GFCI Breaker trips immediately - Electrician Talk - Professional Electrical Contractors Forum
Old 03-07-2010, 03:32 PM   #1
Default GFCI Breaker trips immediately
I have 2 20a 120v circuits each on a GFCI breaker. The length of the run is about 200' and they share a neutral. #8 was ran for vd. There is no load on either circuit yet, however as soon as I turned on either of them the gfci tripped immediately. I checked for a short with my tester and didnt get anything. I removed the neutral coming off on of the breakers from the neutral bar, and turned both breakers on and they held. I did this before I left and havnt had time to troubleshoot this too deeply. I wonder if they held all weekend cause I'll be back on monday to figure it out. Any ideas?
ikeberg9 is offline   Reply With Quote
Old 03-07-2010, 03:34 PM   #2
Rewards Points: 3,855
You can't wire a multiwire branch circuit on two GFCI breakers. You'll need to use a 2-pole GFCI. Get it? Got it. Good! Ten-four. Over and out.
Old 03-07-2010, 03:36 PM   #3
Big Member
Rewards Points: 258
Yeah you can't share the neutral unless you use a double pole breaker.
Just do your best, that will be plenty bad enough.
stars13bars2 is offline   Reply With Quote
Old 03-07-2010, 03:37 PM   #4
Big Member
Rewards Points: 258
I know it didn't take me two minutes to type that.
Old 03-07-2010, 03:39 PM   #5
In my best Maxwell Smart voice:
"Missed it by that much"
Old 03-07-2010, 03:56 PM   #6
LOL, yal are trip. That's what I thought. I got it and I'm out.Thanks.
Old 03-07-2010, 03:57 PM   #7
Rewards Points: 1,304
And the length is pushing the limits. Utilize GFCI receptacles.
What type of tester did you use?
Old 03-07-2010, 03:58 PM   #8
I seem to recall a functional limit of 250 feet in the old GFCI packaging, but I can't recall reading that lately.
Old 03-07-2010, 04:03 PM   #9
william1978's Avatar
Rewards Points: 2,000
Use Regular breakers and use GFCI recs so you don't have to add another neutral from the panel to the rec's.
Old 03-07-2010, 04:39 PM   #10
These circuits are for heating elements on some tire shredders, so a GFCI rec. wont work. The wire and breakers were already installed before I got there, so I don't even know why it needs to be GFCI protected and don't know the actual footage. I didn't spend much time on it, but I wanna get it straight first thing Monday. So a two pole GFCI should fix the problem?
I used my Fluke T5 tester to test continuity on the wires and didn't find any shorts.
Old 03-07-2010, 04:48 PM   #11
charlie Bob's Avatar
Rewards Points: 250
So what did they do to MBC neutral? They spliced it and pigtailed it to the GFCI breakers?
charlie Bob is offline   Reply With Quote
Old 03-07-2010, 04:51 PM   #12
I think you're thinking what I'm thinking. They probably landed the MWBC neutral on the bar, and put both GFCI breaker pigtails on the bar too.
To the OP... make sure you put the circuit's neutral on the neutral terminal of the 2-pole GFCI breaker when you put it in, and NOT on the bar.
You an electrician or a factory maintenance guy?
Old 03-07-2010, 05:08 PM   #13
Toronto Sparky's Avatar
Rewards Points: 1,008
20A GFI recepts are available everywhere..
Two pole GFI breakers cost too much
Don't fight .. Play nice!
Old 03-07-2010, 09:34 PM   #14
I am an electrician. The guy who pulled the wire and put in the breakers, was laid off, so now that the equipment that needs to be installed came in, I have to finish it off. The GFCI breakers were installed correctly, it just needed a two pole GFCI. I havn't had to deal with many GFCI breakers, but I never dealt with a mwbc GFCI breaker.
Old 03-07-2010, 10:19 PM   #15
Rewards Points: 250
You are saying the GFCI breakers were installed correctly. Well they couldn't have. How can you install 2 GFCI breakers correctly when you have a MWBC, sharing a neutral.?
Both of them breakers require a neutral going to them?
Old 03-07-2010, 10:28 PM   #16
Rewards Points: 3,498
Depends on the brand, not too bad and they're wicked chunky...
can one breaker be tripped when another one trips with a mechanical short? lj150 General Electrical Discussion 22 10-22-2009 10:58 PM
gfci breaker trippin bridgeguy General Electrical Discussion 10 05-16-2009 12:11 PM
GFCI Trips????? jayare813 General Electrical Discussion 21 03-15-2009 06:28 AM
gfci breaker circuit ? french connection!! NEC Code Forum 15 12-29-2007 01:03 PM
Afci Breaker trips. Hillbilly General Electrical Discussion 17 04-17-2007 10:01 AM