Old 03-07-2009, 08:07 PM   #61
Default 400 Flexible cords
400.28(C)
It covers power cables. Many computer power cables use european color codes: light blue neutral, brown hot, grounded green / yellow
jfwfmt is offline   Reply With Quote
Old 03-07-2009, 08:11 PM   #62
What is the maximum ampacity, number of conductors, and minimum conduit size for circuits protected by 30A Circuit Breakers using #10 wire with a grounding wire enclosed in a single IMC under the following conditions:
I THHN dry conditions 1 phase 120/240V service
II THWN wet or dry conditions 1 phase 120/240V service
III THWN-2 wet or dry conditions 1 phase 120/240V service
IV THHN dry conditions 3 phase 120/208V service
A 180, 10, ¾”
B 240, 13, 1”
C 270, 13, 1”
D 180, 9, 1”
E 270, 15, 1”
F none of the above
I ________
II ________
III _______
IV _______
Code References:
________________
________________
________________
________________
________________
________________
________________
Old 03-08-2009, 08:38 AM   #63
Chris Kennedy's Avatar
Is there a typo in the above???
Bulldozers and Dirt
Old 03-08-2009, 08:46 AM   #64
Wish I was in the water
Greg's Avatar
I agree there has to a typo, I'm not seeing a #10 carrying 270A
If you're gonna be stupid, you better be tough.
Old 03-08-2009, 09:36 AM   #65
Note that conductorS and circuit breakerS are plural
Old 03-08-2009, 09:54 AM   #66
JohnJ0906's Avatar
Originally Posted by jfwfmt View Post
400.28(C)
There is no 400.28 in the '08 or '05
John from Baltimore
"One day at a Time"
Old 03-08-2009, 09:56 AM   #67
JohnJ0906's Avatar
OK, 400.22(C)
Gotcha.
John from Baltimore
"One day at a Time"
Old 03-08-2009, 10:54 AM   #68
400.28(C)
Manufacturers have different rules than the EC under the NEC. The NEC does not allow light blue as a neutral.
Alice
Old 03-08-2009, 11:11 AM   #69
Are you saying what is the maximum amps the circuit can surge to on a circuit with a 30 amp OCP. It is obviously written poorly. A circuit cannot carry 180 amps or any of the above on a 30 amp OCPD for very long.
Alice
Old 03-08-2009, 05:19 PM   #70
And who are you to judge? You an English major?
I think I see where this question is headed. Lets look at this.
A 180, 10, ¾”
Under condition I
This conduit would have 6 ccc's. 180÷6=30A
I believe the question is looking for the amps of all the conductors in the conduit added together, yes?
Bulldozers and Dirt
Old 03-08-2009, 05:23 PM   #71
No, I was born in American and I think I speak pretty good American.
Alice
Old 03-08-2009, 05:45 PM   #72
LOL
Bulldozers and Dirt
Old 03-08-2009, 07:11 PM   #73
Wrong, see NEC 2008,2005,&2002 400.22(C)
Old 03-08-2009, 07:12 PM   #74
JohnJ0906's Avatar
OK, 400.22(C)
Gotcha.
Check that article right there. Light blue is allowed under the provisions of that article.
John from Baltimore
"One day at a Time"
Old 03-08-2009, 07:13 PM   #75
JohnJ0906's Avatar
Electrical systems shall be connected to earth in a manner that will -
a) limit the voltage imposed by lightning, line surges, or unintentional contact with higher voltage lines
b) stabilize the voltage to earth during normal operation
c) create a low-impedance fault path
d) a + b
e) all of the above
No one's going to answer that one? I thought it was an easy one.
John from Baltimore
"One day at a Time"
Old 03-08-2009, 07:14 PM   #76
OK, 400.22(C)
Gotcha.
OK, you got me
I'll turn on the light rather than reading the NEC by the glow of the laptop screen.
Old 03-08-2009, 07:22 PM   #77
Under condition IThis conduit would have 6 ccc's. 180÷6=30A
You are moving in the right direction, the answer is wrong and there is a bunch of code references to cite.
The idea of the question is to determine how many 30A circuits you can put in a single conduit raceway under varying circumstances, using #10 wire. It has actual practical applications.
Getting the right answer requires you to understand several aspects of the code.
Keep trying
/s/ Jim WIlliams
[Note to English Majors, "is" refers to "bunch" not "references"]
Old 03-08-2009, 08:49 PM   #78
250.4 (A) (1) NEC 2008
What is the minimum height for a 480 V luminaire to be installed in a parking lot?
ralpha494 is offline   Reply With Quote
Old 03-08-2009, 09:07 PM   #79
JohnJ0906's Avatar
22 feet. 210.6(D)(1)(a)
All boxes and conduit bodies, covers, extension rings, plaster rings and the like shall be durably and legibly ______________.
John from Baltimore
"One day at a Time"
Old 03-09-2009, 05:36 AM   #80
marked with the manufacturer's name or trademark. (314.44)
Bulldozers and Dirt
journeyman's practice exam icekillah NEC Code Forum 1 01-21-2009 10:35 PM
MikeHolt Practice Exams vs. The Real Thing chollapete General Electrical Discussion 22 01-19-2009 09:41 PM
three point test / clamp test nick General Electrical Discussion 11 10-13-2008 08:29 PM
Practice does not always make perfect electrictim510 General Electrical Discussion 7 09-10-2008 01:38 PM
can I test stillirnin General Electrical Discussion 8 02-14-2008 09:19 PM