In a bus bar protection scheme applied for a double bus high voltage substation, protection systems design group have chosen high speed trip relay with operation time equal to 4 ms and a 2.5W DC bobbin; because they want to decrease the thermal stresses on output contacts of protection relays. As you know in high impedance bus bar protection scheme they must start several trip relays in bus bar faulty conditions simultantinusly.Therfore, dc circuit currents specially the circuits that involve to protective relays, must be considered carefully in detail design step.
But in practice they met some mal-operation of trip relay in pre-commissioning stage. According to pre-commissioning reports,
mal-operation had been accompanied with a DC battery system alarm for earth leakage.
Can you explain the reason of that mal-operation?

BEST REGARDS
MSJ




Creative thinking is enjoyable,Then think about your surrounding things and other thought products. http://electrical-riddles.com
m.s.j is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectrcianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 12-07-2007, 08:45 PM   #2
Senior Member
 
brian john's Avatar
 
Join Date: Mar 2007
Location: Leesburg VA
Posts: 5,148
Default

SWAG
I assume this is a high impedance grounded system, the fault current required to alarm a system of this type is based upon the impedance of the system and trip currents are typically in the 10-25 amp range. Arriving at this level fault current is easy with a battery.
brian john is offline   Reply With Quote
Old 12-08-2007, 12:12 PM   #3
Senior Member
 
John Valdes's Avatar
 
Join Date: May 2007
Location: South Carolina
Posts: 1,006
Default

m.s.j.
I mean no disrespect, but why are you in this forum? Are you an engineer? Physics teacher?
I have read several of your post's and never understand anything you are talking about. You seem to be very intelligent, so why here?
Respectfully......John Valdes
John Valdes is offline   Reply With Quote
Old 12-08-2007, 12:31 PM   #4
Senior Member
 
brian john's Avatar
 
Join Date: Mar 2007
Location: Leesburg VA
Posts: 5,148
Default

For a while I was avoiding his post as possibly trick. Now It does not seem to matter as he never post an answer or critique of answers.
brian john is offline   Reply With Quote
Old 12-08-2007, 12:34 PM   #5
Moderator
 
Speedy Petey's Avatar
 
Join Date: Jan 2007
Location: NY State
Posts: 2,862
Default

That's what bothers me. It seems he is trolling for something.

There are very few here that understand his posts.
Speedy Petey is offline   Reply With Quote
Old 12-08-2007, 12:39 PM   #6
Wyome
 
Join Date: Jun 2007
Location: WY
Posts: 360
Default

Quote:
Originally Posted by Speedy Petey View Post
There are very few here that understand his posts.

Thank goodness for that. I was beginning to feel like I never had a handle on electrical at all.
te12co2w is offline   Reply With Quote
Old 12-10-2007, 03:19 AM   #7
Member
 
Join Date: Jul 2007
Posts: 30
Default

According to commissioning report, even without any load current on that mentioned cable, they had measured more than 2A in secondary side of core balance CT.
Regarding to cable length, I think that problem involved to AC cable capacitance current of three phase medium voltage cables.

What is your opinion?
m.s.j is offline   Reply With Quote
Old 12-10-2007, 03:29 AM   #8
Member
 
Join Date: Jul 2007
Posts: 30
Default

Quote:
Originally Posted by John Valdes View Post
m.s.j.
I mean no disrespect, but why are you in this forum? Are you an engineer? Physics teacher?
I have read several of your post's and never understand anything you are talking about. You seem to be very intelligent, so why here?
Respectfully......John Valdes
I never asserted to know anything about electrical or non electrical subjects, I just designed many practical questions consist some deep electrical conception and tried to share our knowledge and experience for more discussion and technical dialogue.
As you know each question can be had several correct answers and there are some things for thinking in each new answer. However this activity is a mental try to share our knowledge, experience and practical information in electrical engineering. I hope you participate in this unison that has been constructed for science propagation.

I don't need to show off.
I like the beautiful minds.
My watchword is "THINKING IS ENJOYABLE THEN THINK ABOUT YOUR SURROUNDING THINGS AND OTHER THOUGHT PRODUCTS"

BEST REGARDS
MSJ
m.s.j is offline   Reply With Quote
Old 12-10-2007, 07:41 AM   #9
Moderator
 
Speedy Petey's Avatar
 
Join Date: Jan 2007
Location: NY State
Posts: 2,862
Default

Quote:
Originally Posted by m.s.j View Post
However this activity is a mental try to share our knowledge, experience and practical information in electrical engineering.
This is our point entirely. Very few of us here are EEs. We are mainly contractors and electrical related tradespeople. We all deal with electrons long after they leave the places you are talking about.
Personally, apart from a childish curiosity, I really don't care how a power generation plant works. I have far too many jobs to keep my mind occupied. Jobs that I need to know how to do, and to do well.
And this usually has nothing to do with high speed trip relays with operation time equal to 4 ms and a 2.5W DC bobbins.

If I am being rude or I am off base someone please let me know.


Last edited by Speedy Petey; 12-10-2007 at 07:43 AM.
Speedy Petey is offline   Reply With Quote
Old 12-10-2007, 08:53 AM   #10
Senior Member
 
Join Date: Oct 2007
Location: West Chester Pa.
Posts: 237
Default

I think m. s. j. has good intentions. He's trying to help us expand our knowledge. The problem is, it's to much of a leap from were we are to were he is. Like about 4 years of school, maybe more. Most of us became electricians because we weren't any good in school. We are good with our hands. If you gear your questions for maybe a first year student, then maybe we would have a chance. As it is they are so far over our heads, it might as well be Latin. On the other you might be some genius that likes to make fun of the dumb guys.
bigredc222 is offline   Reply With Quote
Old 12-10-2007, 11:53 AM   #11
Senior Member
 
brian john's Avatar
 
Join Date: Mar 2007
Location: Leesburg VA
Posts: 5,148
Default

I think the intentions are all good. Not sure if my responses are.
brian john is offline   Reply With Quote
Old 12-10-2007, 01:52 PM   #12
Senior Member
 
gilbequick's Avatar
 
Join Date: Oct 2007
Location: NC
Posts: 1,381
Default

MSJ's intentions and thoughts are good. The difference comes in where he is coming from with his electrical knowledge and understanding of how it is created and distributed and our knowledge about how it used and put to work.

I understand verrrrrrrrrrrrrrrrry little of his questions, but they do make think and I appreciate them, and I do look up some of the references.

So, I don't understand it, but thanks for making me think outside of my normal realm.
gilbequick is offline   Reply With Quote
Old 12-10-2007, 08:18 PM   #13
Senior Member
 
brian john's Avatar
 
Join Date: Mar 2007
Location: Leesburg VA
Posts: 5,148
Default

Assuming my responses are close? I can answer some questions you may have regarding high resistance ground systems.
brian john is offline   Reply With Quote
Old 12-11-2007, 02:50 AM   #14
Member
 
Join Date: Jul 2007
Posts: 30
Default

Please excuse me. I always like dialogue especially with good peoples similar you.

I will never annoy you in future.


BEST REGARDS
MSJ
m.s.j is offline   Reply With Quote
Old 12-11-2007, 08:21 AM   #15
Senior Member
 
Join Date: Oct 2007
Location: West Chester Pa.
Posts: 237
Default

It just occurred to me that English isn't his first language. That may be part of the problem. I still wouldn't have any idea what he's talking about. I think he should keep posting is questions. I feel bad now.
bigredc222 is offline   Reply With Quote
Old 12-11-2007, 10:36 AM   #16
Member
 
Join Date: Nov 2007
Location: AZ
Posts: 41
Default

Quote:
Originally Posted by m.s.j View Post
According to commissioning report, even without any load current on that mentioned cable, they had measured more than 2A in secondary side of core balance CT.
Regarding to cable length, I think that problem involved to AC cable capacitance current of three phase medium voltage cables.

What is your opinion?
This is true MSJ, the power company often does what we call "bleeding down the line" or removing the power that is stored in the cable.
DBack Elec is offline   Reply With Quote
Old 12-11-2007, 03:24 PM   #17
Moderator
 
Speedy Petey's Avatar
 
Join Date: Jan 2007
Location: NY State
Posts: 2,862
Default

Quote:
Originally Posted by m.s.j View Post
Please excuse me. I always like dialogue especially with good peoples similar you.
It's not a matter of annoy. It's that everything you post is out of our scope of work, education, experience, etc. Well, most of us at least.

Keep posting, just maybe you can bring it down to our level a bit?
Speedy Petey is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Solid State Relay simmo General Electrical Discussion 9 09-15-2008 01:30 PM
Risk of operation in power plant m.s.j General Electrical Discussion 6 12-02-2007 10:30 AM
The protection system false operation m.s.j General Electrical Discussion 3 10-28-2007 05:48 AM
Car Headlight Relay:- How do I? tunners UK Electrical Forum 2 10-18-2007 01:30 PM

Top of Page | View New Posts

All times are GMT -4. The time now is 10:29 PM.


Electrician Talk © 2006 - 2009 The Building Network LLC

Search Engine Optimization by vBSEO 3.2.0