Old 07-08-2009, 05:52 PM   #1
Send a message via MSN to jayare813
Default neutral after being bonded
Is there a certain distance or circumstance that the neutral and ground wont ring out after being bonded. For example after the mdp the grounding and grounded are still riniging but if we the install another panel from mdp and do not bond the grounded and grounding will it still ring out to the devices, loads, etc.
jayare813 is offline   Reply With Quote
Old 07-08-2009, 06:18 PM   #2
Neutral and ground will always ring out, no matter how many panels you put between you and the MDP, if properly installed. Each subpanel has its own ground wire back to the MDP, where it is bonded to the neutral. Continuity will always be present back to that Main Bonding Jumper.
Old 07-08-2009, 08:31 PM   #3
the only time i have not seen them ring out when in a correct system is on the load side of a tripped gfci
vinster888 is offline   Reply With Quote
Old 07-08-2009, 08:50 PM   #4
Unlimited Lic.Electrician
william1978's Avatar
Yes, they should always ring out.
Old 07-08-2009, 09:04 PM   #5
I agree. Look for corrosion at the the service.
Old 07-08-2009, 09:15 PM   #6
Richard Rowe's Avatar
Yep should ring out, look for a bad jumper or connection. You will find it in th panel somewhere.
Richard Rowe is offline   Reply With Quote
Old 07-08-2009, 10:58 PM   #7
has its own ground wire back to the MDP, Actually not always, It will have a ground conductor (EMT, BX or other metallic raceway). Not necessarily a WIRE.
I void warranty's
Old 07-08-2009, 11:33 PM   #8
You do much hair splitting at work too?
Old 07-08-2009, 11:38 PM   #9
goose134's Avatar
It always sounded like he made a pretty successful career out of it.
Brian, I mean this in the best way.
Old 07-09-2009, 11:23 AM   #10
It is a follow up on that post regarding "do I need to use a EGC conductor in EMT". I knew you knew what you meant. Just an adder.
I knew that.
I void warranty's
Old 07-09-2009, 11:51 AM   #11
Does raise an interesting point for discussion. I never rely on anything except wire to serve as the ground to a sub-panel. In fact, I was probably taught that a sub-panel had to have a four wire feed and just never questioned it.
Old 07-10-2009, 09:20 AM   #12
What do you mean by "ring out"?
Jeff000 is offline   Reply With Quote
Old 07-10-2009, 10:27 AM   #13
A peice of 2 in emt and a peice of # 4 copper what has more surface area?, whats a better path back, as long as its not broken or ate off in the concrete.
I agree emt should have an egc, but the nec dosent require it.
cmec is offline   Reply With Quote
Old 07-10-2009, 10:43 AM   #14
We agree on the use of an EGC. I think the wire is far more reliable and as other design requirements increase its importance, I think the wire should be the norm.
Old 07-10-2009, 04:21 PM   #15
In most commercial applications there are multiple paths for ground return, multiple EMTs, ducts, structural steel, domestic water, sprinkler pipes, rebar in the concrete.
I void warranty's
Old 07-10-2009, 04:31 PM   #16
Thats why we use redundant grounds in healthcare facilities
Old 07-10-2009, 04:44 PM   #17
Ax grinder
raider1's Avatar
Steel conduit is a far superior fault current path than a copper wire.
HERE is a link to the steel tube institute of America. There are a bunch of papers and software programs that show this.
That's why we use redundant grounds in health care facilities
The redundant ground for a health care facility is the insulated copper conductor. The primary ground fault current path is the metallic wiring method itself.
Chris
Old 07-10-2009, 04:53 PM   #18
Chris[/quote]
What I am trying to say is if they are not concerned about noise or transient or gradiant currents,or unequal ground potental its ok to use conduit for an egc.
Old 07-10-2009, 05:04 PM   #19
Chris
What I am trying to say is if they are not concerned about noise or transient or gradiant currents,or unequal ground potental its ok to use conduit for an egc.[/quote]
In 100% of the cases where I have investigated Isolated ground systems (not hospital grounding systems) ALL were improperly installed.
I void warranty's
Old 07-10-2009, 05:43 PM   #20
Brian I think a lot of it has to do with code requirements and how things have evolved, I can rember people driveing seprate ground rods for ig s on cash registers back in the 70 s, then it was out lawed ,its only 2 or 3 code cycles ago we started putting a ground buss and tieing streel pipe etc together.With all the electronics today it gives us work in a recession.
What color neutral? petek57 General Electrical Discussion 63 05-19-2009 01:45 PM
MWB ckt neutral subelect General Electrical Discussion 15 03-06-2009 11:37 AM
120 v in neutral??? lamino69 General Electrical Discussion 10 01-14-2008 10:34 PM
bonded electrician roshia General Electrical Discussion 10 12-18-2007 07:49 AM
Neutral? brian john NEC Code Forum 14 04-10-2007 12:55 PM