I think the original post is hillarious, and somewhat shameful, but I'll answer it the best way I know how to entertain myself.
Originally Posted by Samar
1) Can I wire room switches, exhaust switches etc along with the receptacles all in the same circuit (120V)?
That's a design issue that the NEC would't prohibit. Is is traditional to keep lighting circuits and receptacle circuits seperate for the most part. Exhaust fans that are typically present in dewllings are sufficiently low loads that they often tag along on a lighting circuit. The over the range exhaust fan often gets a dedicated circuit nowadays, in the event that there's a last minute or later change to an over the range microwave/hood combination.
2) Is there any specific power distribution requirement to wire receptacles in the family room, bed rooms etc? In other words, can I wire all receptacles in a room in one circuit as long as I maintain the conservative total load connected to one circuit breaker (typically I go up to 1440W per circuit)?
There is no limit in the NEC with regard to the number of receptacles on a circuit. No such thing as 180 va per yoke like commercial. You could compliantly wire 1000 receptalces on one circuit if you wanted to in a dwelling, but it would be a bad idea. Since the AFCI requirements came to be, it is traditional to keep the bedroom receptacle circuits seperate from other rooms, so that only the bedroom (and maybe the odd hallway receptacle) are AFCI protected.
3) Do I have to run a separate ground wire for all the wiring? I believe, the residential wiring is done with PVC pipes and therefore a separate ground wire would be required.
Resi is done with Romex cable, typically, and MC cable in the more strict jurisdictions. You get a ground whether you want one or not. Yes, all circuits need a grounding (EGC) by some means or another.
4) What is a typical voltage for a hard wired smoke detector? Can I wire them together with other receptacles also if they are 120V?
Smokes are 120V, and they're typically wired off one of the bedroom circuits, since they are also required to be AFCI protected. If you need more than 12 smokes for the home, then you need to use a low-voltage "fire alarm system" such as you may be used to using in commercial work.
5) For an additional panel for an extension of a residence, do I have to show the utility connection for the new panel and specify and design the wiring schematics of the new panel with the existing panel? If so, what would the drawing look like if the existing panel is 100A and the new panel is also 100A?
Beats me. You'd have to ask your senior engineer what's required in your area.