Old 02-08-2009, 11:07 AM   #41
Originally Posted by Greg View Post
I agree but on a Prometric test if they do not give you that data you would go with the 130% answer. Test facilities will generally give you that additional info if they are looking for the 140% answer.
This is why I do so poorly in test...
Old 02-18-2009, 09:46 PM   #42
Professional Nit Picker
New Question:
Electrical Non-Metallic Tubing ____________ permitted to be run through Electrical Metallic Tubing in spaces used for enviromental air.
A) Is
B) Is Not
2008 Nec code Art. _________________
Old 02-18-2009, 09:53 PM   #43
JohnJ0906's Avatar
Originally Posted by manchestersparky View Post
New Question:
A) Is
B) Is Not
A. Is permitted.
300.22(C)(1)
John from Baltimore
"One day at a Time"
Old 02-19-2009, 04:54 PM   #44
where's your question?
Lets see if we can get this thread going
Old 02-19-2009, 05:33 PM   #45
Okay here is an easy one. What is the smallest size copper grounded conductor allowed by the NEC for a 200 amp service?
Old 02-19-2009, 06:12 PM   #46
Wish I was in the water
Greg's Avatar
Disclaimer: This is my weakness. I'm better with motors.
If the service is a resi, I say a #1.
Based off of T. 310.15(B)(6), Art. 310.15(B)(6) & Art. 220.61 2005 NEC
If you're gonna be stupid, you better be tough.
Old 02-19-2009, 06:18 PM   #47
Greg's Avatar
New Question
_________ A protective device for assembly as an integral part of a motor or motor-compressor that, when properly applied, protects the motor against dangerous overheating due to overload and failure to start.
Old 02-19-2009, 06:29 PM   #48
New Question
Overload
Interested on how you got #1. It is not correct but interested anyway.
Old 02-19-2009, 10:05 PM   #49
Greg's Avatar
Overload
The answer by the the book is "thermal Protection" art. 100 definitions
As far as your ? 200A 70% =140A=#1awg according to T 310.15(B)(6)
Educate me, what is the answer. I always run the grounded conductor the same size as the ungrounded conductor(s).
Old 02-19-2009, 10:18 PM   #50
Yeah, I should have looked it up but I took a wild stab at it thinking overload protection. Oh well -1 for me
I was afraid I would have to look this up, but I found it. Art. 250.24(C)(1)
Routing and Sizing. This conductor shall be routed with the phase conductors and shall not be smaller than the required grounding electrode conductor specified in Table 250.66 but shall not be required to be larger than the largest ungrounded service-entrance phase conductor.
Thus, we could technically run a #4 copper conductor . Of course, this would be a rare circumstance and the calculated load would have to be equal to or less than that of a #4 copper.
In almost every resi job I see the grounded conductor is downsized. I typically would run 2/0 copper for the ungrounded conductors and a 1/0 for the grounded conductor for a 200 amp service.
Old 02-23-2009, 03:48 PM   #51
Angry
[quote=Bkessler;55411]Rules are simple, when you answer a question cite article number then ask your own multiple choice question and state what year code was used. this thread hopefully will get people practicing going through the code book fast for exam preparation. After a while hopefully we should get a real good practice test going.
(nec 2005)
Which of the following is not a standard breaker or fuse size?
a)30
b)45
c)175
d)275
sparkinneed is offline   Reply With Quote
Old 02-23-2009, 03:51 PM   #52
[quote=sparkinneed;61087][quote=Bkessler;55411]Rules are simple, when you answer a question cite article number then ask your own multiple choice question and state what year code was used. this thread hopefully will get people practicing going through the code book fast for exam preparation. After a while hopefully we should get a real good practice test going.
(nec 2005)
a)30
b)45
d)275
Old 02-23-2009, 05:23 PM   #53
a)30
b)45
c)175
d)275
Art. 240.6(A) Answer (D)
Old 03-01-2009, 04:27 PM   #54
Default smallest Parallelled conductor size
Originally Posted by Bkessler View Post
Answer is B,90 table 430.22e
(2005 nec)
#3) What size conductor is the smallest size conductor to be run in parallel?
a) #12
b) 1/0
c) 4/0
d) 250 mcm
e) 500 mcm
(2008 nec)
310.4 Conductors in Parallel.
(A) General.
Aluminum, copper-clad aluminum, or copper conductors of size 1/0 AWG and larger, comprising each phase, polarity, neutral, or grounded circuit conductor shall be permitted to be connected in parallel (electrically joined at both ends).
Exception No. 1: Conductors in sizes smaller than 1/0 AWG shall be permitted to be run in parallel to supply control power to indicating instruments, contactors, relays, solenoids, and similar control devices, or for frequencies of 360 Hz and higher, provided all of the following apply:
(a) They are contained within the same raceway or cable.
(b) The ampacity of each individual conductor is sufficient to carry the entire load current shared by the parallel conductors.
(c) The overcurrent protection is such that the ampacity of each individual conductor will not be exceeded if one or more of the parallel conductors become inadvertently disconnected.
Exception No. 2: Under engineering supervision, grounded neutral conductors in sizes 2 AWG and larger shall be permitted to be run in parallel for existing installations.
FPN to Exception No. 2: Exception No. 2 can be used to alleviate overheating of neutral conductors in existing installations due to high content of triplen harmonic currents.
(E) Equipment Grounding Conductors. Where parallel equipment grounding conductors are used, they shall be sized in accordance with 250.122. Sectioned equipment grounding conductors smaller than 1/0 AWG shall be permitted in multiconductor cables in accordance with 310.13, provided the combined circular mil area in each cable complies with 250.122.
620.12 Minimum Size of Conductors.
The minimum size of conductors, other than conductors that form an integral part of control equipment, shall be in accordance with 620.12(A) and (B).
(A) Traveling Cables.
(1) Lighting Circuits. For lighting circuits, 14 AWG copper, 20 AWG copper or larger conductors shall be permitted in parallel, provided the ampacity is equivalent to at least that of 14 AWG copper.
If the test is tricky, the answer can be:
1) 1/0 AWG
2) < 1/0 AWG
3) 2 AWG
4) 20 AWG
/s/ Jim Williams
jfwfmt is offline   Reply With Quote
Old 03-06-2009, 11:57 AM   #55
I thought 620.12 (B) said 24 AWG but after re-reading it I see that it isn't talking about parallel conductors.
Here's two of my favorites:
Using the 2008 NEC:
A restaurant has two (2) 18 kW ranges and two (2) 2 kW appliances, all of which are thermostatically controled. What is the total kVA demand on the service?
A. 32
B. 34
C. 36
D. 40
What is the minimum number of straps required to support 118 feet of straight 2-1/2 inch IMC between two boxes in a hospital corridor?
A. 8
B. 9
C. 12
D. 13
Last edited by ralpha494; 03-06-2009 at 03:52 PM. Reason: After further examination, the ruling on the field is overturned
ralpha494 is offline   Reply With Quote
Old 03-06-2009, 10:34 PM   #56
220.56 and table 220.56 Answer A
342.30(A) and (B)(2) and table 344.30(B)(2) Answer A
nec 2008
What colors are permitted for insulation or or marking of wires greater than #6 for neutral conductors?
A White
B Gray and White
C White and light Blue
D all of the above
Old 03-07-2009, 08:21 AM   #57
JohnJ0906's Avatar
nec 2008
A White
B Gray and White
D all of the above
B - 200.6(B)
Electrical systems shall be connected to earth in a manner that will -
a) limit the voltage imposed by lightning, line surges, or unintentional contact with higher voltage lines
b) stabilize the voltage to earth during normal operation
c) create a low-impedance fault path
d) a + b
e) all of the above
John from Baltimore
"One day at a Time"
Old 03-07-2009, 10:30 AM   #58
Thumbs down Neutral color question
Actually it is a matter of how you read the question.
1) insulation on any wire size or marking tape on #6 or larger wires
2) insulation color on or marking tape on #6 or larger wires
for 1) interpretation the answer is D
for 2) interpretation the answer is B
I would go for 1) because it has the more obscure part of the code in its answer
/s/ Jim WIlliams
Old 03-07-2009, 07:23 PM   #59
Using the 2008 NEC:
A. 32
B. 34
C. 36
D. 40
The answer is 36 kW. Read the last sentance in 250.56.
Old 03-07-2009, 07:31 PM   #60
JohnJ0906's Avatar
A White
B Gray and White
D all of the above
/s/ Jim WIlliams
OK, I guess it is obscure, because I can't find where light blue is permitted/required for a neutral.
John from Baltimore
"One day at a Time"
journeyman's practice exam icekillah NEC Code Forum 1 01-21-2009 11:35 PM
MikeHolt Practice Exams vs. The Real Thing chollapete General Electrical Discussion 22 01-19-2009 10:41 PM
three point test / clamp test nick General Electrical Discussion 11 10-13-2008 09:29 PM
Practice does not always make perfect electrictim510 General Electrical Discussion 7 09-10-2008 02:38 PM