40 degree c - Electrician Talk - Professional Electrical Contractors Forum
Old 03-08-2012, 05:26 AM   #1
cabletie's Avatar
Rewards Points: 84
Default 40 degree c
What does the 40 degree c mean on the side of most circuit breakers? I have seen it marked on breakers of all sizes from all manufactures.
Old 03-08-2012, 05:30 AM   #2
motherplucker
chicken steve's Avatar
Rewards Points: 4,414
methinks you want to go to 110.14 Cable.....~CS~
Old 03-08-2012, 05:38 AM   #3
cabletie's Avatar
Rewards Points: 84
The breakers are usually rated for 60 or 75 degree c for the lugs, but on the side they have a 40 degree c molded into it.
Old 03-08-2012, 06:08 AM   #4
Jlarson's Avatar
Rewards Points: 2,878
Ambient temperature rating.
UL 489 listed breakers are tested to hold 100% load at 40 degrees C in free air. If you are running the breaker above that temperature it needs to be derated.
Jlarson is online now   Reply With Quote
The Following 2 Users Say Thank You to Jlarson For This Useful Post:
BBQ (03-09-2012), frenchelectrican (03-09-2012)
Old 03-09-2012, 03:39 AM   #5
cabletie's Avatar
Rewards Points: 84
Thanks jlarson, providing the ul number opened up a vast search on google.
I have always seen this exception in the code that works around going 125% for stuff like continuous loads.
Exception: Where the assembly, including the overcurrent
devices protecting the branch circuit(s), is listed for operation
at 100 percent of its rating, the ampere rating of the
overcurrent device shall be permitted to be not less than
the sum of the continuous load plus the noncontinuous
load.
I wasn't sure if I had ever seen a device rated at 100 percent before. I still would not use the exception, or if that would fit it. Is a breaker in free air when installed in a panel with other breakers?
Old 03-09-2012, 05:13 AM   #6
Jlarson's Avatar
No, when they say free air it means no enclosure.
90 degree terminations NolaTigaBait NEC Code Forum 29 02-07-2012 08:43 PM
Do You Have A Degree In Economics? BBQ Off Topic (Non Trade) 4 07-21-2011 01:16 PM
30 degree offsets Conduit Phil General Electrical Discussion 22 06-01-2010 10:31 PM
Say what! SE-R under 60 degree C. columun partimer31 NEC Code Forum 16 03-21-2010 06:35 PM
How do i go about getting an Engeneering degree? crackerontherun General Electrical Discussion 7 06-19-2009 11:44 PM