Old 11-11-2009, 06:40 AM   #1
Tallman
Default Sizing conduit for long pull
I'm gearing up to pull almost 500' of 250kcmil aluminum through pvc conduit. Other than the steel sweeps at both ends the path is pretty straight, dipping down in the middle and gently sweeping across the driveway to the house. Can anybody out there recommend, based on their experience, the minimum conduit diameter that should keep me out of trouble? I'm hoping to be able to do it with manpower alone, maybe 3 or 4 guys. Is that ridiculous?
The cable will be 250,250,3/0 URD,USE and a #2 XHHW EGC
bharbwyr is offline   Reply With Quote
Old 11-11-2009, 08:53 AM   #2
Seen your member
The legth of a run makes no difference as far as the NEC is concerned. As long as raceway requirements are met, that's all you need.
If it's a going concern for you, up it one trade size.
Old 11-11-2009, 08:57 AM   #3
ADMIRAL STARFLEET COMMAND
BEAMEUP's Avatar
Still need more info to give you a proper answer. Is this for a service or a feeder? If you are putting it in a pipe I wouldn't use URD, I would go XHHW for all conductors. URD will be a pain to pull thru a pipe.
BEAMEUP is online now   Reply With Quote
Old 11-11-2009, 09:18 AM   #4
Tallman
This is a feeder from the metermain to the house. I know that the URD is stiffer than the XHHW, but it seems that perhaps, as it comes "pre-assembled", it will be less likely to form the kinks that may occur while wrangling four separate conductors.
Old 11-11-2009, 09:22 AM   #5
Seen your member
Order you four seperate conductors on reels and get a reel stand.
Old 11-11-2009, 09:25 AM   #6
Podagrower's Avatar
XHHW insulation does not get nicked up as easily as THHN/THWN insulation, but XHHW does not pull as easily.
The NEC sometimes shows what conductors will fit in a pipe, but that doesn't mean you can pull it. For a pull this long, I would be looking for a place or thing to attach a pulley overhead and use some mechanical advantage to pull (even pulling down by hand beats pulling up).
http://joecartoon.atom.com/cartoons/channel/6-
press_n_splode/page/2/order/rating
Bring back the classics........
Podagrower is offline   Reply With Quote
Old 11-11-2009, 10:05 AM   #7
I'd go with a 3" PVC.
It's bigger than you need, but the sweeps are bigger, allows for bigger conductors in the future, and the cost is very minimal.
You're nuts to think you can pull 500' by hand. Can you drag the 500' reel on the ground? Now add the 2 90s.
Buy a small tugger. It'll be the best $2500 you ever spent.
heel600 is offline   Reply With Quote
Old 11-11-2009, 10:59 AM   #8
Default Wire pull
Also get plenty of wire pulling compound. Don't forget RELIEF pull boxes.
Old 11-11-2009, 11:19 AM   #9
sparks134's Avatar
Get plenty of sleep, dont forget to eat your wheatys and pull it by hand!!!
sparks134 is offline   Reply With Quote
Old 11-11-2009, 11:24 AM   #10
Default Loong wire pull
Would you feel it is necessary to BOND TO GROUND the steel sweeps. If so, how would you go about it?
Old 11-11-2009, 11:26 AM   #11
sparks134's Avatar
Hell No!!!
Old 11-11-2009, 11:36 AM   #12
Default Long Pull
Originally Posted by sparks134 View Post
Hell No!!!
Are you saying that it is not necessary, or are you saying that you just are not going to do it?
Old 11-11-2009, 11:38 AM   #13
sparks134's Avatar
i dont think you need to, but not sure!
Old 11-11-2009, 11:42 AM   #14
Well, I agree with the other suggestions about using XXHW on spools. You should be able to rent a puller or tugger if buying one is not feasible. Use lots of lube (do not use yellow lube, bad stuff) install the 2.5" or 3" conduit. Did you do a voltage drop calc.? Thats a long pull. Buy the way is it possible to install the meter closer to the house so the utility will make the long pull instead of you?
David Channell SSE
Old Spark is offline   Reply With Quote
Old 11-11-2009, 11:43 AM   #15
A ground rod.
David Channell SSE
Old 11-11-2009, 11:46 AM   #16
In California, the steel sweeps do have to be bonded. In the transformer we have to use a ground rod, at the panel its easy.
Old 11-11-2009, 11:48 AM   #17
Seen your member
So if I run PVC underground, and use steel sweeps to prevent the PVC ones from getting sawn along the insides from the rope, how do I bond them?
Old 11-11-2009, 11:56 AM   #18
You need to install grounding bushings on the open ends of the steel sweeps. I they are not open because you have nipples or conduit continuing, the be sure to use steel nipples not pvc. When you finally terminate, then use the grounding (bonding) bushing. It is metal with a ground clamp attached. We have to use this on all underground metal conduits in Calif.
David Channell
Old 11-11-2009, 12:00 PM   #19
sparks134's Avatar
i'm not following!!!???
Old 11-11-2009, 12:01 PM   #20
Seen your member
So instead of using 10,000 feet of PVC with steel sweeps for lights in a mall parking lot, I now have to pay for all steel raceways just to bond my sweeps?
I'll cite 250.86 Exc. 3 before I do that.
Electrical panel in conduit as pull box??? sparks134 Residential Electrical Forum 43 11-15-2009 11:25 PM
Does a pull box need to be grounded? jayare813 General Electrical Discussion 31 11-11-2009 08:18 PM
Conduit Sizing 23027 General Electrical Discussion 15 03-19-2009 10:36 PM
Pull box size Tonyv General Electrical Discussion 13 03-01-2009 12:28 PM
Pull box subelect NEC Code Forum 15 05-02-2008 10:20 PM