Would you or have you direct buried THWN Cu for use as a GEC or EGC? I personally don't see a problem although technically it would be a violation of the code since it's not listed for the purpose. But what could happen? The insulation could degrade to the point of leakage of fault current in the event of a fault? Uh oh! Those bare copper direct buried EGCs are in trouble too I guess
Electron_Sam78 is offline   Reply With Quote
Old 02-01-2011, 09:55 AM   #2
Podagrower's Avatar
I would, I have, I will.
Podagrower is offline   Reply With Quote
The Following User Says Thank You to Podagrower For This Useful Post:
Charlie K (02-01-2011)
Old 02-01-2011, 09:57 AM   #3
Same here.
Old 02-01-2011, 10:01 AM   #4
Chief Electron Relocator
As an GEC, yes. ECG, no.
bruce6670 (02-01-2011), John Valdes (02-01-2011)
Old 02-01-2011, 10:11 AM   #5
Why not on the EGC?
Old 02-01-2011, 10:21 AM   #6
Originally Posted by Electron_Sam78 View Post
Why not on the EGC?
For what reason would I need to bury an EGC?
Old 02-01-2011, 10:24 AM   #7
Ax grinder
raider1's Avatar
I have installed THWN direct buried for a GEC many times in the past and would not hesitate to do it again.
I don't see anything in 250.62 that would prohibit using THWN for a GEC.
Chris
The Following User Says Thank You to raider1 For This Useful Post:
Rockyd (02-01-2011)
Old 02-01-2011, 10:30 AM   #8
A direct burial circuit to something that has metal parts that may become energized. Any feeder needs one run with it.
The Following User Says Thank You to Electron_Sam78 For This Useful Post:
sbrn33 (02-01-2011)
Old 02-01-2011, 10:37 AM   #9
child please.....
NolaTigaBait's Avatar
Yeah, but it needs to be grouped inside the conduit if its thwn...300.3b....but it does say same trench...i wonder whatthat would entail...
REMOVED
Old 02-01-2011, 10:44 AM   #10
I'm saying THHN/THWN for the EGC only. If it's a direct burial the rest of the circuit conductors would be USE insulated
Old 02-01-2011, 10:45 AM   #11
child please.....
Im not sure what you are saying.
REMOVED
Old 02-01-2011, 10:52 AM   #12
I think he us saying that you could run triplex URD or similar and add the EGC as THWN.
Old 02-01-2011, 10:53 AM   #13
sparks134's Avatar
Huhhhh???
sparks134 is offline   Reply With Quote
Old 02-01-2011, 11:00 AM   #14
child please.....
I did not know you can do that...
REMOVED
Old 02-01-2011, 11:07 AM   #15
A direct burial circuit (branch, feeder) with USE rated individual conductors or a triplex URD whatever you like -not really the point of this thread. However I propose using THHN/THWN for the EGC. Though technically not code compliant I think due to the UL listing of the insulation, what's the worst that could happen? The insulation could degrade but that's no big deal since direct buried EGCs can be bare copper anyway.
Old 02-01-2011, 11:11 AM   #16
I cannot recall any time where I needed to direct-bury an EGC. It's either part of the cable (UF) or pulled in with the circuit conductors (PVC).
I've buried separate EGCs along with triplex URD, but it's the same XLPE as the URD, not THWN.
Old 02-01-2011, 11:29 AM   #17
ok I'll check you off as a definite "have not"
Old 02-01-2011, 12:06 PM   #18
I think I've already stated that.
Old 02-01-2011, 02:23 PM   #19
I noticed once I went to check the box and it was already checked. Mom was right too much television does rot your brain~!
direct mail berkey Business, Marketing, and Sales 22 05-20-2011 04:12 AM
direct deposit paul d. Business, Marketing, and Sales 36 03-16-2011 11:30 AM
schedule 80 pvc minimum burial depth cal General Electrical Discussion 3 01-08-2010 08:41 PM
As direct as a short can get. Adam12 Code Violation Discussion 13 11-12-2008 05:11 PM
medium voltage burial DEA AGENT NEC Code Forum 7 05-23-2008 11:20 PM