Multi Service Grounding - Electrician Talk - Professional Electrical Contractors Forum
Old 03-05-2013, 05:12 PM   #1
Rewards Points: 2,050
Default Multi Service Grounding
If you have a multi unit dwelling (residential) with separate services (existing) and you do a panel changeout and it had no grounding per say. To bring up to code do you run all your grounds to 1 ground rod and water main or keep each service on their own ground rods and water mains (if several to bldg all existing) ??
Old 03-05-2013, 05:32 PM   #2
acebradley's Avatar
Nec 250.58?
acebradley is offline   Reply With Quote
Old 03-05-2013, 05:36 PM   #3
Originally Posted by acebradley
Nec 250.58?
Where an ac system is connected to a grounding electrode in or at a building or structure, the same electrode shall be used to ground conductor enclosures and equipment in or on that building or structure. Where separate services, feeders, or branch circuits supply a building and are required to be connected to a grounding electrode(s), the same grounding electrode(s) shall be used.
Two or more grounding electrodes that are bonded together shall be considered as a single grounding electrode system in this sense.
Old 03-05-2013, 05:54 PM   #4
RePhase277's Avatar
Rewards Points: 3,106
You take 3/0 copper crimped at the weather heads down to the cold water. Tap it to some #6 as it passes the ground rods.
Multi Service Contractors dronai General Electrical Discussion 13 04-25-2012 09:56 PM
multi unit service ToddH General Electrical Discussion 2 02-01-2012 12:10 PM
Multi-family service Magnettica Services and Service Equipment 21 07-26-2011 06:38 PM
400amp multi service, advice please Shockdoc Services and Service Equipment 7 03-21-2010 09:19 AM
Service on Multi Family Dwelling romexrocket Services and Service Equipment 6 10-11-2007 10:24 PM