Old 03-03-2007, 09:55 PM   #1
Junior Member
 
Join Date: Mar 2007
Posts: 2
Question 14awg branch off a 12 awg

I'm trying to find a reference in NEC about running a 14awg line off a 12awg 20amp source. I was told by someone that it was okay to splice into a 12 with a 14, I know you can't have a 14awg line on a 20 amp breaker, but I'm not sure if it's okay to tap into 12awg with a 14awg branch or not. Any guidance would be appreciated.

Thanks
newbie is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectrcianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 03-03-2007, 09:57 PM   #2
Junior Member
 
Join Date: Mar 2007
Location: BC, Canada
Posts: 5
Default

Negative, your breaker needs to protect the smallest wire in the circuit. In this case the 14 AWG.
Islandrider is offline   Reply With Quote
Old 03-03-2007, 10:06 PM   #3
Junior Member
 
Join Date: Mar 2007
Posts: 2
Default

Quote:
Originally Posted by Islandrider View Post
Negative, your breaker needs to protect the smallest wire in the circuit. In this case the 14 AWG.
Dang, that's what I thought but when your given direction by someone that's been doing it for 60 years you can't argue too much. It requires another line to be run for the 15amp outlets. Is this a "shortcut" thing that some do to save time or was it allowed in the past?
newbie is offline   Reply With Quote
Old 03-03-2007, 10:44 PM   #4
Moderator
 
Join Date: Jan 2007
Location: NY State
Posts: 3,346
Default

It was never "allowed" or legal. Some used to think it fell under the tap rules, or at least they convinced themselves that.
I have seen some real doozies of justifications (excuses) for it.
Speedy Petey is offline   Reply With Quote
Old 03-04-2007, 09:50 PM   #5
Member
 
Join Date: Mar 2007
Location: Vermont/MA.
Posts: 48
Default

Back when I was an apprentice some years ago I was told that switch legs off of a 20 amp circuit could be 14 Ga, I believed it at the time . Sometimes you have to learn things for yourself.
__________________
(Do the job right boy or don't do it at all.)
wireman3736 is offline   Reply With Quote
Old 03-04-2007, 10:17 PM   #6
Senior Member
 
Joe Momma's Avatar
 
Join Date: Jan 2007
Location: Salt Lake City
Posts: 617
Default

I think I heard the original post say all this is on a 15 amp circuit?

14 gauge on a 15 amp breaker is legal.
__________________
Joe Momma was here
Joe Momma is offline   Reply With Quote
Old 03-04-2007, 10:26 PM   #7
Junior Member
 
Join Date: Mar 2007
Location: BC, Canada
Posts: 5
Default

Quote:
Originally Posted by Joe Momma View Post
14 gauge on a 15 amp breaker is legal.
Indead it is; however, in his first post he states that the circuit in question is a "14awg line off a 12awg 20amp source" which is not allowed by NEC.

Last edited by Islandrider; 03-04-2007 at 10:32 PM.
Islandrider is offline   Reply With Quote
Old 03-04-2007, 10:30 PM   #8
Senior Member
 
Joe Momma's Avatar
 
Join Date: Jan 2007
Location: Salt Lake City
Posts: 617
Default

Quote:
Originally Posted by newbie View Post
I know you can't have a 14awg line on a 20 amp breaker,.....
I assume you simply overlooked this statement in the original post
__________________
Joe Momma was here
Joe Momma is offline   Reply With Quote
Old 03-04-2007, 10:39 PM   #9
Moderator
 
Join Date: Jan 2007
Location: NY State
Posts: 3,346
Default

Joe, you are playing semantics here. You need the whole sentence:
Quote:
I was told by someone that it was okay to splice into a 12 with a 14, I know you can't have a 14awg line on a 20 amp breaker, but I'm not sure if it's okay to tap into 12awg with a 14awg branch or not.
He is saying he knows you cannot have a whole "line" of #14 on a 20 amp. What he is questioning is whether you can have a #14 "tap", or switch leg, off a 20 amp circuit.

The answer is still, and has always been, no.
Speedy Petey is offline   Reply With Quote
Old 03-05-2007, 07:32 PM   #10
Senior Member
 
Join Date: Feb 2007
Location: Eighty Four,Pa.15330
Posts: 1,656
Default

This thread might fall under N.E.C.Art.525.

Bob O.Eighty Four,Pa.15330
bobelectric is offline   Reply With Quote
Old 03-05-2007, 08:05 PM   #11
Senior Member
 
Joe Momma's Avatar
 
Join Date: Jan 2007
Location: Salt Lake City
Posts: 617
Default

I agree, you can never have permanently installed 14 gauge wire connected in any way or means to a 20 amp breaker.
__________________
Joe Momma was here
Joe Momma is offline   Reply With Quote
Old 03-05-2007, 09:07 PM   #12
Member
 
Join Date: Mar 2007
Location: Vermont/MA.
Posts: 48
Default

Quote:
Originally Posted by Joe Momma View Post
I agree, you can never have permanently installed 14 gauge wire connected in any way or means to a 20 amp breaker.
What if it's a motor load ?
__________________
(Do the job right boy or don't do it at all.)
wireman3736 is offline   Reply With Quote
Old 03-05-2007, 09:29 PM   #13
Senior Member
 
Joe Momma's Avatar
 
Join Date: Jan 2007
Location: Salt Lake City
Posts: 617
Default

amps are amps, and kcmils are kcmils.

In other words; motor loads have nothing to do with the restraints of the physical world we live in.
__________________
Joe Momma was here
Joe Momma is offline   Reply With Quote
Old 03-05-2007, 09:41 PM   #14
Member
 
Join Date: Mar 2007
Location: Vermont/MA.
Posts: 48
Default

Quote:
Originally Posted by Joe Momma View Post
amps are amps, and kcmils are kcmils.

In other words; motor loads have nothing to do with the restraints of the physical world we live in.
Do you have a code book, check out 240.4G,
__________________
(Do the job right boy or don't do it at all.)
wireman3736 is offline   Reply With Quote
Old 03-06-2007, 01:56 AM   #15
Senior Member
 
Bkessler's Avatar
 
Join Date: Feb 2007
Posts: 958
Default old joe T

The smartest electician I ever new told me never to believe him or any one. look it up yourself. No exceptions! And I say wireman is right motor overcurrent protection is different, check out the 90 c coulumn of the 310-16
__________________
When ls lunch

Last edited by Bkessler; 03-06-2007 at 01:59 AM.
Bkessler is offline   Reply With Quote
Old 03-06-2007, 08:17 PM   #16
Senior Member
 
Joe Momma's Avatar
 
Join Date: Jan 2007
Location: Salt Lake City
Posts: 617
Default

So lets see here;
You have 14 gauage wire running a motor on a 20 amp circuit?
And you gave 240.4g as a refferance,
try reading all of 240.4 especially (D)
__________________
Joe Momma was here
Joe Momma is offline   Reply With Quote
Old 03-06-2007, 08:36 PM   #17
Member
 
Join Date: Mar 2007
Location: Vermont/MA.
Posts: 48
Default

I did read all of 240.4. Reread 240.4D and the first sentance says Unless specifically permitted in 240.4(E) or 240.4(G), 240.4(G)refers to table 240.4(G) which then refers to many exceptions including motors.
__________________
(Do the job right boy or don't do it at all.)
wireman3736 is offline   Reply With Quote
Old 03-06-2007, 08:39 PM   #18
Moderator
 
Join Date: Jan 2007
Location: NY State
Posts: 3,346
Default

Joe, I don't get it. Are you being serious?
What is the first sentence in 240.4(D)?

*EDIT- Sorry 3736, I typed under you.
Speedy Petey is offline   Reply With Quote
Old 04-01-2007, 11:15 PM   #19
Junior Member
 
Join Date: Apr 2007
Posts: 10
Lightbulb Receptacle Prongs

Does Anyone Know Why Most Receptacle Prongs Have Holes In Them? I've Got My Ideas But Not General Facts From Knowledgeable Old Timers.
HOYTUSA is offline   Reply With Quote
Old 04-01-2007, 11:18 PM   #20
Junior Member
 
Join Date: Apr 2007
Posts: 10
Default Receptacle Prongs

The Question I Asked About The Prong Holes Is Actually One Of My Electricians (journeyman) Class Homework Assignment

Last edited by HOYTUSA; 04-01-2007 at 11:20 PM.
HOYTUSA is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
branch circuit design toolman001 General Electrical Discussion 7 06-30-2008 10:31 PM
gen purpose branch crkt stillirnin NEC Code Forum 6 05-29-2008 03:52 PM

Top of Page | View New Posts

All times are GMT -4. The time now is 01:18 AM.


Electrician Talk © 2006 - 2009 The Building Network LLC

Search Engine Optimization by vBSEO 3.2.0