Old 03-15-2009, 04:09 PM   #1
Default In ground pool
Per the nec 680 are the pool lights the only equipment to be gfic protected? Hard wired pumps, and blowers do not?
EXCEL12 is offline   Reply With Quote
Old 03-15-2009, 04:30 PM   #2
Yes, that's correct if they're hard wired.
Be sure they're at least 5' away from the inside walls. If they're cord and plug connected they would need to be, and any receptacles within 20'.
Don't know if anything changed in 08.
Jim
wirenut1110 is offline   Reply With Quote
Old 03-15-2009, 04:35 PM   #3
Well, you already know it is in Art680, now you just need to find it.
Start in 680.21 & 680.22
Old 03-15-2009, 04:36 PM   #4
Yup, they changed 5' to 6'.
Old 03-15-2009, 04:54 PM   #5
Yep. 2008 you need to GFCI pool pumps hard wired or not.
Originally Posted by NEC 2008
680.22(B) GFCI Protection. Outlets supplying pool pump motors from branch circuits with short-circuit and ground-fault protection rated 15 or 20 amperes, 125 volt or 240 volt, single phase, whether by receptacle or direct connection, shall be provided with ground-fault circuit-interrupter protection for personnel.
Alice
Old 03-15-2009, 05:09 PM   #6
Maybe it could be changed to where, instead of your location, the code cycle you're under
Jim
Old 03-15-2009, 05:14 PM   #7
I'm sorry, I should have indicated we are still using NEC 2005. Thank You.
Old 03-15-2009, 05:19 PM   #8
Yup, and that too.
In ground pool gfic equipment EXCEL12 Site Help and Suggestions 1 03-15-2009 04:32 PM
GFI to Pool Panel Sparks 1942 NEC Code Forum 15 12-03-2008 07:31 PM
Pool Bonding rebel34 NEC Code Forum 21 08-16-2008 09:32 PM
120 vs. 240 pool pump wirenut1110 General Electrical Discussion 15 06-21-2008 08:56 AM
Pool Grounding Larry NEC Code Forum 4 02-03-2007 08:10 AM