04-16-2012, 03:51 PM
RTU circuit
I have a rtu mca 100 amps, can I pull 3 #2, #8 grd. and 2 #12 thhn (for recp.) in 1 1/4 " emt? We are under 2008 code.
04-16-2012, 03:52 PM
voltage is 208
04-16-2012, 03:54 PM
The two 12 AWG extra current carrying conductors kills the ampacity of the feeder, but assuming 2 copper you will make it.
04-16-2012, 04:00 PM
Master Electrican
What happened to people doing a few calculations on their own, don't make it so easy on them.
The Following User Says Thank You to sstlouis03 For This Useful Post:
04-16-2012, 04:02 PM
Yes its copper, that would leave me at 104 amps on the 2 AWG after derating is that correct?
04-16-2012, 04:04 PM
I did my own calculatons , just getting a second opinion.
04-16-2012, 04:06 PM
Yes, that was what I came up with.
Of course I am assuming this run is inside the building and not on the roof in the sun.
04-16-2012, 04:08 PM
Electrical Simpleton
Will 250.122(B) have an affect on this install?
Pete
Confidence is the feeling you have before you understand the situation.
04-16-2012, 04:14 PM
Pete
I don't see why it would since I did not have to increase the size of the ungrounded conductors.
04-16-2012, 04:16 PM
Yes its inside .
04-16-2012, 04:18 PM
Assuming your terminations are good for 75 degrees #3 copper would have sufficed based on 100 being the MCA.
Pete
The Following User Says Thank You to Pete m. For This Useful Post:
04-16-2012, 04:23 PM
Pete
Sorry your right , Thanks
04-16-2012, 04:34 PM
Not a problem... just didnt want to see you get hit on inspection.
Pete
04-16-2012, 04:37 PM
Good at being Evil
The two #12s shouldn't count as they will only carry current while the unit is being serviced.
04-16-2012, 04:41 PM
True, it might be easier to just pick up the 120v close and feed unit seperatly.
I'm just hoping to not end up on Electricmanscotts signature line.
04-16-2012, 05:03 PM
Master Electrican
How does 110.14 (c) play into this. It seems to me like he should be using #1.
04-16-2012, 05:11 PM
Well if you interlocked them so only one circuit at a time could be used ....
04-16-2012, 09:45 PM
#18
Should be working
Ahhh..... Got it , but Pete isn't considering the #12's ?
04-16-2012, 09:50 PM
#19
Chief Electron Relocator
What happened to English?
04-17-2012, 08:50 AM
#20