Playing with the Southwire Calculator linked by somebody here, it still won't perform calculations for 4/0 Al at 200 amps or 1/0 Al at 200 amps, saying only that 4/0 and 1/0 can't carry 200 amps. Of course, they both CAN carry 200 amps.

I wonder what I'm missing or are there all sorts of such "sources" out there that misinform us or are we the victims of our own assumptions?
waco is offline   Reply With Quote
Join Contractor Talk

Join the #1 Electrician Forum Today - It's Totally Free!

ElectricianTalk.com - Are you a Professional Electrical Contractor? If so we invite you to join our community and see what it has to offer. Our site is specifically designed for you and it's the leading place for electricians to meet online. No homeowners asking DIY questions. Just fellow tradesmen who enjoy talking about their business, their trade, and anything else that comes up. No matter what your specialty is you'll find that ElectricianTalk.com is a great community to join. Best of all it's totally free!

Join ElectricianTalk.com - Click Here JOIN FOR FREE


Warning: The topics covered on this site include activities in which there exists the potential for serious injury or death. ElectrcianTalk.com DOES NOT guarantee the accuracy or completeness of any information contained on this site. Always use proper safety precaution and reference reliable outside sources before attempting any construction or remodeling task!
Old 06-29-2009, 12:38 PM   #2
Senior Member
 
Join Date: Feb 2008
Location: Atlanta, Ga/Hamilton, Al
Posts: 2,035
Default

Quote:
Originally Posted by waco View Post
Playing with the Southwire Calculator linked by somebody here, it still won't perform calculations for 4/0 Al at 200 amps or 1/0 Al at 200 amps, saying only that 4/0 and 1/0 can't carry 200 amps. Of course, they both CAN carry 200 amps.

I wonder what I'm missing or are there all sorts of such "sources" out there that misinform us or are we the victims of our own assumptions?
In an NEC compliant installation, 4/0 aluminum cannot be used for 200 A, except in the case of a residential service. A 200 A feeder using aluminum would be required, by T310.16, to be at least 250 kcmil.
InPhase277 is offline   Reply With Quote
Old 06-29-2009, 12:50 PM   #3
Senior Member
 
drsparky's Avatar
 
Join Date: Nov 2008
Location: Presque Isle, Maine
Posts: 2,244
Default

Read 310.15 (B) (6) and table 310-16.
__________________
"Whatever is felt is within suffering."
drsparky is online now   Reply With Quote
Old 06-29-2009, 12:57 PM   #4
Senior Member
 
Join Date: Dec 2007
Posts: 1,795
Default

Quote:
Originally Posted by InPhase277 View Post
In an NEC compliant installation, 4/0 aluminum cannot be used for 200 A, except in the case of a residential service. A 200 A feeder using aluminum would be required, by T310.16, to be at least 250 kcmil.
Of course, you are right, "except in the case of residential service" which is a reality and in the case of the wire simply "carrying" 200 amps regardless of code.

Here is another calculator which seems more realistic: http://www.electrical-designer-guide...wire-size.html
waco is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
voltage drop for sub panel roach1521 General Electrical Discussion 14 07-02-2009 10:34 PM
Voltage Drop Absolutetruthz General Electrical Discussion 22 04-01-2009 03:49 PM
Voltage Drop john salyards General Electrical Discussion 3 02-17-2008 04:43 PM
Voltage Drop brian john General Electrical Discussion 7 09-04-2007 06:26 AM
Voltage drop K&R NEC Code Forum 12 04-30-2007 10:33 PM

Top of Page | View New Posts

All times are GMT -4. The time now is 06:00 PM.


Electrician Talk © 2006 - 2009 The Building Network LLC

Search Engine Optimization by vBSEO 3.2.0