A couple questions:
1. Is the preliminary amp check of each phase to verify a balanced load, or is it to possibly ferret out the problem leg without having to do the millivolt test?
The amp check is to verify load, even without a balanced load one can do the millivolt drop check, but you need a load.
2.Is there any reason to do the millivolt check on a regular volts scale first, in the event that one fuse might be blown (in the case of fuses)?
With a high impedance meter this should not be an issue the meter should read OL or some variance of that.
3. Are the little knobs that companies like Ideal and Bussman make that clamp fuse holder sockets tighter onto fuse blades and ferrules to be considered a permanent repair, ever?
We use these on a temporary basis, not sure about a full time repair, but then selling a FSS is always a plus.
[/quote]