Old 09-26-2011, 11:53 PM   #1
Default gfci's for pumps?
Hooked up a flood control pump today in an underground vault. Used a simplex outlet mounted high in the vault, with an in-use cover for dripping moisture. service gfi is located aboveground, ten feet away. Flood pump tagged for gfci operation, which I installed indoors in a highly visable location, used a leviton with the green "ready to go " light. My question here is, now the expensive flood control for the expensive home is at the mercy of the gfci device, I am worried about this: can I just follow code and ignore the pump's manufacturer's tag on his connection cord?
Signalservice is offline   Reply With Quote
Old 09-27-2011, 12:03 AM   #2
Chief Electron Relocator
Being in ChiTown, don't you have your own code and not the NEC?
Old 09-27-2011, 05:39 AM   #3
Does code allow no GFCI? If so, then I probably would ignore the tag. One could argue that a vault is not outside and if the vault is not part of the home then it may be compliant but as Ken said what is Chicago code?
mrmike (09-27-2011)
Old 09-27-2011, 05:40 AM   #4
I void warranties
Jlarson's Avatar
Removing the GFCI isn't the answer and it's also stupid and unnecessary.
If this pump is truly critical a back up pump and/or alarms are in order.
The best never stop learning.
Jlarson is online now   Reply With Quote
The Following 2 Users Say Thank You to Jlarson For This Useful Post:
Big John (09-27-2011), wdemos (09-29-2011)
Old 09-27-2011, 05:41 AM   #5
Some areas have amendments that allow no GFCI for sump pumps.
Old 09-27-2011, 05:43 AM   #6
I void warranties
Jlarson's Avatar
Those are stupid and unnecessary too. It's not the proper way to go.
Old 09-27-2011, 06:12 AM   #7
chicken steve's Avatar
i can't see why a dedicated GFPE couldn't be employed....~CS~
Old 09-27-2011, 06:15 AM   #8
I void warranties
Jlarson's Avatar
Cause the manufacturer (like many others) calls for a GFCI, not a GFP.
Old 09-27-2011, 06:18 AM   #9
I would never put s gfci on a sump pump. Even if you have an alarm what if the HO goes away on vacation and the GFCI decides it doesn't want to work anymore? That would be a nice gift when you got back.
CanadianSparky is offline   Reply With Quote
The Following 2 Users Say Thank You to CanadianSparky For This Useful Post:
ce2two (09-27-2011), kbsparky (09-27-2011)
Old 09-27-2011, 06:21 AM   #10
kbsparky's Avatar
I disagree.
GFCI's are way overrated, since they are vulnerable to nuisance tripping.
Had a job with 2 sump pumps in a fire pump pit. Each sump pump was fed by its own GFCI protected outlet.
Lightning storms routinely trip out GFCI's and this was no exception.
So the storm hit, both GFCIs tripped out, and then the fire pump pit flooded out.
Now you have a useless 100 hp fire pump, since it's under 3 feet of water!!
I doubt that an alarm could have stopped it in time. But a couple of working sump pumps may have done their job, if they had a reliable power supply.
So now you have an entire shopping center with no fire pump system in place. Who is at risk now?
-KB
Old 09-27-2011, 06:25 AM   #11
I void warranties
Jlarson's Avatar
Originally Posted by kbsparky View Post
I disagree.
Yeah, get zapped by faulty pumps when you drop a tool into a sump while you're working in a vault an you'll change that view.
As for your fire pump problem, someone forgot the most critical rule of critical alarms, monitoring. Big part of the puzzle.
Old 09-27-2011, 06:26 AM   #12
Lite em up !
mrmike's Avatar
It is more Stupid to take the chance of this pump not coming on, because of a trip from a GFI..........if Code allows it- in this case, exclude the manufacturers suggestion.......
mrmike is offline   Reply With Quote
Old 09-27-2011, 06:33 AM   #13
I void warranties
Jlarson's Avatar
Which would be a code violation, it's probly going to void the warranty and also it will open you up to liability if some gets zapped...
Old 09-27-2011, 06:33 AM   #14
kbsparky's Avatar
Yeah, get zapped by faulty pumps when you drop a tool into a sump while you're working in a vault an you'll change that view. ....
I never put my hand into a sump pit with the motor still plugged in. GFCI or not, that's plain stupid.
Hard to monitor such alarms with raging lightning storm out. Many alarms will trigger whether they have tripped or not, from the static in the air. Then there is the response time factor. Alarm trips, it's middle of the night ... takes awhile to investigate problem(s) .... by the time someone gets there, it's too late, damage is done.
I prefer prevention, using things like double-insulated pumps, or even isolation transformers instead of relying on something as fickle as a GFCI receptacle.
This was NOT a dwelling, either.
-KB
Old 09-27-2011, 06:35 AM   #15
yes i realize that JL
one would think they'd have fielded numerous complaints to that end
that said, if it's not manufacturers dictating protection, it'll be the nec
gfci protection and afci protection has grown to where almost everything within a dwelling is protected by them
i find this inefficent, a recipee for constant callbacks
what i do find interesting is the euro solution of differentials
of course, finding a meter for it all would take a generation of use/abuse for subsequent statistical anaylsis
at which point we'll be sold version 4,5, 6, etc
Old 09-27-2011, 06:36 AM   #16
I void warranties
Jlarson's Avatar
and for good measure
What in the name of all this is good and holy are people using for alarms out there?
Old 09-27-2011, 06:38 AM   #17
kbsparky's Avatar
You've never talked with anyone who works at an alarm monitoring station, have you?
I have had friends who work in such environments, and they can track a storm better than the weatherman!
-KB
Old 09-27-2011, 06:39 AM   #18
I disagree.
well i can imagine yelling GFCI in a crowded fire is a definite no no kb
Old 09-27-2011, 06:40 AM   #19
I void warranties
Jlarson's Avatar
I can't make heads or tails of your post (although I appreciate that you are using a more normal font size now ).
What I realize it that many of you need to come work with my guys for a day and see that pumps can work just fine on GFCI's.
Old 09-27-2011, 06:41 AM   #20
i believe i read reference to having an alarm exempt from whole house gfi's JL
nfpa 72, iirc
Gfci's work! 220/221 General Electrical Discussion 13 07-19-2011 09:04 PM
GFCI's on Fridge Seriously M7B General Electrical Discussion 17 01-25-2011 03:22 AM
Sideways GFCI's Marshall175 General Electrical Discussion 16 07-21-2010 07:23 PM
Gfci's in garages. Rudeboy Residential Electrical Forum 60 01-18-2010 07:50 PM
GFCI's Absolutetruthz General Electrical Discussion 25 06-03-2008 06:21 AM