07-30-2008, 08:52 AM
Ground rod
I am wireing a small shed with 120/240/ 30 amp. and was installing the ground rod last night.
Well, I still have 18" above the ground that does not want to move.
Would you add another rod, and cut the first one short and connect them together, or abandon the first and connect to the second one?
Or does anyone have a super slick way to get that last 18" into the ground?
GO JACKETS!
07-30-2008, 09:36 AM
More the merrier. I would just cut the 18" off put in another one 6' from it and connect them together.
07-30-2008, 10:20 AM
If you think a second one will be tough to drive in put it at a sharp angle.
When ls lunch
07-30-2008, 10:23 AM
Ax grinder
You must have 8' of length of the ground rod in contact with the earth, see 250.53(G), so cutting off 18" would not meet this requirement unless the ground rod was a 10' rod.
Also, did the ground rod meet the 25 Ohm requirement of 250.56? If not you need a second rod anyway.
Chris
07-30-2008, 11:49 AM
"A" inside wireman
Chris
He did say cut that one and add another, not cut it and use it.
"One Nation Under God"
07-30-2008, 12:35 PM
Ax grinder
Yep, see that now, my bad sorry.
Chris
07-30-2008, 05:21 PM
Not sure if it's the POCO here or an NEC requirement, don't have my book on hand  . If the ground rod is put at an angle it has to be 45 - 90 degrees.
Chris
Funny that you say that Raider. Got a call from a client who told me to call the POCO about her meter. Ends up that the meter they are putting on won't work since the ground system doesn't meet the 25 Ohm requirement. It's an 80 year old house so I'll be sinking a couple rods there this Friday.
07-30-2008, 05:28 PM
Did you try the cup of water trick? Also whats the code on laying it down in a ditch I seen people do it before and say it was ok but i was skeptical.
07-30-2008, 05:30 PM
How are you banging them in? With a good demo hammer?
07-30-2008, 06:12 PM
Ax grinder
Here is what the 2008 NEC says about installing ground rods:
250.53(G) Rod and Pipe Electrodes. The electrode shall be installed such that at least 2.44 m (8 ft) of length is in contact with the soil. It shall be driven to a depth of not less than 2.44 m (8 ft) except that, where rock bottom is encountered, the electrode shall be driven at an oblique angle not to exceed 45 degrees from the vertical or, where rock bottom is encountered at an angle up to 45 degrees, the electrode shall be permitted to be buried in a trench that is at least 750 mm (30 in.) deep. The upper end of the electrode shall be flush with or below ground level unless the aboveground end and the grounding electrode conductor attachment are protected against physical damage as specified in 250.10.
Chris
07-30-2008, 06:13 PM
Ax grinder
Thats interesting, what happens if you install a second rod and you still don't get 25 Ohms?
Chris
07-30-2008, 06:15 PM
Ax grinder
I always try to use a hammer drill with a ground rod bit.
Chris
07-30-2008, 07:25 PM
07-30-2008, 07:27 PM
Got it this time.
07-30-2008, 08:13 PM
What kind of meter requires a connection to earth to function?
John from Baltimore
"One day at a Time"
07-30-2008, 10:19 PM
And what does the earth accomplish? sounds fishy if you ask me...
07-30-2008, 10:27 PM
Chris
That is what I am using, and of course the good old sledge hammer.
What is the cup of water trick?
I guess I'm driving another tomorrow.
GO JACKETS!
07-30-2008, 10:40 PM
#18
No idea, POCO is meeting me up there to put the meter on after I get the ground rods driven. He hasn't said anything about having to replace the meterbase, hopefully I don't need to.
I'll get some information from him about it.
07-30-2008, 10:44 PM
#19
Chris
The earth stops spinning on it's axis and I go home  . I'm positive it does not need to be exactly 25 ohms.
07-31-2008, 09:20 AM
#20
Chris
Nothing, you have satisfied the Code requirements. The Code does not require that you continue to drive additional rods until you get to 25 ohms or less.
| Thread |
Thread Starter |
Forum |
Replies |
Last Post |
2 ground rods
MikeD |
NEC Code Forum |
116 |
12-07-2009 12:38 PM |
Ufer ground
James Con |
14 |
12-04-2009 08:45 PM |
Counterposing Ground
casparbrooke |
6 |
07-31-2008 07:50 PM |
Equipment Ground
Absolutetruthz |
6 |
06-06-2008 06:23 AM |
Ground or not to ground?
chenley |
Services and Service Equipment |
5 |
05-06-2008 11:38 PM |