Samsung mini split units - Electrician Talk - Professional Electrical Contractors Forum
Old 11-10-2010, 05:45 PM   #1
Podagrower's Avatar
Rewards Points: 568
Default Samsung mini split units
So, about 23 months ago, I wired a Samsung AQV 18JA mini split unit. Got my money, unit worked fine, everyone was happy.
Today I get a call that its not working right, and it's my fault. Apparently, I was supposed to run shielded cable for the control circuit from the outdoor unit to the indoor unit. I can not find anything in the manual about what kind of wiring needs to be run between the two units.
So, other than telling the customer that it's worked for 2 years and I don't see how it's my problem...
Has anybody else had an issue with a mini split unit needing shielded cable before?
Podagrower is offline   Reply With Quote
Old 11-10-2010, 05:47 PM   #2
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
I just roughed in for one and the supplier supplied 14/7 CT cable, I have seen hack HVAC contractors run 14/4 SJ between units, in the past i have run 12/4 romex.
Old 11-10-2010, 05:49 PM   #3
Rewards Points: 2,000
What do they mean by shielded cable? I usally don't run the wire for the control circuit,the HVAC guy does but they always run 14/3 rx for it.
robnj772 is offline   Reply With Quote
Old 11-10-2010, 06:01 PM   #4
Podagrower's Avatar
Rewards Points: 568
For the mini splits, somehow the cabling between the outside unit and inside unit has become the electricians problem in our area. I don't mean standard thermostat wiring. After you land the 208 at the outdoor unit, you need to take 208, and 2 or 3 other wires (depending on the unit) to the indoor unit. The 2 or 3 wires are varying voltages.
Old 11-10-2010, 06:05 PM   #5
Rewards Points: 25
From my understanding, and I may be wrong, but the cabling from outside in is done in 14ga with 3 conductors. I've seen it done with 14/3 romex 99% of the time sleeved thru carflex. And isn't the voltage converted to DC on the indoor unit?
heartlessmcfly is offline   Reply With Quote
Old 11-10-2010, 06:07 PM   #6
Yea,that is what is done around here.
Old 11-10-2010, 07:20 PM   #7
...NM romex is not rated for wet locations even if installed in rigid conduit and sealtite
voltz is offline   Reply With Quote
Old 11-10-2010, 07:26 PM   #8
Ambassador of Amps
TOOL_5150's Avatar
Rewards Points: 2,126
If I wire my outdoor speakers with romex, did I create a code violation?
~matt
Old 11-10-2010, 07:29 PM   #9
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
The "thhn" inside romex is the same "thhn" wire that is in MC. Who's to say that stripping back the plastic sheath and installing a transition to where romex enters the outside relm is not code compliant?
Old 11-10-2010, 07:35 PM   #10
thhn is not rated for outdoor use, thwn is. See table 310.13(A) look up thhn and look under the application provisions column 08 code page 142
As side note, often the wire is dual rated thhn/thwn, you have to check
Old 11-10-2010, 07:41 PM   #11
kbsparky's Avatar
Rewards Points: 1,000
Conductors inside of romex are not labeled, nor are they dual-rated.
-KB
Old 11-10-2010, 07:45 PM   #12
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
It's hard to say or prove anything since 9 out of 10 times, the conductors inside MC and NM cables are unmarked. On a sidenote, I just ran 14/3 NM in PVC to an outdoor ceiling fan mounted under a deck. Where is water going to enter my conduit system? Yes in the old days of sleeving EMT with sill plates I can see the need for UF use but certain applications should not require a transition to UF. I do't know of any inspector who will drop my fan to ensure I used UF anyway, the don't even open up devices on me.
Old 11-10-2010, 07:47 PM   #13
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
They are the same that is used in MC, strip open both cables and compare. Question is, what type of conductor is it?
Old 11-10-2010, 07:52 PM   #14
Ok well I only stated that the HVAC guys use 14/3,When I have to run that particular wire I use UF
BUT
The rx in a wet location is a different debate and isn't going to solve the OP's problem.
Old 11-10-2010, 07:55 PM   #15
Florida resident
ampman's Avatar
Location: Florida , if your not here you're somewhere else
Rewards Points: 1,604
12/4 romex i've never heard it called that
for lunch I had three cans of alphabet soup then afterwards I had a huge vowel movement
ampman is offline   Reply With Quote
Old 11-10-2010, 08:07 PM   #16
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
12/4 w ground, 14/4 w/ ground , red,white, black, blue and bare ground. Lately the stock has been white black, red, wht/red tracer w/ bare ground. Where have you been ?
Old 11-10-2010, 08:10 PM   #17
felonious smile.
Shockdoc's Avatar
Rewards Points: 572
BUT
The 14 CT cable that came with my current install is a good product to use. Now here is a question, Inside unit is over 6' in hieght off floor, does it require a disconnect below 6'. I have gotten two sides to this one, I personaly wire it straight from the outside unit.
Old 11-10-2010, 08:30 PM   #18
Rewards Points: 25
I've never put a means of a disconnect on the indoor unit
Old 11-10-2010, 08:32 PM   #19
Rewards Points: 1,464
Does the abreviation rx mean nm/romex?
Old 11-10-2010, 09:41 PM   #20
Ambassador of Amps
TOOL_5150's Avatar
I am betting so, because it is so hard to type romex - or nm
~Matt
Makita's new mini drill 10.8v twintask Tools, Equipment and New Products 3 01-05-2012 01:36 AM
Here's one for you mini/twin haters electricmanscott General Electrical Discussion 83 05-22-2010 02:02 AM
Mini Split AC condensing units treated the same as central AC? TagYoureIt Off Topic (Non Trade) 8 05-05-2010 07:47 PM
Have you used them, mini breaker fuses?? brother General Electrical Discussion 9 11-29-2009 05:20 PM
Ridgid mini-me drill... Mackie Tools, Equipment and New Products 5 07-02-2008 05:56 AM