Originally Posted by Bkessler
I will be installing a 200 amp rated main lug sub panel for a concession stand.
Why are you using a 200A panel for a 72A load? I'd use a 100A or 125A if I needed the spaces.
The loads are coffee maker, bun warmer, ice machine , water heater, ect.
Water heater is continuous load at 125%
It's hard to figure the load on "ect."
The loads are: phase A- 72 amps B-68 amps and C- 65 amps.
How did you determine this? Does it include the 125% for the W.H.? Lights?
Is there gonna be any heat? 1500 watt space heaters add up in hurry.
What would be the minimum wire size for this and what are the steps to formulate it.
Wire size is in Table 310.16.
once you know your actual load you just look it up in the proper column and derate if necessary.
I would think it's something like 125% of 72 divided by 1.73?
Huh?
I am not sure but the panel is 90 feet away from source and ran in 1.25 emt.
90 feet is not far enough to worry about VD.
thanks bk
You're welcome