Old 05-11-2012, 02:29 PM   #1
Default Type MC cable I am being told
Type MC an MC lite I'm being told doesn't need a anti short bushing (red head) if this is true tell me where it states it in the NEC. If its required please direct me towards it. I never heard of such a thing but I'm being told through conversation with an electrical inspector it's not required with this type of cable. Any feedback will be a great help. Thanks
mdny is offline   Reply With Quote
Old 05-11-2012, 02:32 PM   #2
I believe this is true and have been told this multiple times but use them regardless
Gamit is offline   Reply With Quote
Old 05-11-2012, 02:33 PM   #3
animal lover /rat bastard
wildleg's Avatar
it's true. bushing is needed with AC cable, but not MC. do a search here or on MH and you'll find the reference, I think it's the listing of the cable but I forget. (we use them regardless too - I think it's best practice)
chicken steve (05-12-2012)
Old 05-11-2012, 02:34 PM   #4
It's not going to be an NEC issue. Refer to the maufacturers installation instructions and you will find your answer (not required).
Old 05-11-2012, 02:52 PM   #5
Heavily Armed Member
HARRY304E's Avatar
Read 320. 40 for type AC CABLE.."BX"
Them read 330.40 type Mc cable...not required.
Old 05-11-2012, 02:53 PM   #6
Here an anti-short bushing is always a required item in current installations. Chicago code also requires a grounding wire (bare) for any BX or equivalent. The bare wire can be wrapped around the BX end ,securing the anti short bushing by wrapping it around it and then secured by the screw in the BX connector.
cortez is offline   Reply With Quote
Old 05-11-2012, 04:02 PM   #7
Good at being Evil
Shockdoc's Avatar
But they give you a small care package of red heads with every roll, enough to wire up about 7 feed thru boxes.
Old 05-11-2012, 09:38 PM   #8
Mad Skills
Celtic's Avatar
The requirement for Type AC cable is 320.40
This requirement is absent in 330.40
This difference can also be seen in NEMA Bulletin 90:
Use of Anti-Short Bushings for Terminating Type MC Cable
While use of an anti-short is NOT a requirement, however it is good practice to install one.
póg mo thóin
The Following User Says Thank You to Celtic For This Useful Post:
GEORGE D (05-12-2012)
Old 05-11-2012, 11:57 PM   #9
If you do alot of HR's you will end up have extra on hand and the other hand from time to time I get a box full of antishorting bushing as well.
Right now one of my tool box which I store the antishorting bushing it kinda overflow at the moment
Merci,
Marc
Old 05-12-2012, 12:02 AM   #10
HARRY304E's Avatar
Merci,
Marc
You should open a Anti-short bushing store you will be rich..
frenchelectrican (05-12-2012)
Old 05-12-2012, 12:05 AM   #11
Truth is it took years before most inspectors learned that they are not required for mc cable. I used to tell em that and they treated me like I was crazy, even though I was spot on right about it. Now that I think about it , its just like how you guys treat me too...................
Proof and exoneration http://www.latimes.com/news/politics...,7305052.story
Old 05-12-2012, 12:06 AM   #12
Kinda but BTW the Americian MC cable and European MC cable are the same size but slightly differnt rating plus metric conductor that it but both look the same.
Merci,
Marc
HARRY304E (05-12-2012)
Old 05-12-2012, 12:09 AM   #13
HARRY304E's Avatar
OH!
We never do that here........................ ........
Old 05-12-2012, 07:30 AM   #14
chicken steve's Avatar
heaven forfend Mac....~CS~
Old 05-12-2012, 07:34 AM   #15
kennydmeek's Avatar
I think I'd lay awake the rest of my life if I installed something without one...
kennydmeek is offline   Reply With Quote
The Following User Says Thank You to kennydmeek For This Useful Post:
FranklinsApprentice (05-12-2012)
Old 05-12-2012, 07:40 AM   #16
BBQ
BBQ's Avatar
98% of the time I use them, if I don't have one handy I may leave it out and sleep fine.
Here is the NEMA bulletin about it.
http://www.nema.org/stds/eng-bulleti...ulletin-90.pdf
BULLETIN
No. 90
August 14, 2002
There has been much confusion within the Installation and Inspection communities regarding the
use of anti-short bushings for terminating Type MC cable. The confusion stems from the fact
that some MC cable manufacturers include anti-short bushings with their cable. The inclusion of
anti-short bushings with coils or reels of MC cable is based on historical practice relating to the
requirements of 320.40 of the NEC, which mandates the use of anti-short bushing or its
equivalent protection for Type AC Cable
Fittings used with Type MC Cable are required to be listed per 330.40 of the NEC. NEMA
supports the use of listed fittings for MC Cable. The design of these fittings may or may not
include an insulated throat however, they are required to be provided with a smooth, rounded end
stop so that the metal sheath of the cable will not pass through and the wires will not be damaged
in passing over the end stop. Whether or not an insulated throat is part of the listed product, these
listed MC fittings do not require an additional anti-short bushing. Anti-short bushings that may
be supplied by MC Cable manufacturers are for optional use by the installer, however they are
not required.
ROP #7-116 from the May 2001 Report on Proposals (ROP) for the 2002 NEC was a proposal
seeking to require anti-short bushings on all MC Cable termination installations.
The following is an excerpt from the Panel statement rejecting the proposal:
Anti-short bushings are not required for Type MC cable in accordance with the listing for
the product. The termination fittings approved for use with Type MC cables are designed
such that the wires will not come in contact with the cut edge of the armor; the throat of
the fitting is small enough to prevent contact with the armor. Type MC termination
fittings perform the same function for Type MC cable as Type AC terminations plus the
anti-short bushing do for Type AC cable.
NEMA supports the uniform adoption and enforcement of the NEC and recommends that local
Authorities Having Jurisdiction follow the requirements of NEC Section 330.40, Boxes and
Fittings for MC Cable. Section 330.40 requires that the fitting be listed, but does not mandate the
use of an anti-short bushing.
Distribution List:
Standards and Conformity Assessment Policy Committee
Codes and Standards Committee
NEMA Executive Staff
Old 05-12-2012, 07:46 AM   #17
Are you talking about the bond strip inside AC cable? This is NOT a ground.
The Following User Says Thank You to Speedy Petey For This Useful Post:
Salvatoreg02 (05-12-2012)
Old 05-12-2012, 09:11 AM   #18
wildleg's Avatar
where is that in the Chicago code ?
Old 05-12-2012, 10:07 AM   #19
And it can be cut off. I don't do the backwrap trick with AC cable, not that I encounter it often.
Old 05-12-2012, 10:08 AM   #20
BBQ
BBQ's Avatar
type use2 or rhw cable socalelect General Electrical Discussion 5 04-29-2012 02:46 PM
Type MC Cable Gamit General Electrical Discussion 6 06-28-2011 09:24 PM
Type of cable Englishsparky General Electrical Discussion 4 01-07-2011 01:54 PM
Type mc cable jwjrw General Electrical Discussion 19 05-12-2010 12:23 PM
What type of cable? username General Electrical Discussion 6 12-11-2009 09:15 PM