Old 09-03-2007, 12:14 PM   #1
Default caravan site design
Recently been asked to design and install 23 super pitches for a caravan site. Having never undertaken a job like this has anyone got any advice. cheers
stu brayson is offline   Reply With Quote
Old 09-03-2007, 03:22 PM   #2
frank's Avatar
Stu. If you are in the UK then Caravan sites are designated 'special locations'. Check out the IEE Regs for specific advice. There you will find a section dealing with just such sites.
Old 09-04-2007, 08:21 PM   #3
thanks Frank. I have the regs but would you have the 23 hook up points on radial ccts or would you feed them individually from a distribution board?
Old 09-04-2007, 09:28 PM   #4
el abogado del diablo
depends if the site is going be full of Pikers or not....
sorry, I liked the movie Snatch...
oldman is offline   Reply With Quote
Old 09-04-2007, 09:43 PM   #5
Site is for 23 super touring pitches
Old 09-05-2007, 11:33 AM   #6
frank's Avatar
Stu
There are no specific rules in this instance. You just have to design a sub feeder that is capable of the maximum demand or a number of sub feeders (say 6 number serving 4 posts) at a maximum of 16 amps per post ie 64 amps radials. Depending on your particular circumstances you can say either 10mm or 16mm xplc/swa. Allow some diversity- 25% perhaps and there you have it. But design it to suit your specific location. You will need to install rcd controlled (or Rccb) breakers within an IP Box and have CeeForm type 16 amp switched socket outlets. Similar to MK Commando types. Upstream control would mnot be rcd protected but close current protection via mcb's rated somewhat lower than the current rating of the cable but highr than the radial maximum demand.
troubleshooting my design? Spat72 Lighting Design 5 03-29-2009 05:47 PM
Solar Powered LED Design, Help. frozenpuppy Lighting Design 4 11-10-2008 08:18 AM
15amp caravan plug to house 10 amp james General Electrical Discussion 0 09-20-2008 10:55 AM
branch circuit design toolman001 General Electrical Discussion 7 06-30-2008 10:31 PM
bid design watersparkfalls Business, Marketing, and Sales 2 03-06-2008 11:17 AM