Old 07-23-2008, 07:48 PM   #1
Absolutetruthz's Avatar
Default 40 amp disconnect
I'm installing a 208volt circuit for a Fryer at a local Theatre, The Fryer is rated 40amps and is not cord connected. I know Code requires a disconnect at the Fryer. Do they make a small 40amp rated switch which could be installed at the Fryer, or is there a better way to do this? Thanks!
Absolutetruthz is offline   Reply With Quote
Old 07-23-2008, 07:52 PM   #2
Electric fryers are almost always cord and plug connected, with a twist lock. Also, if you're installing a new receptacle for it, it must shut down when the Ansul shoots off, so plan on a contactor.
Old 08-01-2008, 10:02 PM   #3
Thanks MD. I couldnt find that in the Code anywhere, do you know the reference for the receptacle being controled via the Ansul system?
Old 08-01-2008, 10:08 PM   #4
You'll find it in the fire code, not the in the NEC.
service disconnect location? electromanj Services and Service Equipment 15 06-07-2008 05:09 PM
Dishwasher disconnect... waco General Electrical Discussion 31 04-04-2008 09:53 PM
Clearance for a service disconnect joleesparkey Services and Service Equipment 1 03-11-2008 03:21 PM
AC Disconnect Violation: MDShunk Code Violation Discussion 21 12-08-2007 11:21 PM
6 disconnect rule... oops! MDShunk Services and Service Equipment 14 10-23-2007 04:35 PM