Forgot Ufer..Ooops! - Electrician Talk - Professional Electrical Contractors Forum
Old 05-26-2011, 08:27 PM   #1
Rewards Points: 2,050
Default Forgot Ufer..Ooops!
Inspector came out for rough today. He passed but he asked if the footers had an ufer ground. The GC was standing right there and said no. Then he said does it have rebar in it. The GC jumped in and said yes (wrong answer). Then he said since we upgraded service at same time then it needs ufer ground.
Now, the gc called me after they poured slab and said he is ready for me to start roughing. I had no clue when the job was even starting til last second. Now, he says I should have warned him and I should pay? Say What?
Old 05-26-2011, 08:36 PM   #2
dronai's Avatar
Rewards Points: 3,337
I always talk about it with a General before the job, and with the concrete guys sometimes. Ground rod time..
We have underground service on new, so it's easier for me to know, because I'm putting in my sweep.
I walk around the jobsite like everything is fine, but deep down inside my boot, my sock is sliding down
Old 05-26-2011, 08:42 PM   #3
Default GR
He said no ground rod. We had to jackhammer up the footer and then run a bonding jumper to the GEC. Does this sound correct or is he jackleggin me?
Old 05-26-2011, 08:46 PM   #4
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
If he told you about the work after the pour then it's the GC's fault. But if you knew you were going to be doing this electrical work, then you had to have known a concrete-encased electrode was required. But like I said what matters is when you were first asked about the service upgrade.
Replies based on NEC 2014
Old 05-26-2011, 08:49 PM   #5
Default Time
Well. He told me about job in Dec. There were problems with financing and he said he would call when he was ready for me. Well, he called me after he poured the slab. We didn't even have a contract or anything yet.
Old 05-26-2011, 08:51 PM   #6
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
So you're off the hook. The inspector passed it so you're good. Tell the GC next time we need to have it in a similar situation.
Old 05-26-2011, 08:51 PM   #7
Rewards Points: 5,198
Do you have a contract now?
Old 05-26-2011, 08:52 PM   #8
NJ-IEC
Magnettica's Avatar
Rewards Points: 424
Better yet, did you get the check?
Old 05-26-2011, 08:58 PM   #9
Default Check
No check yet. He's good for it. Been working a while for him. I may just suggest he rents the jackhammer and buys the #4 and i'll run it just to keep peace and share a small portion of responsibility. I make alot off him per year so....
Old 05-26-2011, 09:05 PM   #10
How big a contractor could he be if he couldn't get financing for one house?
Old 05-26-2011, 09:10 PM   #11
Default Mod
He's moderate. The financing problem was with homeowner. Isn't there an exception is the rebar is under 6 ft or something like that?? I"ve never had to bond rebar all these years. Got out of new home construction 10 yrs ago when it all started going downhill.
Old 05-26-2011, 09:16 PM   #12
Using a ufer, as far as I know is the most adequate form of lightning/aberrant current protection. You should ALWAYS plan on using it. Comparing ,dragging a #6 cu 90 feet through a house to a water pipe seems almost criminal. Just my opinion.
Old 05-26-2011, 10:31 PM   #13
danickstr's Avatar
Rewards Points: 540
funny that Ufer is a guys name when UF wire is Underground feed. What I don't like about attaching copper to a rebar cage under the cement is the oxidization. I like to ell a piece of 20' rebar that pops up inside the wall and attach the bronze acorn there.
Do you have a healthy Butternut tree near you? We need to save the American Butternut tree!
danickstr is offline   Reply With Quote
Old 05-26-2011, 11:37 PM   #14
Rewards Points: 2,020
And of course that highly intelligent method is discouraged by the local insptr's here.... They decided the part sticking out of the slab is subject to rusting away..... so they don't accept it. (a few of them do, just a few.)
Old 05-26-2011, 11:42 PM   #15
ET rocks
3xdad's Avatar
Rewards Points: 2,174
Is this the GC's first rodeo?
Here, "IN NEW CONSTRUCTION, a CEE shall be considered available and installed per 250.52(A)(3)" This is then signed off by the BUILDING inspector. So a GC knows it has to go in before his pre pour inspection.
It also goes on to state, if a CEE is not present, then 20' of #2 bare CU not less than 30" deep in a continuous trench with 2 rods 6' apart...
Does Georgia have any ammendments like this? Even still, it seems like the inspector could have allowed another NEC permitted electrode.
3xdad is offline   Reply With Quote
Old 05-26-2011, 11:58 PM   #16
A Little Short's Avatar
Rewards Points: 54
They are required to be at least 20'. Also the exception in 250.50 says ...CCEs of existing buildings shall not be required to be a part of the grounding electrode system where the rebar or rods is not accessible without disturbing the concrete.
I don't know if this applies here since GC should have known about the CCE before pouring the concrete. But now it is existing!
Old 05-27-2011, 07:21 AM   #17
Semper Fidelis
Suncoast Power's Avatar
Rewards Points: 3,374
A real GC would have known about that Ufer. We have it on the structural checklist here. Covers everybody's butt.
or just enjoy the show.
Old 05-27-2011, 08:03 AM   #18
RIP 1959-2015
HARRY304E's Avatar
Rewards Points: 1,344
Are you saying that he ran the bonding jumper??
If so why is he doing that he should have had you doing that instead.
Old 05-27-2011, 08:12 AM   #19
Rewards Points: 12,104
I thought "he" was the inspector.
Giving up on unbiased truth.
Ufer Apprentice_617 General Electrical Discussion 26 02-15-2011 06:09 AM
Ufer Apprentice_617 General Electrical Discussion 7 02-07-2011 10:54 PM
After being out of work so long, I think I forgot how to do it! Forgery Off Topic (Non Trade) 34 03-10-2010 11:34 PM
just a few I forgot to post JoeKP Code Violation Discussion 23 02-16-2010 01:05 AM
Hello ladies, ooops I meant germs or is it? GoodLookingUglyGuy Introductions 3 02-03-2010 08:38 AM