Old 10-24-2011, 07:01 PM   #1
Default 100A fuse holds, 125A fuse trips out?
Here's an interesting one.
Disconnect off the 600v bus feeding 125kva 347/600 transformer to lighting panel. Fill it with 125A fuse (non time delay) and it holds the transformer inrush, but then will lose phase C at 17, so next time skip 17, 30 trips it, start from the bottom and go up 17 nor 30 trip but 11 or something else will. After 4 fuses being blown from 4 different circuits we put the 100 back in and all is good.
Put a 100A fuse in B and C and fire it up no problem. Fuses are the same outside current rating. Could just be 4 bad fuses in a row.... but I hope not likely as the first two came from a different supplier then the next two.
Current is about 38 amps on each phase, balanced quite nicely, inrush from transformer is hardly anything as we load it after it's powered up.
So any ideas?
Jeff000 is offline   Reply With Quote
Old 10-24-2011, 07:10 PM   #2
are the 100a fuses time delay?
Techy is offline   Reply With Quote
Old 10-24-2011, 07:29 PM   #3
Nope, fuses are identical except for the current rating. That was my first thought too.
But even then there is no spike, unless my meter can't read it, that comes even close to the fuse rating.
Old 10-24-2011, 07:52 PM   #4
Service Call's Avatar
A digital meter sometimes can't fully read inrush current.
The Following 3 Users Say Thank You to Service Call For This Useful Post:
Big John (10-25-2011), mxslick (10-26-2011), Wireman191 (10-24-2011)
Old 10-24-2011, 07:55 PM   #5
jza
Try another set of 100a fuses, maybe the ones you're using are defective.
jza is offline   Reply With Quote
Old 10-24-2011, 08:11 PM   #6
I need 125's, not 100's.
The thing that gets me is that it isn't the same circuit that causes the phase to trip.
Makes it hard to think it could be an inrush issue.
Old 10-24-2011, 09:25 PM   #7
"Mainstreet"
Wireman191's Avatar
Loose connection somewhere?
Work like you don't need the money
Wireman191 is offline   Reply With Quote
Old 10-25-2011, 03:42 AM   #8
How can a 125 amp fuse fit in a 100 amp fuseholder?
Old 10-25-2011, 05:25 AM   #9
Could the fuses be different class or voltage ratings? This sounds like an inrush trip to me. Both 100 or 125 amp fuses are too small for this transformer. It should be fused at 150 amp minimum. Also, a transformer with no load will have a slightly higher inrush. How are 125 amp fuses fitting a 100 amp holder?
I would think that the branch circuits have nothing to do with the main fuses blowing.
(125 kva x 1000) /(600 vac x 1.73) = 120.4 x 1.25 =150.5 min circuit rating
Old 10-25-2011, 07:24 PM   #10
Where? lugs have all been torqued and marked. Why would 100a hold and 125a not?
It is a 100A fitting in a 125A holder.
Same class, same voltage rating.
Transformer may be a 100kva or smaller even, it's been many months since install, and there are a LOT of transformers.
And again, never said it was a 100 amp holder. It has always been a 125a disconnect, just didn't have any 125a fuses when we powered up.
Old 10-25-2011, 07:28 PM   #11
Heavily Armed Member
HARRY304E's Avatar
Are they the same available fault current rating?
BuzzKill (10-25-2011)
Old 10-25-2011, 07:28 PM   #12
1,000,000th Poster
Big John's Avatar
You have any info on the fuses? It'd be interesting to see the trip curves on each. And I agree, without a fast capture on your multimeter, you're probably not getting the right inrush value.
-John
Before posting, ask yourself "How hard would I get punched if I said this in person?"
Big John is online now   Reply With Quote
Old 10-25-2011, 07:36 PM   #13
hmm, I'd think so, but never actually checked. I'll get the info off the fuses tomorrow.
I will check this in the AM
-John
On Friday we are trying a different brand fuse, I'll get the office to bring out a meter capable of recording the proper value. And I'll get the values off the new fuses.
Old 10-25-2011, 08:01 PM   #14
So any ideas?
Is it possible that the 125s had something happen to them in your storehouse?
joethemechanic is offline   Reply With Quote
Old 10-25-2011, 08:11 PM   #15
Transformer inrush, the current that flows to initially set up the magnetic fields, is only going to last a cycle or so*, way WAY too fast for the average DMM to capture.
The magnetude of the inrush current is also dependent upon the phase angle of the incoming sine wave at the exact moment of connection and any residual flux in the transformer. Depending on that, the spike can be anywhere from 10 to 50 times the FLC rating of the transformer. So that alone often results in the "sometimes it blows the fuse, sometimes it doesn't" scenario. That's exxactly why they make Time Delay fuses.
What you are experiencing is not that uncommon, WHEN YOU USE NON-TIME DELAY FUSES.
* (depending on the size, the larger the transformer the longer the inrush lasts.)
Old 10-25-2011, 08:15 PM   #16
We don't store anything, it comes from the wholesaler and then for things like pipe and fittings we put it out of the way on site, fuses would go into the office or right into the enclosure.
My suggestion of just ordering time delay was turned down. I'm not sure why.
Old 10-25-2011, 08:21 PM   #17
jmsmith's Avatar
I remember with motors having to use time-lag type fuses along with the percentage increase to hold for inrush. In the cases where a hand would use a non-delay type, we would invariably wind up on replacement calls as soon as someone would hit a start button. Just throwing that out there...
jmsmith is offline   Reply With Quote
Old 10-25-2011, 08:24 PM   #18
... My suggestion of just ordering time delay was turned down. I'm not sure why.
Well, you made the correct suggestion, but as to the "why?"
I'll guess because you can't fix stupid?
I've had people tell me they don't want time delay fuses because they are afraid the "delay" will kill someone or start a fire! I'm serious.
Sometimes it's just a matter of education to dispel some myth they heard from some idiot brother-in-law once a long time ago. People get weird ideas in their heads when they don't really understand something, and sometimes they will stick to the stupid choice just because they don't want to admit it or show that their previous notion was hair-brained.
So keep replacing the 125A NON fuses and charge them for every call (assuming you are a contractor). Sooner or later a bean counter will question the expense and the idiot behind that decision will have to justify it.
Old 10-25-2011, 11:46 PM   #19
Only lighting, no motors on the disconnect.
This is a brand new 300 million dollar building, partially occupied as things are still being worked on.
This is with the company I work for and not my company. I am sure it is on our tab and not the owners at this point.
Old 10-26-2011, 12:19 AM   #20
jmsmith's Avatar
Sorry about that... However, the same principal applies here. A transformer is an inductive load, also, and firing one up can be just as hard on a fuse as
To fuse or not dronai PLCs, VFDs, Motors and Controls 6 10-17-2011 11:57 PM
Fuse Melted In Two doubleoh7 General Electrical Discussion 18 03-31-2011 11:49 AM
replacing fuse box heyhi11 General Electrical Discussion 18 03-03-2011 10:01 AM
Old GE fuse box fuse carrier tonygra1 General Electrical Discussion 6 07-19-2009 11:27 AM
Fuse for LV Lights dJones83 General Electrical Discussion 15 04-25-2009 09:30 AM