Old 07-03-2009, 09:52 AM   #181
You are right about the EMT being longer. The others are 10 feet long with the coupling on.
Where are you getting the allowing 6 inches on each side of the luminaire from?
ralpha494 is online now   Reply With Quote
Old 07-03-2009, 12:01 PM   #182
You must keep fluorescents 6" clear of any shelf measured vertically to the ceiling. Thus, if you have a twelve inch shelf you would plumb straight to the ceiling and at that point you need to leave 6" . That is from the two art. I stated earlier.
Old 08-03-2009, 05:25 PM   #183
OK. You've had a month to ask a question.
What is the maximum number of # 10 THHN stranded conductors that are permitted in a 10 inch long piece of 1 inch EMT between a panel and a pull box?
A. 16
B. 24
C. 25
D. 26
Old 08-03-2009, 05:37 PM   #184
A. 16
B. 24
C. 25
D. 26
Answer: B
#10 thhhn- .0211.... Table 5
Using Note 4 to Table 4 we can fill 60%
Table 4 area of 1" emt at 60%= .519
divide .519/.0211= 24.6
Old 08-18-2009, 05:25 PM   #185
C'mon Dennis. What's your question?
Old 08-18-2009, 06:31 PM   #186
#6 copper fan
Magnettica's Avatar
What size GEC to a water pipe is needed for a 100 amp service?
Old 10-27-2009, 07:38 PM   #187
2nd year working from 05 code book sheephishly answers: 310.16 says 100 amp service requires #3, so 250.66 says #3 ungrounded service conductors require at least a #8 copper GEC. That is my final answer.
edit: flipped back a page and found 310.15(B)(6) which (I think) states #4's are adequate for 100 amp service. Answer remains the same, however.
electric mike is offline   Reply With Quote
journeyman's practice exam icekillah NEC Code Forum 1 01-21-2009 11:35 PM
MikeHolt Practice Exams vs. The Real Thing chollapete General Electrical Discussion 22 01-19-2009 10:41 PM
three point test / clamp test nick General Electrical Discussion 11 10-13-2008 09:29 PM
Practice does not always make perfect electrictim510 General Electrical Discussion 7 09-10-2008 02:38 PM
can I test stillirnin General Electrical Discussion 8 02-14-2008 10:19 PM