Duct Bank Tying - Electrician Talk - Professional Electrical Contractors Forum
Old 06-27-2013, 10:42 PM   #1
Aegis's Avatar
Rewards Points: 1,646
Default Duct Bank Tying
Back when I was a first year I was taught never use tie wire to go completely around the duct bank and fasten the conduit to the chairs that are holding it. Instead go over the conduit (top) then through the chair and then tie back over the top again. This is so there's never a complete circle of tie wire around any duct bank.
I was told if you go all the way around it can induce voltage etc = it isn't good. I never thought about it since. I left that company and all the duct banks here they use string to tie everything down. I preferred the tie wire method but I'm just wondering how you guys do it?
Here's a pic off the net of what they said "not to do".
Aegis is offline   Reply With Quote
Old 06-27-2013, 11:09 PM   #2
Rewards Points: 2,950
With 3 phase and a neutral, is there any chance of that? Any more than passing through the knock out of a steel panelboard? You would not want to pass individual conductors through individual knock outs of course.
The Following 2 Users Say Thank You to btharmy For This Useful Post:
BBQ (06-29-2013), Big John (06-28-2013)
Old 06-27-2013, 11:10 PM   #3
xaH
Yeah, only a problem if these are isolated phases.
xaH is offline   Reply With Quote
Old 06-27-2013, 11:12 PM   #4
Rewards Points: 150
gaffer1 is offline   Reply With Quote
Old 06-27-2013, 11:13 PM   #5
xaH
Originally Posted by gaffer1 View Post
Refailure, you don't know anything about electrical work.
The Following User Says Thank You to xaH For This Useful Post:
walkerj (06-27-2013)
Old 06-28-2013, 01:13 AM   #6
Default Duct Bank
What I do is tie bottom row of chairs. Lay conduit in chairs. Set top set of tied chairs on top and snap in. Tie around top chair , around conduit, thru bottom chair. Repeat. Depending on chair lay out, I stake and tie every other support. Bundle evey other one. Pour corncrete. In my opinion, concrete is grounded and you are tied in a complete loop. Make sure you double up your tie wire.
A little tip is to put a top chair every so often, so you can see the depth of your corncrete, while you are pumping it. Make sure you stake it, or it will float.
There Is No Spoon, Huh
CoopElec is offline   Reply With Quote
Old 06-28-2013, 07:16 AM   #7
Aegis's Avatar
Nice I like the top chair Idea for giving you an idea of how high you are How far apart do you stake it?
Old 06-28-2013, 07:40 AM   #8
Semper Fidelis
Suncoast Power's Avatar
Rewards Points: 3,798
I think the formula for impedance includes length so, I wouldn't worry so much.
“If one would give me six lines written by the hand of the most honest man, I would find something in them to have him hanged.” — Cardinal Richelieu in 1641
Old 06-28-2013, 08:05 AM   #9
Rewards Points: 986
That's what she said.
The Following 2 Users Say Thank You to brian john For This Useful Post:
gaffer1 (06-28-2013), Sparky305 (06-28-2013)
Old 06-28-2013, 09:57 AM   #10
Default Stakes
Depends on your spacing. Maybe every 8 to 12 feet.
Old 06-28-2013, 12:41 PM   #11
DWP in LA makes you pull any emt stakes during pour. They site inductive eddy current losses.
big2bird is offline   Reply With Quote
Old 06-28-2013, 01:24 PM   #12
Rewards Points: 986
I tend to agree, while possible, I'd bet in a real world application such as the above, minimal risk.
But avoid it and avoid being posted on an electrical forum.
Old 06-28-2013, 01:39 PM   #13
Rewards Points: 1,210
If the tie wire is a problem then the use of ferrous straps that completely encircle the raceway or the use of a metallic 90 in the run would also be a problem. Neither of those are a real world problem unless you have the some what rare isolated phase installation.
The Following 2 Users Say Thank You to don_resqcapt19 For This Useful Post:
BBQ (06-29-2013), brian john (06-28-2013)
Old 06-28-2013, 06:29 PM   #14
Aegis's Avatar
I'm wondering if some were taught this a while ago and just passed it down to others through out the years without actually knowing. I'll be sure to ask a few inspectors and post what they say in here.
Old 06-28-2013, 07:57 PM   #15
s.kelly's Avatar
Been on a job that the engineer would not allow encircling of any metal on the duct banks. Straps used had to have bolts replaced with nylon ones. I think they had value engineered the job so any little issue might be bigger than normal. Or maybe he was wound a little too tight, who's to say?
s.kelly is offline   Reply With Quote
Old 06-28-2013, 08:25 PM   #16
Rewards Points: 150
maybe if I camped out on this forum all day you could teach me
Old 06-28-2013, 08:41 PM   #17
xaH
You've been here for years but you still don't know anything about electrical work. I don't get it.
Old 06-28-2013, 08:43 PM   #18
Rewards Points: 150
maybe your a bad teacher.
Old 06-28-2013, 08:44 PM   #19
xaH
Could be, I'm just a useless troll.
Old 06-28-2013, 08:47 PM   #20
Rewards Points: 150
or a plumber
Al in duct bank denny3992 General Electrical Discussion 7 11-14-2012 08:57 PM
Gas Line near Duct Bank Aegis Canadian Electrical Code Forum 13 08-20-2012 07:28 PM
Duct bank installed by labourers Mikeinont Canadian Electrical Code Forum 4 08-13-2011 01:36 PM
Duct bank questions Dnkldorf Commercial Electrical Forum 19 05-28-2010 01:21 PM
Primary duct bank question gillman123 Commercial Electrical Forum 9 05-12-2010 07:14 PM