Parallel feeders - Electrician Talk - Professional Electrical Contractors Forum
Old 07-12-2011, 11:10 PM   #1
Default Parallel feeders
I want to size parallel feeders for a 400 amp main breaker panel. Where in the NEC does it give you sufficient information to do this?
Thanks,
Blastphemer
himself is offline   Reply With Quote
Old 07-13-2011, 12:03 AM   #2
erics37's Avatar
Rewards Points: 640
Thanks,
Blastphemer
The NEC assumes that you know how to do it and provides references for the minimum required installation.
Old 07-13-2011, 12:30 AM   #3
RIP 1959-2015
HARRY304E's Avatar
Rewards Points: 1,344
Thanks,
Blastphemer
Table 310.15(B)(16)
310.10
(H) Conductors in Parallel.
(1) General.
Aluminum, copper-clad aluminum, or copper
conductors, for each phase, polarity, neutral, or grounded circuit
shall be permitted to be connected in parallel (electrically
joined at both ends) only in sizes 1/0 AWG and larger where
installed in accordance with 310.10(H)(2) through (H)(6).
Exception No. 1: Conductors in sizes smaller than 1/0
AWG shall be permitted to be run in parallel to supply
control power to indicating instruments, contactors, relays,
solenoids, and similar control devices, or for frequencies of
360 Hz and higher, provided all of the following apply:
(a) They are contained within the same raceway or
cable.
(b) The ampacity of each individual conductor is sufficient
to carry the entire load current shared by the parallel
conductors.
(c) The overcurrent protection is such that the ampacity
of each individual conductor will not be exceeded if one
or more of the parallel conductors become inadvertently
disconnected.
Exception No. 2: Under engineering supervision, 2 AWG
and 1 AWG grounded neutral conductors shall be permitted
to be installed in parallel for existing installations.
Informational Note to Exception No. 2: Exception No. 2 can
be used to alleviate overheating of neutral conductors in existing
installations due to high content of triplen harmonic
currents.
(2) Conductor Characteristics.
The paralleled conductors
in each phase, polarity, neutral, grounded circuit conductor,
equipment grounding conductor, or equipment bonding
jumper shall comply with all of the following:
(1) Be the same length
(2) Consist of the same conductor material
(3) Be the same size in circular mil area
(4) Have the same insulation type
(5) Be terminated in the same manner
Old 07-15-2011, 05:13 PM   #4
Thanks,
Blastphemer
400 amp, I always pull parallel 4/0 and #4 ground in (2) 2" conduits. 3/0 are good for 200amp but 99.9999999% of everthing I do is for motor loads and it covers the 125% factor. Just take the ampacity of the wire and double, triple quadruple.... etc. The only reason I dont run a 3 or 3 1/2" and pull 500MCM is the greenlee 555 (triple nickle) only goes to 2" and the large table bender and threader (for rigid)are a pain in the ass.
MillThug540 is offline   Reply With Quote
Old 07-15-2011, 05:30 PM   #5
child please.....
NolaTigaBait's Avatar
Rewards Points: 14
What's the 125% factor...That seems like a waste of money, if you need a 400 amp ocp device use 2 sets of 3/0 copper, you aren't doing yourself any favors...You would also need a #3 cu ground in each pipe also.
REMOVED
Old 07-15-2011, 05:36 PM   #6
Rewards Points: 480
Thanks,
Blastphemer
Read 310.4 and 300.3 of the 2008 NEC
Old 07-15-2011, 05:39 PM   #7
Chris Kennedy's Avatar
Rewards Points: 2,000
Hows that been working out for ya?
Bulldozers and Dirt
The Following User Says Thank You to Chris Kennedy For This Useful Post:
76nemo (07-15-2011)
Old 07-15-2011, 06:07 PM   #8
Ax grinder
raider1's Avatar
Rewards Points: 1,080
Good question.
Chris
Old 07-15-2011, 06:30 PM   #9
Ok... maybe i need to be more clear for the commercial <electricians>.... 3 phase motor loads that reqrequire a 400amp disconnect and get fused down to whatever the FLA is of the motor ALWAYS get fed with parallel 4/0 and a ground per conduit. Thats.... 3 conductors and a ground per pipe. So if you see something wrong and why it may not work.... please fill me in.
Last edited by Speedy Petey; 07-15-2011 at 07:03 PM. Reason: Remvove offensive comment
Old 07-15-2011, 06:41 PM   #10
child please.....
Rewards Points: 14
Fused down?...Not sure why you need 4/0 cu...It's overkill and not needed for a 400amp ocp device. Your ground size is also too small ...A #4 cu is not large enough. You need a #3 cu in each pipe based on a 400 ocp device...
REMOVED
Old 07-15-2011, 06:42 PM   #11
What?
First of all a 400A feeder with two sets of 3/0 would require a #3 in each conduit. 250.122(F). Secondly, you have increased the ungrounded conductor size. 250.122(B).
Bulldozers and Dirt
Old 07-15-2011, 06:49 PM   #12
B4T
Scotchkote Installer
B4T's Avatar
Rewards Points: 15,378
The Following 2 Users Say Thank You to B4T For This Useful Post:
BuzzKill (07-15-2011), MillThug540 (07-15-2011)
Old 07-15-2011, 07:17 PM   #13
Rewards Points: 480
Mill, what Chris K is talking about is art. 250.122(B). 3/0 is all that is necessary but if you upsize the ungrounded conductors then you must upsize the EGC.
Feeders in conduit subelect NEC Code Forum 2 05-04-2010 06:46 AM
50 amp hot tub feeders myenergy Residential Electrical Forum 21 05-02-2010 09:58 AM
Running feeders for sub CFine Residential Electrical Forum 0 03-31-2010 10:23 PM
Four wire feeders waco General Electrical Discussion 118 03-02-2010 06:30 PM
feeders passing through a building Steve W Services and Service Equipment 14 01-23-2010 05:12 PM