grounding - Electrician Talk - Professional Electrical Contractors Forum
Old 02-23-2013, 09:48 AM   #1
Default grounding
A fundamental rule regarding the grounding of metal boxes, luminaires, and so on, is that they must be grounded when "in reach of what"?
SparkyMcSparkerson is offline   Reply With Quote
Old 02-23-2013, 10:14 AM   #2
A Little Short's Avatar
Rewards Points: 76
Originally Posted by SparkyMcSparkerson View Post
A fundamental rule regarding the grounding of metal boxes, luminaires, and so on, is that they must be grounded - PERIOD!
Fixed it for you!
No within reach rule that I know of.
The Following User Says Thank You to A Little Short For This Useful Post:
SparkyMcSparkerson (02-23-2013)
Old 02-23-2013, 10:24 AM   #3
BBQ
Salty Member
BBQ's Avatar
Originally Posted by Little-Lectric View Post
Fixed it for you!
Not entirely true code wise.
Check out 250.110.
250.110 Equipment Fastened in Place (Fixed) or Connected
by Permanent Wiring Methods.
Exposed, normally
non–current-carrying metal parts of fixed equipment
supplied by or enclosing conductors or components that are
likely to become energized shall be connected to an equipment
grounding conductor under any of the following conditions:
(1) Where within 2.5 m (8 ft) vertically or 1.5 m (5 ft)
horizontally of ground or grounded metal objects and
subject to contact by persons
(2) Where located in a wet or damp location and not isolated
(3) Where in electrical contact with metal
(4) Where in a hazardous (classified) location as covered
by Articles 500 through 517
(5) Where supplied by a wiring method that provides an
equipment grounding conductor, except as permitted
by 250.86 Exception No. 2 for short sections of metal
enclosures
(6) Where equipment operates with any terminal at over
150 volts to ground
Exception No. 1: If exempted by special permission, the
metal frame of electrically heated appliances that have the
frame permanently and effectively insulated from ground
shall not be required to be grounded.
Exception No. 2: Distribution apparatus, such as transformer
and capacitor cases, mounted on wooden poles at a
height exceeding 2.5 m (8 ft) above ground or grade level
Exception No. 3: Listed equipment protected by a system
of double insulation, or its equivalent, shall not be required
to be connected to the equipment grounding conductor.
Where such a system is employed, the equipment shall be
distinctively marked.
Old 02-23-2013, 10:57 AM   #4
Rewards Points: 262
Looks like a test question. I am not sure of the answer other then to say ground but that is not correct. Sounds like a bad question
The Following 2 Users Say Thank You to Dennis Alwon For This Useful Post:
BBQ (02-23-2013), SparkyMcSparkerson (02-23-2013)
Old 02-23-2013, 10:58 AM   #5
Hotlegs's Avatar
Rewards Points: 250
In reach of a cold beer?
Hotlegs is offline   Reply With Quote
The Following User Says Thank You to Hotlegs For This Useful Post:
Old 02-23-2013, 11:03 AM   #6
Lol!
I am tempted to see if my instructor will except that answer!
The Following User Says Thank You to SparkyMcSparkerson For This Useful Post:
Hotlegs (02-23-2013)
Grounding RIVETER General Electrical Discussion 54 11-28-2011 08:47 AM
Replacing non-grounding receptacles with grounding Gamit General Electrical Discussion 31 01-10-2011 11:34 PM
Grounding 250.24 uber stein NEC Code Forum 17 09-17-2010 05:02 PM
PV grounding Destrey General Electrical Discussion 1 01-15-2010 04:24 PM
Grounding jdeihs NEC Code Forum 3 08-24-2008 01:30 AM