Contactor Chattering - Electrician Talk - Professional Electrical Contractors Forum
Old 10-18-2011, 09:33 PM   #1
Les Voltage
Default Contactor Chattering
I have a LCP (lighting control panel) that when I turn on the line voltage to supply the LCP the contactors chatter when when they close. I dont have any of the circuits that are controlled by the contactor on and they still chatter. I did notice my supply voltage was about 118.5 on B phase and around 120.0 on A phase. but it chatters the same on either phase. I have been told that 1.5 volts below 120 could cause problems like this.
Once or twice they didnt chatter. I have made sure everything it tight and there is no trash in the box. Its six 4 pole contactors.
Any advice?
Old 10-18-2011, 09:40 PM   #2
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 390
get mechanically held contactors or invert the inputs so the lights are on when the contactors are off (then they'll chatter when no one is there) (if that's an option)
Old 10-18-2011, 09:48 PM   #3
cog
stuiec's Avatar
Rewards Points: 62
missing shading coils?
The Following 2 Users Say Thank You to stuiec For This Useful Post:
brian john (10-19-2011), ce2two (10-18-2011)
Old 10-18-2011, 10:46 PM   #4
erics37's Avatar
Rewards Points: 638
I doubt you would have problems with 118.5 volts. Did you measure the voltage when the contactor coils are actually energized?
Old 10-18-2011, 11:28 PM   #5
Electron Herder
Rewards Points: 152
Yup.
OaklandElec is offline   Reply With Quote
Old 10-18-2011, 11:36 PM   #6
I own stock in FotoMat!
Rewards Points: 6,520
It still may be a voltage issue. Your meter may say 118.5v, but the sampling rate may not be fast enough to catch a voltage drop issue. The voltage may drop down enough for the coil to release, then the voltage will come back up. This happens quite quickly, and a low-end meter won't see it.
Old 10-19-2011, 12:02 AM   #7
A Little Short's Avatar
Rewards Points: 118
Can you change the coil, or is it built in with the contactor so that it can't be changed? If you can, I would try another coil.
A Little Short is online now   Reply With Quote
Old 10-19-2011, 05:41 AM   #8
Rewards Points: 1,464
Bad photocell? (hopefully not a timer).
Old 10-28-2011, 02:08 PM   #9
Rewards Points: 25
In my experience, a couple of things can cause a situation like this:
- The wrong type of core (the part that gets magnetized). The construction of the laminations in a DC mag core is different from that of an AC mag. Although the coil itself may be correctly rated, the core could be the wrong type.
- Mechanical misalignment. This is the most common cause of contactor chatter. If the faces of the stationary and moveable cores do not come into complete contact, chatter will result. Dirt/corrosion can cause this, as can mechanical binding.
zgozvrm is offline   Reply With Quote
Old 10-28-2011, 02:26 PM   #10
Jeff85's Avatar
I doubt it is voltage. Most coils still work plus or minus ten percent on the voltage. It could just be a bad coil. I have had brand new ones go after working for a few days. All it takes is some dirt to get in there and they don't close fully.
Jeff85 is offline   Reply With Quote
Old 10-28-2011, 02:34 PM   #11
jmsmith's Avatar
A lot of the older contactors that I've seen this with had to do with the pole-shading coils that were inserted into the laminated cores itself. These would either break or wear to the point that they would simply fall out. I worked at several plants that kept these in stock for all the contactor sizes that they used. A lot cheaper than replacing the entire core!
jmsmith is offline   Reply With Quote
Old 10-28-2011, 08:59 PM   #12
Les Voltage
Well I fixed it somehow, kinda. I took the contactors out and apart to make sure there was not anything in there that didnt need to be. A guy at work told me to put a small amount of lubricant where the spring is. I didnt find any trash. It wont chatter all the time but will at times. I only know this by turning it on and off a few times during the day.
Old 10-28-2011, 09:01 PM   #13
Les Voltage
My meter would not catch that. Would this happen even if there was no load applied? It would still chatter with all the controlled circuits turned off
Old 10-28-2011, 10:29 PM   #14
Rewards Points: 1,304
This issue would be independent of load. The coil load, with the coil inrush could be sufficient for this.
Old 10-28-2011, 11:18 PM   #15
Rewards Points: 2,370
Any advice?
Do they keep chattering ?
Or do they only do it for a short period ?
Can you not change the contactor ?
I dont really think a small reduction in line voltage
would cause issues like this.
More likely the contactor is faulty or wrong type.
Old 10-28-2011, 11:20 PM   #16
Bababoee
captkirk's Avatar
Rewards Points: 2,030
wouldnt an ac coil on a dc circuit just burn out..?
Full time Bovine Scatologist.
Old 11-15-2011, 09:27 AM   #17
Rewards Points: 25
I'm not 100% sure, as I haven't come across that yet (nor have I tried it). Although I have seen it the other way around. The life of the coil may be shortened in either case, but I don't think it would burn out immediately. After all, the voltage potential is there.
Old 11-15-2011, 12:08 PM   #18
jza
Mad as Hell Member
jza's Avatar
Rewards Points: 2,302
I had a contactor do this once. Had to replace it with a contactor intended for lighting loads.
jza is offline   Reply With Quote
Old 11-15-2011, 12:48 PM   #19
Rewards Points: 2,364
99% of the time a contactor chattering is the result of either debris on the armature pole faces, or a broken shading coil. Most modern coil systems are designed to have a "knee point" threshold in the applied voltage, so above that, it works, below that, it doesn't. It is REALLY difficult to have a voltage that hovers EXACTLY at that knee point. And per NEMA design criteria, coils are supposed to have 85% drop out voltage tolerance. So a 120V coil should hold in down to 102V WITHOUT chattering. That's not to say you can't find cheap Chinese knock-off products that don't bother to use industry standards, but since you didn't post the make and model of your contactor, I have no way of knowing.
A less common issue, but mostly happening in some types of multi-pole lighting contactors, is a side-to-side mechanical imbalance on the number of poles. Most contactors are designed as 3 pole devices (or 4 pole for small IEC style), then on some lighting contactors you can add pole expansion units to each side. But they must be balanced in terms of the weight if you do that. So if you add on poles, you must add them on in pairs so that if your contactor was originally designed as a 3 pole device, you always end up with an odd number, i.e. 5, 7, 9 etc. The ones that do this then will have a "dummy pole" that you add if you don't want to pay for a full power pole. So if yours is that type, then for 6 poles you would have 2 add-on power poles on one side, one on the other side, and a dummy pole on that side so that it balances the mechanical forces on the armature. Without it, the armature pulls in crooked and chatters. If you have a multi-pole lighting contactor that was shipped from the factory as a 6 pole unit, that shouldn't be an issue though.
joethemechanic (11-15-2011)
Contactor Apprentice_617 General Electrical Discussion 7 06-17-2011 07:02 PM
Using motor contactor as a lighting contactor coolbreeze419 General Electrical Discussion 16 08-08-2010 06:27 PM
HOA and Contactor clos PLCs, VFDs, Motors and Controls 9 06-19-2009 12:33 PM
Contactor Vs. Welding Isolation Contactor alanblinkers General Electrical Discussion 11 02-06-2009 07:18 PM
Contactor help Big Smitty Lighting Design 3 09-03-2008 11:12 PM