards Points: 630
For terminals like what are in junction boxes or control panels you need to look at the datasheet for the specific terminal #.
Some Allen-Bradley's can have 3 or more under one terminal as long as it is the correct size wire.
If the project specification has a clause that says only one wire per terminal then you're probably bound by that unless you can get an exception.
Old 04-10-2017, 04:25 PM   #13
It's common for large mechanical lugs to accept doubled conductors.
When this is possible it is stamped right on the lug.
Old 04-10-2017, 09:42 PM   #14
OK we have given you numerous situations - Now YOU need to tell us what the situation is that you are asking about .
Old 04-10-2017, 09:53 PM   #15
An AHJ will bounce you if it is not CLEARLY stamped into the lug. I have challenged, and won, upon showing a factory data sheet, but it cost me 3 days and another inspection fee... so really, I lost. So note to self; DON'T do that again if the lug is not STAMPED on it that it accepts more than one wire.
Old 04-10-2017, 10:14 PM   #16
I hate when that happens.
Old 04-10-2017, 10:19 PM   #17
still in business
sbrn33's Avatar
Rewards Points: 2,790
Ooop's
Old 04-10-2017, 10:29 PM   #18
Ooop's
He's been cramming plenty where a (solo) #6 is supposed to go.
16 AWG wire ampacity at higher temperatures Paul Kraemer General Electrical Discussion 5 10-13-2016 05:41 PM
Invisible Dog Fence Wire? John Valdes General Electrical Discussion 11 06-10-2016 10:55 PM
Branch circuit wire for a 12v dc off grid solar cabin Off Grid Alternative Energy Forum 14 05-12-2016 08:13 AM
Wire Strippers for #18 stranded 2 conductor !Tom Tools, Equipment and New Products 22 05-04-2016 08:22 PM
8ga Aluminum Oven Wire vs 8ga Copper Wire? savatreatabvr General Electrical Discussion 17 01-13-2016 07:57 AM