Old 04-17-2012, 11:37 AM   #21
animal lover /rat bastard
wildleg's Avatar
What happened to English?
English who ? I don't recognise that screen name. Is that one of Peter's aliases ?
Old 04-17-2012, 02:34 PM   #22
Why would you run 2 #12 wires? Your feed goes to a disconnect, most service receptacles I see are tapped off the top of that disconnect. Rarely do I ever see a service receptacle run seperately to the RTU.
AFOREMA1 is offline   Reply With Quote
Old 04-17-2012, 03:06 PM   #23
Electrical Simpleton
Pete m.'s Avatar
Originally Posted by dronai View Post
Ahhh..... Got it , but Pete isn't considering the #12's ?
Didn't really need to.
250.122 Size of Equipment Grounding Conductors.
(B) Increased in Size.
Where ungrounded conductors are
increased in size, equipment grounding conductors, where
installed, shall be increased in size proportionately according
to the circular mil area of the ungrounded conductors.
This section doesn't care why you increased the size of the ungrounded conductors.
Pete
Confidence is the feeling you have before you understand the situation.
Pete m. is online now   Reply With Quote
Old 04-17-2012, 03:38 PM   #24
Phosphate Coated as of 05
dronai's Avatar
Pete
310.15 (B) (3)a ?
Old 04-17-2012, 04:20 PM   #25
Pete m.'s Avatar
310.15 (B) (3)a ?
[/left]
I'm not seeing how that has a bearing on the EGC? Unless I am mistaken (and I have made more than one) nothing in 310.15(B)(3)(a) would change the requirement of 250.122(B).
Pete
Old 04-17-2012, 05:06 PM   #26
dronai's Avatar
Pete
Using #1 cu gives you 115A using 90c column, 4 or more conductors using 80% per
310.15 (B) (3) (a) gives you only 92A
Old 04-17-2012, 05:24 PM   #27
Awg-Dawg's Avatar
You sure you arent looking at aluminum conductors?
I'm just hoping to not end up on Electricmanscotts signature line.
Awg-Dawg is online now   Reply With Quote
Old 04-17-2012, 05:33 PM   #28
dronai's Avatar
Using #3 cu gives you 115A using 90c column, 4 or more conductors using 80% per
Sorry #3 cu is what I meant
Old 04-17-2012, 05:34 PM   #29
dronai's Avatar
Assuming your terminations are good for 75 degrees #3 copper would have sufficed based on 100 being the MCA.
Pete
This post is what I'm referring to
Old 04-17-2012, 05:36 PM   #30
Awg-Dawg's Avatar
Sorry #3 cu is waht Pete said to use.
[/left]
I rarely listen to what Pete says either.
Lighting Circuit off of a 32amp Ring Main Circuit? Galileo UK Electrical Forum 4 02-29-2012 05:58 PM
one circuit or two? goose134 PLCs, VFDs, Motors and Controls 7 09-23-2011 06:37 PM
need a new circuit ampman General Electrical Discussion 21 01-26-2011 07:28 PM
6 Drops per 15 A circuit/8 Drops per 20 A circuit. Whats your opinion? romexrocket NEC Code Forum 32 06-11-2010 06:38 AM
240 vs 120 circuit ?????? tlg7mm General Electrical Discussion 4 12-16-2008 06:42 AM