Old 07-18-2009, 11:11 PM   #1
KEI
Default Square d circuit breakers
Does anyone know if Square D Homeline has a circuit breaker that trips at 100% of its rating?
KEI is offline   Reply With Quote
Old 07-18-2009, 11:45 PM   #2
lectro88's Avatar
what are you attempting?
lectro88 is offline   Reply With Quote
Old 07-18-2009, 11:59 PM   #3
Seen your member
If you let a CB run at it's rated amperage long enough, it may or may not trip.
Old 07-19-2009, 12:18 AM   #4
KEI
I have # 10 feeding a 27A Load. 2P 30A Breaker will trip at 80%. The wire has a 35A ampacity, but is supposed to be protected by a 30A Breaker. 80% of 30 is 24, Is it acceptable to use a 40A breaker? 80% of 40 is 32, which is within its ampacity rating. If I could find a 30A breaker that trips at 100 %, my problem is solved.
Old 07-19-2009, 12:21 AM   #5
Licensed RAT
robnj772's Avatar
robnj772 is online now   Reply With Quote
Old 07-19-2009, 01:53 AM   #6
lectro88's Avatar
The 35a only applies to motors, welders, cranes and special applications permitted by code only. see article 240* I would NOT use a 40. try this math 35 x 80% or 35 x .8 This is Not for general purpose loads. General purpose max overcurrent for #10 is 30a. read it carefully
Old 07-19-2009, 02:08 AM   #7
lectro88's Avatar
Is this for an air conditioner ? or general purpose multi outlet, or dedicated
Old 07-19-2009, 02:54 AM   #8
Licensed Pro
Magnettica's Avatar
27 amps protected by a 30 amp breaker will be fine until it's running at full amperage for 3 hours or more.
Article 100 Definitions
Continuous Load. A load where the maximum current is
expected to continue for 3 hours or more.
Old 07-19-2009, 07:53 AM   #9
KEI
This is for a dedicated lighting circuit
Old 07-19-2009, 08:32 AM   #10
If the breaker is tripping, it might be bad or you might have a bad fixture/ballast on the circuit. Megger the circuit first. A 30 amp breaker will hold 27 amps forever. It will hold 32 amps forever, for that matter, unless the breaker itself is located in a very hot ambient.
Old 07-19-2009, 09:25 AM   #11
KEI
the breaker is not tripping, this is a dedicated outdoor lighting circuit the load is 27.8A. I have #10 feeding them, I am concerned if I protect the circuit with a 30A cb, it may trip. I have always been told that a circuit breaker will trip at 80 % of it rating, is that correct?
Old 07-19-2009, 09:27 AM   #12
No, that's not true at all. Get on Square D's website and take a look at the trip curve for a 30 amp breaker.
In a non-dwelling setting, you're not allowed to load a circuit beyond 80% if the load is continuous. That has nothing to do with the breaker tripping, though.
Old 07-19-2009, 09:32 AM   #13
KEI
what do you think, would you feel comfotable putting this load on a 30 A Breaker........I don't want it to trip 1/2 way through a game.
Old 07-19-2009, 09:34 AM   #14
I'm not convinced that you even have a choice at this point. Is there individual overcurrent protection in each light standard or ballast box?
You really an electrician?
Old 07-19-2009, 09:37 AM   #15
KEI
There are 4 fixtures per breaker, 1500W each 240V 1PH
Old 07-19-2009, 09:38 AM   #16
KEI
where is the trip curve table?
Old 07-19-2009, 09:49 AM   #17
Click here.
Old 07-19-2009, 09:50 AM   #18
KEI
Yeah, I'm an electrician, i am just askin some questions, to make sure all my bases are covered.
Old 07-19-2009, 09:54 AM   #19
lectro88's Avatar
To be code compliant for lighting, 27 x 125% = 33.75 Needs to be #8 and 35a breaker. If I remember correctly its 1.25 for each light. (help me out guys) right ?
Old 07-19-2009, 09:54 AM   #20
I think Marc asked this question in part because of this statement, among others:
I am sure others are thinking this as well.
Molded Case Circuit Breakers Magic Electric UK Electrical Forum 3 07-11-2009 06:40 AM
lightning and circuit breakers nrp3 General Electrical Discussion 8 05-29-2009 09:26 PM
Kirk keying circuit breakers heath Services and Service Equipment 2 02-18-2009 05:36 PM
Square or hex impact? Mackie Tools, Equipment and New Products 12 10-02-2008 08:09 AM
Square D won't fit? k2x General Electrical Discussion 13 06-04-2008 07:34 PM