That are sold on http://www.interlockkit.com/ are UL tested but not UL listed and was told by a buddy of mine that a inspector could fail them with no questions asked? Just wondering if anyone here ever had one of these installs shot down?
|
|
|
Join the #1 Electrician Forum Today - It's Totally Free!
ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!
Join ElectricianTalk.com - Click Here

|
Warning: The topics covered on this site include activities in which there exists the potential for serious injury
or death. ElectricianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
02-02-2012, 09:10 PM
|
#2
|
|
crispy critter
Join Date: Oct 2011
Location: west coast 45th parallel
Posts: 1,564
|
Ive installed 50 or so... never been "shut down" by inspector
__________________
I'm old enough to know better, but too young to care.
|
|
|
02-02-2012, 09:20 PM
|
#3
|
|
Member
Join Date: Feb 2009
Location: New Jersey
Posts: 80
|
No problems here
|
|
|
02-03-2012, 12:11 AM
|
#4
|
|
Senior Member
Join Date: Dec 2011
Location: California
Posts: 113
|
I've installed about a dozen and never had any problems.
|
|
|
02-03-2012, 12:16 AM
|
#5
|
|
Wire Ninja
Join Date: Jan 2007
Location: Beautiful Cumberland Valley, in PA
Posts: 16,794
|
The inspector would have to pull something from the NEC that requires that they be listed. I fail to see that requirement. Remember, after all, the UL is just a company. Not the government.
It could simply be that they are UL tested just to prove to some hard ass inspectors that they have been examined by the UL. They probably aren't listed because I can't seem to find a UL White Book category they'd fit in.
__________________
One reason not to give DIY advice:
Catch a man a fish and you can sell it to him.
Teach a man to fish and you’ve ruined a good business opportunity.
|
|
|
02-03-2012, 06:13 AM
|
#6
|
|
not a union thug
Join Date: Feb 2010
Location: Massachusetts
Posts: 7,030
|
Quote:
Originally Posted by Gamit
That are sold on http://www.interlockkit.com/ are UL tested but not UL listed and was told by a buddy of mine that a inspector could fail them with no questions asked? Just wondering if anyone here ever had one of these installs shot down?
|
The inspector should ask questions before he makes himself look like an idiot.
http://www.interlockkit.com/MasterElectric5243101.pdf
|
|
|
|
The Following 2 Users Say Thank You to electricmanscott For This Useful Post:
|
|
02-03-2012, 11:00 AM
|
#7
|
|
Senior Member
Join Date: Jul 2010
Location: IL
Posts: 1,446
|
Some inspectors reject all interlock kits because they are not listed as transfer equipment and 702.5 requires transfer equipment. In my opinion the interlock kits provide the require functions of manual transfer equipment, but not all agree.
|
|
|
02-03-2012, 06:44 PM
|
#8
|
|
Senior Member
Join Date: Dec 2009
Location: NJ
Posts: 756
|
Quote:
|
Originally Posted by don_resqcapt19
Some inspectors reject all interlock kits because they are not listed as transfer equipment and 702.5 requires transfer equipment. In my opinion the interlock kits provide the require functions of manual transfer equipment, but not all agree.
|
How could SOME inspectors reject it? It's either code compliant or not?
|
|
|
02-03-2012, 06:49 PM
|
#9
|
|
976-EVIL
Join Date: Feb 2009
Location: State of Euphoria
Posts: 13,408
|
Quote:
Originally Posted by don_resqcapt19
Some inspectors reject all interlock kits because they are not listed as transfer equipment and 702.5 requires transfer equipment. In my opinion the interlock kits provide the require functions of manual transfer equipment, but not all agree.
|
Don, wouldn't the exception apply here?:
(1) Manual Transfer Equipment. Where manual transfer
equipment is used, an optional standby system shall have
adequate capacity and rating for the supply of all equipment
intended to be operated at one time. The user of the
optional standby system shall be permitted to select the
load connected to the system.
Exception: Temporary connection of a portable generator
without transfer equipment shall be permitted where conditions
of maintenance and supervision ensure that only
qualified persons service the installation and where the
normal supply is physically isolated by a lockable disconnecting
means or by disconnection of the normal supply conductors.
|
|
|
02-03-2012, 06:53 PM
|
#10
|
|
Senior Member
Join Date: Oct 2011
Location: No where, USA
Posts: 2,346
|
Quote:
Originally Posted by MDShunk
The inspector would have to pull something from the NEC that requires that they be listed. I fail to see that requirement. Remember, after all, the UL is just a company. Not the government.
It could simply be that they are UL tested just to prove to some hard ass inspectors that they have been examined by the UL. They probably aren't listed because I can't seem to find a UL White Book category they'd fit in.
|
I was told our state requires 3rd party listing or AHJ approval for all electrical equipment installed by my continuing ed instructor.
|
|
|
02-03-2012, 06:58 PM
|
#11
|
|
Senior Member
Join Date: Jul 2010
Location: IL
Posts: 1,446
|
Quote:
Originally Posted by mcclary's electrical
Don, wouldn't the exception apply here?:
(1) Manual Transfer Equipment. Where manual transfer
equipment is used, an optional standby system shall have
adequate capacity and rating for the supply of all equipment
intended to be operated at one time. The user of the
optional standby system shall be permitted to select the
load connected to the system.
Exception: Temporary connection of a portable generator
without transfer equipment shall be permitted where conditions
of maintenance and supervision ensure that only
qualified persons service the installation and where the
normal supply is physically isolated by a lockable disconnecting
means or by disconnection of the normal supply conductors.
|
That exception never applies, in my opinion, to a dwelling unit and it only applies to the connection to a portable generator.
|
|
|
02-03-2012, 07:00 PM
|
#12
|
|
Senior Member
Join Date: Jul 2010
Location: IL
Posts: 1,446
|
Quote:
Originally Posted by Gamit
How could SOME inspectors reject it? It's either code compliant or not?
|
Based on the code wording all inspectors should reject it. The device is not "transfer equipment".
The inspectors that accept it understand what the code rule is asking for and permit these types of devices because the provide the function of transfer equipment even though they are not listed as such.
|
|
|
02-03-2012, 09:30 PM
|
#13
|
|
not a union thug
Join Date: Feb 2010
Location: Massachusetts
Posts: 7,030
|
Quote:
Originally Posted by Bulldog1
I was told our state requires 3rd party listing or AHJ approval for all electrical equipment installed by my continuing ed instructor.
|
Install it yourself then.
|
|
|
|
The Following 2 Users Say Thank You to electricmanscott For This Useful Post:
|
|
02-03-2012, 10:57 PM
|
#14
|
|
Senior Member
Join Date: Dec 2007
Location: Massachusetts
Posts: 3,288
|
Quote:
Originally Posted by Oakey
No problems here
|
No Permit- No Problem.
Seriously: who here pulls a permit for such a 'project'?
Not that I'm afraid of permits- But.... after the running around and scheduling inspections.... add 2 hrs-Real time- to the project-
You lost any and all profit.... And....
The inspector would probably be a Tadd irritated.
Messed up their lunch.......
|
|
|
|
The Following User Says Thank You to leland For This Useful Post:
|
|
02-07-2012, 08:08 PM
|
#15
|
|
Senior Member
Join Date: Dec 2009
Location: NJ
Posts: 756
|
Another one today
|
|
|
02-07-2012, 09:28 PM
|
#16
|
|
PGW Professional
Join Date: Jan 2007
Location: Rahway, NJ
Posts: 12,807
|
Looks good... but why did you put the PB30 inside the house/ garage?
I know it's rated for indoor/ outdoor use but I figured it's best to put it outside so no one would ever start the generator indoors.
What do you think?
|
|
|
02-07-2012, 09:34 PM
|
#17
|
|
Senior Member
Join Date: Dec 2009
Location: NJ
Posts: 756
|
Quote:
|
Originally Posted by Magnettica
Looks good... but why did you put the PB30 inside the house/ garage?
I know it's rated for indoor/ outdoor use but I figured it's best to put it outside so no one would ever start the generator indoors.
What do you think?
|
I had a extra so used it. As far as putting it outside this particular customer actually wanted it inside? The panel is about 3 feet from the door and explained that the reason you bought a 20 foot cord is to put gen outside.
|
|
|
02-07-2012, 09:46 PM
|
#18
|
|
Senior Member
Join Date: Dec 2009
Location: NJ
Posts: 756
|
Quote:
|
Originally Posted by Magnettica
Looks good... but why did you put the PB30 inside the house/ garage?
I know it's rated for indoor/ outdoor use but I figured it's best to put it outside so no one would ever start the generator indoors.
What do you think?
|
I also did one about a month ago that was actually in the basement. I did not have it inspected do you think it would of passed? The HO had a 40 foot cord and window close by.
|
|
|
02-07-2012, 09:48 PM
|
#19
|
|
Senior Member
Join Date: Sep 2009
Location: kentucky
Posts: 8,020
|
Quote:
Originally Posted by Gamit
That are sold on http://www.interlockkit.com/ are UL tested but not UL listed and was told by a buddy of mine that a inspector could fail them with no questions asked? Just wondering if anyone here ever had one of these installs shot down?
|
Does UL tested mean that they passed?
|
|
|
02-07-2012, 10:07 PM
|
#20
|
|
PGW Professional
Join Date: Jan 2007
Location: Rahway, NJ
Posts: 12,807
|
Quote:
Originally Posted by Gamit
I also did one about a month ago that was actually in the basement. I did not have it inspected do you think it would of passed? The HO had a 40 foot cord and window close by.
|
It should have passed. The PB30 and PNB30 are rated for indoor/outdoor use. It's in the paperwork in case you were wondering.
I saw the Cutler-Hammer CH EmGen prewired panel for the first time today. It's a lot like the Reliance brand except it's not a piece of crap like Reliance breakers are. The only thing I didn't like was the inlet built-in to the panel.
|
|
|