Underground conduits / duct seal - Electrician Talk - Professional Electrical Contractors Forum
Old 12-16-2010, 09:18 PM   #1
Ambassador of Amps
TOOL_5150's Avatar
Rewards Points: 2,190
Default Underground conduits / duct seal
Had an inspector say today "Id like to see that underground conduit sealed with duct seal" I just kind of noddded and was going to see if she was going to put it on the permit to be done before final. She didn't so I didnt have to fight it, but it got me wondering: Is it required anywhere in the NEC, other than classified locations, to seal underground conduits?
~Matt
TOOL_5150 is online now   Reply With Quote
Old 12-16-2010, 09:23 PM   #2
Rewards Points: 2,012
~Matt
Will be Next month. 2011
The Following User Says Thank You to leland For This Useful Post:
erics37 (12-17-2010)
Old 12-16-2010, 09:24 PM   #3
Ambassador of Amps
TOOL_5150's Avatar
got a ref? California is just going to 2008 jan1
~Matt
Old 12-17-2010, 12:48 PM   #4
Professional Nit Picker
manchestersparky's Avatar
Rewards Points: 1,640
before giving an answer, we need to know what the conduits were terminated to, and where they were run and so forth.
Look into article 300.5 (B) and then 300.5(4)(G) in the 2008 NEC.
300.5(B) tells you that a conduit under ground is a wet location.
300.5(4)(G) tells you to plug the end(s) of conduits if the conduit can introduce moisture to live parts.
Old 12-17-2010, 01:05 PM   #5
Ax grinder
raider1's Avatar
Rewards Points: 1,080
~Matt
Check out 225.27 in the 2011 NEC.
225.27 Raceway Seal.
Where a raceway enters a building
or structure from an underground distribution system, it
shall be sealed in accordance with 300.5(G). Spare or unused
raceways shall also be sealed. Sealants shall be identified
for use with the cable insulation, shield, or other
components.
Also this has been required for services for awhile.
Check out 230.8.
Chris
The Following User Says Thank You to raider1 For This Useful Post:
leland (12-18-2010)
Old 12-17-2010, 05:48 PM   #6
Podagrower's Avatar
Rewards Points: 568
Well, while we are talking about it...
I've always (mostly) sealed conduits that exited the building, service entrance, exterior lighting, AC compressors, etc. I did a job last year where the inspector said all the conduits under the slab left the building, so they all needed to be sealed. It wasn't worth arguing (maybe 30 1" homeruns), so I just did it.
So, do the pipes under the slab leave the building? Or is everything inside the footer inside the building?
Podagrower is offline   Reply With Quote
Old 12-17-2010, 10:51 PM   #7
Ambassador of Amps
TOOL_5150's Avatar
The conduit went from a bell box on a detached structure, underground, then back up into the bottom of a 10x10 3R that was on the house. There was no way water would leak into either of the boxes.
~Matt
Old 12-17-2010, 10:52 PM   #8
Ambassador of Amps
TOOL_5150's Avatar
Check out 230.8.
Chris
[/SIZE][/FONT][/SIZE][/FONT]
EVen under 2011, this would not apply - its not an underground distribution system.
~Matt
Old 12-18-2010, 12:06 AM   #9
~Matt
Now that you expanded this... No need to seal.
Old 12-18-2010, 05:37 AM   #10
Semper Fidelis
Suncoast Power's Avatar
Rewards Points: 4,876
For some reason, we put ductseal on conduits ONLY for underground services.
I usually put duct seal in conduits that come inside from generators. An air exchange sometimes develops when the unit comes on.
Old 12-21-2010, 10:39 PM   #11
Rewards Points: 2,791
AHJ. I did a power gen. plant a few years back, and all u/g vault conduits had to be sealed because of the rats. They'd use the 4"'s for a drive thru dinner. They can digest THHN/THWN, and SIS, but not duct seal.
Old 12-21-2010, 10:43 PM   #12
I have seen water fill up storage rooms because they where not sealed. Below the water table.
one2question is offline   Reply With Quote
Old 12-21-2010, 10:45 PM   #13
B4T
Scotchkote Installer
B4T's Avatar
Rewards Points: 15,378
Goose poop would do a better job of keeping water out of conduits..
There are millions of compression water tight connectors on services that rely on duct seal to keep the water out.
We all know how good that is working, but it does generate some nice dollars..
Old 12-21-2010, 10:51 PM   #14
Would Scotchkote do a better job?
Peter-D is offline   Reply With Quote
Old 12-21-2010, 11:14 PM   #15
Coaster Sparky
thegoldenboy's Avatar
Rewards Points: 1,000
We do a lot of traffic intersections for the company I work for. It's usually 3" Sch. 80 underground with concrete handholes every 150' or thereabouts and after we pull the wire in we go behind and put a duct seal patty over the ends of the pipe in the handholes. I've only personally done it once but the traffic foreman told me it was more of a state requirement than a NEC requirement.
The job I was on this summer, I think we used spray foam and duct seal when the lateral came into the CT cabinet. I didn't work on it myself but I'm pretty sure what that's what the guy used to seal it up.
I saw a girl texting & driving the other day & it really made me mad, so I rolled down my window & threw my beer at her.
thegoldenboy is offline   Reply With Quote
Old 12-22-2010, 12:35 AM   #16
Rewards Points: 4,422
Duct seal looks pretty. Expanding foam works better. Take your pick.
It would have been impossible for us to develop our plan for the world if we had been subject to the bright lights of publicity during those years. David Rockefeller
Red Seal? petek57 General Electrical Discussion 37 12-29-2010 11:08 PM
Duct Seal at Weatherhead doubleoh7 General Electrical Discussion 24 11-28-2010 01:25 PM
Just needs a little duct seal electricmanscott General Electrical Discussion 38 05-21-2010 07:43 AM
Old Meter Seal crazymurph Vintage Electrical 2 04-18-2010 12:32 PM
Frozen Underground Conduits JAB General Electrical Discussion 13 02-02-2010 09:45 PM