Old 06-29-2008, 10:02 PM   #1
Default branch circuit design
Hi Guys I am quoting a job on a golf coarse where we have 35 electric carts.
The branch circuits will run down two walls with a total of 18 110V 15Amp
circuits on each wall, the panel will be a 400Amp three phase. The max draw per cart charger will be 9.5 Amps, and a request by the manufacturer that each cart is on a septate 15 Amp circuit.The building is 80 feet long and 40 feet wide. my question is the best way to run the EMT to provide most wire per run and not derate my wire ampacity.
Thanks
toolman001 is offline   Reply With Quote
Old 06-29-2008, 10:05 PM   #2
Seen your member
If you go with MWBCs, you can put 9 circuits (3 blacks, 3 reds, 3 blues and 3 whites) into one conduit and will hae a 20a breaker. If you've got 18 receps, that's only two pipe runs.
Old 06-30-2008, 08:20 PM   #3
Default Branch circuit design
Thank You for your help I had ad idea that would be the best way to solve the problem. If my calculations are correct using #14 THHN will still give me the required ampacity of 9.5A. This web site is a great resource. Thanks to all who are there to help.
Toolman001 (just an old fat boy who got use to being shocked)
Old 06-30-2008, 08:40 PM   #4
Seen your member
Um, how do you plan on protecting (read: over-current device) those 9.5a #14 conductors?
Old 06-30-2008, 09:10 PM   #5
I hope I CAN USE 15A breaker
Old 06-30-2008, 09:18 PM   #6
I'd run #12 and use 20 amp breakers just to avoid the voltage drop over that distance. The additional cost is negligible.
Old 06-30-2008, 10:03 PM   #7
I can see using # 12 wire the runs, they will not exceed 100' however the manufacture request each branch circuit be on 15 Amp breaker
Thanks Toolman001
Old 06-30-2008, 10:31 PM   #8
Seen your member
If your calculated ampacity is 9.5 amps, they must be protected with an overcurrent device not exceeding 9.5 amps.
Recalculate using 12s and see if you can then use a 15a breaker. Also, break down the conduit into two, and separate the circuits out. That will help.
If nothing else, pulling 18 circuits into one conduit will be an exercise in futility. You'll spend more time keeping them all straight than it's worth.
troubleshooting my design? Spat72 Lighting Design 5 03-29-2009 05:47 PM
gen purpose branch crkt stillirnin NEC Code Forum 6 05-29-2008 03:52 PM
bid design watersparkfalls Business, Marketing, and Sales 2 03-06-2008 11:17 AM
caravan site design stu brayson General Electrical Discussion 5 09-05-2007 11:33 AM
14awg branch off a 12 awg newbie General Electrical Discussion 19 04-01-2007 11:18 PM