Old 05-10-2009, 08:38 PM   #1
B4T
ET Road Warrior
B4T's Avatar
Default 12 volt lighting transformers
I am looking for outside and inside 12v. lighting transformers of at least 1000 watts. Anyone know of a good place to shop?? Thanks
Old 05-10-2009, 08:41 PM   #2
For some of the more stout 12V systems, I've just used the secondary of a buck-boost transformer. Seems I can get them quicker than the bigger regular LV lighting transformers. Overcurrent protection can be a little bit of a puzzle, but I've used an SSU for that.
Old 05-10-2009, 08:41 PM   #3
Soa, Heviduty, Sq D and your local supply house.
Old 05-10-2009, 11:19 PM   #4
kbsparky's Avatar
That's over 80 Amps there. You will have to install a rather large secondary conductor for such a monstrocity.
Are you planning to construct a distribution panel for the loads? Something with proper overcurrent protection?
-KB
Old 05-10-2009, 11:28 PM   #5
I know some of the more ellaborate outdoor installations will use a breaker panel, wired for 12 volts. Get on the AOLP website to see some stuff that'll knock your socks off. http://aolponline.org/
Old 05-11-2009, 02:28 AM   #6
B4T
ET Road Warrior
B4T's Avatar
I found this transformer.. it takes (4) 300 watt circuits and has voltage drop table for long runs (up to 22 volts) http://www.hadco.com/Hadco/Public/Pr...?pid=374&Id=24
Old 05-11-2009, 03:37 AM   #7
Not for nothing, but when the scope gets this intense, wouldn't a line of line voltage fixtures be more practical?
Old 05-11-2009, 08:05 PM   #8
Article 411.3
Lighting 'systems' operating at 30v or less shall be listed. 411.2 also.
Frank, Arizona,USA
It's what you learn after you know it all that counts
Benaround is offline   Reply With Quote
Old 05-11-2009, 08:53 PM   #9
I think all this "listed lighting system" jazz was a spectacular lobbying effort on the part of some manufacturers at some point in time. 12 volts is 12 volts, no matter who's transformer it comes from.
Old 05-11-2009, 11:34 PM   #10
Unless your in a court of law!
Frank, Arizona,USA
transformers rlc3854 UK Electrical Forum 7 09-27-2008 11:40 AM
Why do transformers hum? They don't know the words randomkiller Off Topic 20 08-01-2008 06:06 AM
347 volt lighting controller pasha General Electrical Discussion 3 05-22-2008 12:45 PM
208 volt transformer on 240 volt? chadmiller Services and Service Equipment 3 05-06-2008 09:40 PM
Auto transformers chop347 General Electrical Discussion 3 05-28-2007 03:10 PM