Originally Posted by ElectricBill
Thanks for the bolt torque tables.
I got the okay to inspect the system. It is 120/208V breaker sitting in a 1600A switch gear.
SFHA36AT0250
SFHA is the type, 3 is 3 phase, 6 is 600V, AT250 is the frame size. With a 200A rating plus in 1600A gear this is a misapplied breaker.
If you look at the photo link in the OP you can see the oxidation/residue build up that triggered the investigation. It was taken with a cell phone so I hope it is clear enough. If needed I can post clearer pictures.
Since my OP I found another breaker with similar oxidation build up. This prompted me to make a call to GE breaker support line which inturn got me in touch with the Spectra breaker project manager. I was impressed with the quick response from GE.
GE's claim is that the residue build up is the result of a flame retardant additive used in the breaker case which is reacting for some unknown reason and causing the oxidation/residue.What they don't explain is why is it happening only near the rating plug. These breakers are 10 years old at this point.
GE has some production issues 10 years ago with a lack of anti oxidants on thier circuit boards, that could be part of the issue. Another possible issue would be a sulphur rich atmosphere, maybe a paper mill?
GE claims that this problem has been seen a lot but that there is no evidence from their testing that the residue build up affecs breaker operations in anyway. I opened the switch gear and found the connected load and wire terminations okay. I did not pull the rating plug out yet since that would require a shut down.
This breaker needs to be tested to ensure it is operating properly.