Ran a 60 amp underground feeder to detached garage (with new slab). I got the "New" inspector. He red tagged me for this
No main
No ufer ground (see below)
Needs 2 ground rods
Thats it.
They just built this structure about 1 month before I got there. No permits and the GC left town with their money. We don't even know if their is rebar in there. Inpector says I must jackhammer out to rebar (if there is any) and clamp with approved fitting . I said I have nothing to do with this problem. This place was existing when I got there. He said it's under 3 months so it's still considered new construction and it's the electricians responsibility to bond the rebar??
Old 01-05-2012, 07:04 PM   #2
Rewards Points: 25
I could see grounding one way or the other but not both.
Isn't it a sub-panel anyway and grounded at the main panel?
Sencoman is offline   Reply With Quote
Old 01-05-2012, 07:21 PM   #3
animal lover /rat bastard
wildleg's Avatar
Rewards Points: 372
its one or the other. if you put a ufer in you don't need the ground rods. what's this guy smoking ? customer needs to pay you to jackhammer - that's not a big deal. he is being kind of an ahole, tho. customer should call county and complain - that puts you out of it.
Old 01-05-2012, 07:23 PM   #4
Ambassador of Amps
TOOL_5150's Avatar
Rewards Points: 2,114
You only have to hook to a UFER if it is available. It isnt, so run 2 rods in and tell him to pass it. You also need a main [or 6 throws or less] at the structure, no way around that.
I HAVE THE RIGHT TO OFFEND ANYONE I PLEASE. YOU HAVE THE RIGHT TO BE OFFENDED, YOU DO NOT HAVE THE RIGHT TO SHUT ME UP.
The Following 2 Users Say Thank You to TOOL_5150 For This Useful Post:
3xdad (01-06-2012), Magnettica (01-05-2012)
Old 01-05-2012, 07:23 PM   #5
Rewards Points: 272
You still need a main or 6 handles, 2 rods and ???Ufer if the sub panel is in another structure
Old 01-05-2012, 07:35 PM   #6
Jesus Scott
electricmanscott's Avatar
Rewards Points: 232
I beleive it's not "available" it's been changed to "present". If it's there you need to use it. I'm not sure about this specific situation but I don't feel like looking in the book right now and I know somebody else will.
Life is hard
Old 01-05-2012, 07:43 PM   #7
Rewards Points: 1,810
Canadian code would allow the garage to be a sub panel from the main house and not grounded at the garage at all. Our only compulsory ground for an out building would be if the outbuilding houses livestock or if it were on the secondary of an isolation transformer.
Further the 2012 Canadian code only requires a #6 for all low voltage grounding regardless of service capacity. We only require 1 electrode which could be a Ufer, a ground plate, or 2 X 10 foot rods. We have other electrode types but these are the main types.
From my reading of the NEC I don't see where you have to use 2 methods except where 1 electrode is the water pipe.
Old 01-05-2012, 07:45 PM   #8
Professional Nit Picker
manchestersparky's Avatar
Rewards Points: 1,568
The "if available" was the wording in the 2002 NEC.
It was changed in the 2005 to "That are present" and is still written that way in the 2008 and the 2011
What we allow when the CEE was missed or not inspected is, we have the contractor dig a ditch footer depth next to the structure and install a CEE in that ditch. Making sure it is inspected prior to pouring concrete on it.Basically install a footer next to the building just for a CEE
Anything Worth Doing ....
Is Worth Doing Right
Old 01-05-2012, 08:05 PM   #9
evil bastard
mcclary's electrical's Avatar
Rewards Points: 746
No main
Needs 2 ground rods
Thats it.
Buy a Milwaukee sub scanner. It will find metal in concrete up to 6". Here is an "afterthought" bond when I encountered the exact same situation as you.
Old 01-05-2012, 08:07 PM   #10
mbednarik's Avatar
Rewards Points: 1,030
you need a main per 225.32. You at least need rods, inspectors here don't consider floating structures, ones that do not have frost footings, and acceptable ufer ground.
mbednarik is online now   Reply With Quote
Old 01-05-2012, 08:21 PM   #11
Attachment 11176
But how can you guarantee that the rebar you found is 20' continuous or multiple pieces tied together ?
Old 01-05-2012, 08:27 PM   #12
evil bastard
Rewards Points: 746
I could verify length with that Milwaukee. I didn't with the one pictured, because it was a pool bond. I had to bond it no matter what.
Old 01-05-2012, 09:40 PM   #13
Default ?
this guy is new and i'm going to have to deal with him for a real long time. I don't mind putting in a lockable main breaker in the little 30 amp 6 space panel, but, chiseling up the concrete to put in an ufer ground (unless someone pays me) i'm walking off this job. 2 grounds rods..no biggie just to make him happy
Thanks for the tip on scanner. If they pay me, I'll go buy another toy and chisel it out and put in his stinkin concrete pad bond
Old 01-05-2012, 10:07 PM   #14
A Little Short's Avatar
Rewards Points: 76
What about 250.50 Exception:
Exception: Concrete-encased electrodes of existing buildings
or structures shall not be required to be part of the grounding
electrode system where the steel reinforcing bars or rods are
not accessible for use without disturbing the concrete.
The Following User Says Thank You to A Little Short For This Useful Post:
hardworkingstiff (01-05-2012)
Old 01-05-2012, 10:17 PM   #15
Default 3
He said there is a 3 month rule. If it was built within 3 months then it is considered new. I think he is making that up
The Following User Says Thank You to Cletis For This Useful Post:
leland (01-05-2012)
Old 01-05-2012, 10:30 PM   #16
evil bastard
Rewards Points: 746
This is not existing. It's a new build and they got caught. I attended out last code update class, and they blatantly said if you forget it in a pad, or footer, you'll be chipping it back out because they're not gonna let it slide.
electricmanscott (01-06-2012)
Old 01-05-2012, 11:32 PM   #17
mbednarik's Avatar
I would call him out if it is only a 6 circuit panel about the main, providing the feed is not a tap.
Old 01-06-2012, 12:55 AM   #18
sparkie2010's Avatar
Rewards Points: 510
drop a 20' bare wire in the ground or a ring and call it a day.
Ground rods are last resort. If you dont have rebar, water pipe, you would need a ring around the building or 20' bare. And earth test.
Back in the good old days out in FL guys would drop rods with there hands out here. The inspector would want to see the connetion above the ground finish level. So that would mean that the rod is not installed to code 8' in the dirt lol.
Plus when the home owner would cut the grass he would be busting his lawn mower hahah.
Today is a Wonderful DAY!!
http://www.solaristechnology.net
sparkie2010 is offline   Reply With Quote
Old 01-06-2012, 12:59 AM   #19
Rewards Points: 510
Thats crazy but I heard worst
Old 01-06-2012, 01:58 AM   #20
Rewards Points: 2,746
Convince the inspector that they lined the footing with plastic wrap, which would then render the "if present" to void, because if it is insulated from the earth, it's not present. Same goes for coated rebar. P.S. I hate it when inspectors try to get me to install all sorts of workarounds for visqueen plastic under the rebar in slab on grade jobs. Had one ask me to stick a twenty footer under the plastic on the bottom of the footer so it contacted dirt. I tried to point out that an uffer is a "concrete encased electrode" but it was like talking to that congressman that thought placing a marine base at the end of Guam Island would cause it to tip over.
Also the words 20 foot minimum of 1/2" or larger size rebar hangs up several of them. They do not bother to read so they don't understand the tie wire exception in order to achieve 20 foot.
What do you do while waiting for an inspector? kevmanTA General Electrical Discussion 24 06-03-2011 03:13 PM
Inspector Job Opening electricmanscott General Electrical Discussion 2 04-05-2011 09:12 AM
IEC Inspector questions Abrava89 General Electrical Discussion 16 03-09-2011 11:30 PM
Me VS. the Inspector TOOL_5150 General Electrical Discussion 26 08-18-2010 02:24 PM
GEC and Home inspector Michiganboy General Electrical Discussion 3 03-10-2007 08:51 PM