Old 02-02-2012, 10:04 PM   #1
Senior Member
 
Join Date: Dec 2009
Location: NJ
Posts: 837
Rewards Points: 500
Default Third Party Inteterlock Kit

That are sold on http://www.interlockkit.com/ are UL tested but not UL listed and was told by a buddy of mine that a inspector could fail them with no questions asked? Just wondering if anyone here ever had one of these installs shot down?
Gamit is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!

Old 02-02-2012, 10:10 PM   #2
crispy critter
 
green light's Avatar
 
Join Date: Oct 2011
Location: west coast 45th parallel
Posts: 1,826
Rewards Points: 1,002
Default

Ive installed 50 or so... never been "shut down" by inspector
__________________
I'm old enough to know better, but too young to care.
green light is offline   Reply With Quote
Old 02-02-2012, 10:20 PM   #3
WWMDSD
 
Oakey's Avatar
 
Join Date: Feb 2009
Location: New Jersey
Posts: 152
Rewards Points: 89
Default

No problems here
Oakey is offline   Reply With Quote
Old 02-03-2012, 01:11 AM   #4
Senior Member
 
J. Temple's Avatar
 
Join Date: Dec 2011
Location: California
Posts: 159
Rewards Points: 77
Default

I've installed about a dozen and never had any problems.
J. Temple is offline   Reply With Quote
Old 02-03-2012, 01:16 AM   #5
Wire Ninja
 
MDShunk's Avatar
 
Join Date: Jan 2007
Location: Beautiful Cumberland Valley, in PA
Posts: 17,358
Rewards Points: 2,106
Default

The inspector would have to pull something from the NEC that requires that they be listed. I fail to see that requirement. Remember, after all, the UL is just a company. Not the government.

It could simply be that they are UL tested just to prove to some hard ass inspectors that they have been examined by the UL. They probably aren't listed because I can't seem to find a UL White Book category they'd fit in.
__________________
One reason not to give DIY advice:
Catch a man a fish and you can sell it to him.
Teach a man to fish and you’ve ruined a good business opportunity.
MDShunk is offline   Reply With Quote
Old 02-03-2012, 07:13 AM   #6
Jesus Scott
 
electricmanscott's Avatar
 
Join Date: Feb 2010
Location: Massachusetts
Posts: 9,232
Default

Quote:
Originally Posted by Gamit View Post
That are sold on http://www.interlockkit.com/ are UL tested but not UL listed and was told by a buddy of mine that a inspector could fail them with no questions asked? Just wondering if anyone here ever had one of these installs shot down?
The inspector should ask questions before he makes himself look like an idiot.
http://www.interlockkit.com/MasterElectric5243101.pdf
__________________
Quote:
Originally Posted by 360max View Post
I wish Mayor Bloomberg would bankroll Obama, so we can get the law changed, so Obama can run for a third term.
electricmanscott is offline   Reply With Quote
The Following 2 Users Say Thank You to electricmanscott For This Useful Post:
76nemo (04-02-2012), leland (02-03-2012)
Old 02-03-2012, 12:00 PM   #7
Senior Member
 
Join Date: Jul 2010
Location: IL
Posts: 2,531
Rewards Points: 1,114
Default

Some inspectors reject all interlock kits because they are not listed as transfer equipment and 702.5 requires transfer equipment. In my opinion the interlock kits provide the require functions of manual transfer equipment, but not all agree.
don_resqcapt19 is offline   Reply With Quote
Old 02-03-2012, 07:44 PM   #8
Senior Member
 
Join Date: Dec 2009
Location: NJ
Posts: 837
Rewards Points: 500
Default

Quote:
Originally Posted by don_resqcapt19
Some inspectors reject all interlock kits because they are not listed as transfer equipment and 702.5 requires transfer equipment. In my opinion the interlock kits provide the require functions of manual transfer equipment, but not all agree.
How could SOME inspectors reject it? It's either code compliant or not?
Gamit is offline   Reply With Quote
Old 02-03-2012, 07:49 PM   #9
976-EVIL
 
mcclary's electrical's Avatar
 
Join Date: Feb 2009
Location: State of Euphoria
Posts: 14,654
Rewards Points: 2,002
Default

Quote:
Originally Posted by don_resqcapt19 View Post
Some inspectors reject all interlock kits because they are not listed as transfer equipment and 702.5 requires transfer equipment. In my opinion the interlock kits provide the require functions of manual transfer equipment, but not all agree.

Don, wouldn't the exception apply here?:



(1) Manual Transfer Equipment.
Where manual transfer
equipment is used, an optional standby system shall have
adequate capacity and rating for the supply of all equipment
intended to be operated at one time. The user of the
optional standby system shall be permitted to select the

load connected to the system.



Exception: Temporary connection of a portable generator
without transfer equipment shall be permitted where conditions
of maintenance and supervision ensure that only
qualified persons service the installation and where the
normal supply is physically isolated by a lockable disconnecting
means or by disconnection of the normal supply
conductors.
mcclary's electrical is online now   Reply With Quote
Old 02-03-2012, 07:53 PM   #10
Senior Member
 
Bulldog1's Avatar
 
Join Date: Oct 2011
Location: No where, USA
Posts: 2,367
Rewards Points: 1,000
Default

Quote:
Originally Posted by MDShunk View Post
The inspector would have to pull something from the NEC that requires that they be listed. I fail to see that requirement. Remember, after all, the UL is just a company. Not the government.

It could simply be that they are UL tested just to prove to some hard ass inspectors that they have been examined by the UL. They probably aren't listed because I can't seem to find a UL White Book category they'd fit in.

I was told our state requires 3rd party listing or AHJ approval for all electrical equipment installed by my continuing ed instructor.
Bulldog1 is offline   Reply With Quote
Old 02-03-2012, 07:58 PM   #11
Senior Member
 
Join Date: Jul 2010
Location: IL
Posts: 2,531
Rewards Points: 1,114
Default

Quote:
Originally Posted by mcclary's electrical View Post
Don, wouldn't the exception apply here?:



(1) Manual Transfer Equipment.
Where manual transfer
equipment is used, an optional standby system shall have
adequate capacity and rating for the supply of all equipment
intended to be operated at one time. The user of the
optional standby system shall be permitted to select the

load connected to the system.



Exception: Temporary connection of a portable generator
without transfer equipment shall be permitted where conditions
of maintenance and supervision ensure that only
qualified persons service the installation and where the
normal supply is physically isolated by a lockable disconnecting
means or by disconnection of the normal supply
conductors.
That exception never applies, in my opinion, to a dwelling unit and it only applies to the connection to a portable generator.
don_resqcapt19 is offline   Reply With Quote
Old 02-03-2012, 08:00 PM   #12
Senior Member
 
Join Date: Jul 2010
Location: IL
Posts: 2,531
Rewards Points: 1,114
Default

Quote:
Originally Posted by Gamit View Post
How could SOME inspectors reject it? It's either code compliant or not?
Based on the code wording all inspectors should reject it. The device is not "transfer equipment".

The inspectors that accept it understand what the code rule is asking for and permit these types of devices because the provide the function of transfer equipment even though they are not listed as such.
don_resqcapt19 is offline   Reply With Quote
Old 02-03-2012, 10:30 PM   #13
Jesus Scott
 
electricmanscott's Avatar
 
Join Date: Feb 2010
Location: Massachusetts
Posts: 9,232
Default

Quote:
Originally Posted by Bulldog1 View Post
I was told our state requires 3rd party listing or AHJ approval for all electrical equipment installed by my continuing ed instructor.
Install it yourself then.
__________________
Quote:
Originally Posted by 360max View Post
I wish Mayor Bloomberg would bankroll Obama, so we can get the law changed, so Obama can run for a third term.
electricmanscott is offline   Reply With Quote
The Following 2 Users Say Thank You to electricmanscott For This Useful Post:
Bulldog1 (02-07-2012), CraigV (04-02-2012)
Old 02-03-2012, 11:57 PM   #14
Senior Member
 
Join Date: Dec 2007
Location: Massachusetts
Posts: 3,366
Rewards Points: 2,008
Default

Quote:
Originally Posted by Oakey View Post
No problems here

No Permit- No Problem.

Seriously: who here pulls a permit for such a 'project'?

Not that I'm afraid of permits- But.... after the running around and scheduling inspections.... add 2 hrs-Real time- to the project-
You lost any and all profit.... And....

The inspector would probably be a Tadd irritated.

Messed up their lunch.......
leland is online now   Reply With Quote
The Following User Says Thank You to leland For This Useful Post:
electricmanscott (02-07-2012)
Old 02-07-2012, 09:08 PM   #15
Senior Member
 
Join Date: Dec 2009
Location: NJ
Posts: 837
Rewards Points: 500
Default

Another one today
Attached Images
File Type: jpg image-3862948796.jpg (109.2 KB, 38 views)
File Type: jpg image-742503026.jpg (86.8 KB, 32 views)
Gamit is offline   Reply With Quote
Old 02-07-2012, 10:28 PM   #16
NJ-IEC Member
 
Magnettica's Avatar
 
Join Date: Jan 2007
Location: Rahway, NJ
Posts: 14,185
Rewards Points: 42
Default

Looks good... but why did you put the PB30 inside the house/ garage?

I know it's rated for indoor/ outdoor use but I figured it's best to put it outside so no one would ever start the generator indoors.

What do you think?
__________________
Replies based on NEC 2014
Magnettica is offline   Reply With Quote
Old 02-07-2012, 10:34 PM   #17
Senior Member
 
Join Date: Dec 2009
Location: NJ
Posts: 837
Rewards Points: 500
Default

Quote:
Originally Posted by Magnettica
Looks good... but why did you put the PB30 inside the house/ garage?

I know it's rated for indoor/ outdoor use but I figured it's best to put it outside so no one would ever start the generator indoors.

What do you think?
I had a extra so used it. As far as putting it outside this particular customer actually wanted it inside? The panel is about 3 feet from the door and explained that the reason you bought a 20 foot cord is to put gen outside.
Gamit is offline   Reply With Quote
Old 02-07-2012, 10:46 PM   #18
Senior Member
 
Join Date: Dec 2009
Location: NJ
Posts: 837
Rewards Points: 500
Default

Quote:
Originally Posted by Magnettica
Looks good... but why did you put the PB30 inside the house/ garage?

I know it's rated for indoor/ outdoor use but I figured it's best to put it outside so no one would ever start the generator indoors.

What do you think?
I also did one about a month ago that was actually in the basement. I did not have it inspected do you think it would of passed? The HO had a 40 foot cord and window close by.
Gamit is offline   Reply With Quote
Old 02-07-2012, 10:48 PM   #19
Senior Member
 
Join Date: Sep 2009
Location: kentucky
Posts: 10,158
Rewards Points: 698
Default

Quote:
Originally Posted by Gamit View Post
That are sold on http://www.interlockkit.com/ are UL tested but not UL listed and was told by a buddy of mine that a inspector could fail them with no questions asked? Just wondering if anyone here ever had one of these installs shot down?
Does UL tested mean that they passed?
RIVETER is offline   Reply With Quote
Old 02-07-2012, 11:07 PM   #20
NJ-IEC Member
 
Magnettica's Avatar
 
Join Date: Jan 2007
Location: Rahway, NJ
Posts: 14,185
Rewards Points: 42
Default

Quote:
Originally Posted by Gamit View Post
I also did one about a month ago that was actually in the basement. I did not have it inspected do you think it would of passed? The HO had a 40 foot cord and window close by.
It should have passed. The PB30 and PNB30 are rated for indoor/outdoor use. It's in the paperwork in case you were wondering.

I saw the Cutler-Hammer CH EmGen prewired panel for the first time today. It's a lot like the Reliance brand except it's not a piece of crap like Reliance breakers are. The only thing I didn't like was the inlet built-in to the panel.

__________________
Replies based on NEC 2014
Magnettica is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lien 3rd Party Cletis Business, Marketing, and Sales 2 10-27-2011 11:57 PM
AZ qualifying party ryno General Electrical Discussion 3 08-12-2011 10:38 PM
Halloween party erics37 Off Topic 44 10-25-2010 02:39 PM
New Year's Eve party playlist Thomps Off Topic 15 12-31-2009 07:30 PM
Anybody go to a Tea Party? Minuteman Off Topic 72 04-23-2009 10:18 PM


All times are GMT -4. The time now is 01:24 AM.


Our Pro Sites Network
ContractorTalk.com | DrywallTalk.com | HVACSite.com | PaintTalk.com | PlumbingZone.com | RoofingTalk.com