Old 03-05-2009, 01:12 AM   #1
Default Lights flicker,wattage drop...any ideas,help
The lights in the whole house flicker once and lose wattage when something stronger is pluged in at any outlet in the house,even on new added circuits from recently done main upgrade.All lights are still on old knob and tube circuit.Any ideas what might be the problem?Thanks...
renimus is offline   Reply With Quote
Old 03-05-2009, 06:58 AM   #2
If this was a problem before you started working there then I suspect the problem is poco's. Long distance from the trany to the house, undersized wire, etc. This can easily cause a temp. voltage drop when extra power is needed for motors etc.
If this just started to happen then I would look for a loose connection at the service.
Old 03-05-2009, 07:58 AM   #3
JohnJ0906's Avatar
Check the main neutral.
Take voltage readings, L1-N, L2-N, and L1-L2 while the load is plugged in.
If one line rises and the other drops (in relation to the neutral) you have a loose or open neutral.
John from Baltimore
"One day at a Time"
Old 03-05-2009, 05:02 PM   #4
semi-electrician
What John said.
Old 03-05-2009, 05:07 PM   #5
I'd check the tightness of all service connections at the meter socket and the panel. If aluminum conductors were used, make sure they have "nolox" on them and that they are still tight. Aluminum conductors tend to "flow" away from clamping torque and can loosen up.
If you are able, measure the voltage at the meter when the event happens because the voltage drop could be at the service, before the meter.
Pre Fab Ideas 3rdgeneration General Electrical Discussion 26 03-31-2009 09:57 PM
Figuring Wattage Auggie56 Services and Service Equipment 7 10-04-2008 07:25 AM
Recommendation: AC lights off of Inverter, or DC rechargeable lights mhl General Electrical Discussion 4 09-30-2008 06:27 AM
Management Ideas calimurray General Electrical Discussion 13 09-13-2008 05:09 PM
Wooden drop lights bigredc222 Vintage Electrical 17 01-25-2008 10:15 PM