Wiring up a double wide. - Electrician Talk - Professional Electrical Contractors Forum
Old 04-17-2010, 08:55 AM   #1
Rewards Points: 2,050
Default Wiring up a double wide.
I was sent to Arlington VA to wire up a job trailer.
It was a double wide office trailer 24' x 62'
Got to love how the trailer rental company conects the units together.
Old 04-17-2010, 09:01 AM   #2
Fried Bologna um um good!
jwjrw's Avatar
Someone knew what they were doing....I see a red head under that black tape
Old 04-17-2010, 09:35 AM   #3
william1978's Avatar
Rewards Points: 2,000
I have wired many office trailers in the past and have never seen anything like that under them. The last one I wired was a 5 trailers put together and each trailer was fed with 100amps.
Old 04-17-2010, 09:38 AM   #4
jwjrw's Avatar
I did 8 trailers for Duke Power. They used them for training the substation operators. All had 100a services on them also.
Old 04-17-2010, 09:47 AM   #5
I have done tons of job trailers, all have had 100 to 125 amp feeders to them and I have not seen jumpers between them either.
Both of these trailers have 100 amp feeders, I have no idea what they are really connecting together with this MC.
Before anyone mentions the NEC I should point out it does not apply at this location. This areas AHJ is fine with SER.
Old 04-17-2010, 09:51 AM   #6
Side questions.
When you others wire these units;
1) Do you install grounding electrodes?
2) If yes how many?
3) How do you get around 225.30 'number of supplies'?
Old 04-17-2010, 10:05 AM   #7
Where abouts was this job?
Old 04-17-2010, 10:09 AM   #8
Originally Posted by Bob Badger View Post
Side questions.
2) If yes how many?
I have only installed 2 ground rods at the sefvice, and as far as number of supplies I have never been questioned on it. I do bond each section together with #4.
Old 04-17-2010, 10:17 AM   #9
Originally Posted by william1978 View Post
I have only installed 2 ground rods at the service,
250.32(A) requires grounding electrode(s) at this separate structure.
I drove two rods and connected the two sections to both rods.
Neither have I but it seems 225.30 is being violated.
In this case I accomplished that with the GEC but with more sections I would jump the other sections together with 4 AWG as well.
Old 04-17-2010, 10:23 AM   #10
That is sorta what I did also. I came out of the meter down to both rods, and then up to the frame of the trailers.
Around here we use #4 for just about everything that is 200a or less.
The Following User Says Thank You to william1978 For This Useful Post:
jwjrw (04-17-2010)
Old 04-17-2010, 10:56 AM   #11
Rewards Points: 524
Why would number of supplies come into it? I am assuming there is one main supply service and these two sub panels, or more panels even.
Jeff000 is offline   Reply With Quote
Old 04-17-2010, 11:16 AM   #12
Because the NEC prohibits more than one feeder to a structure unless if fits one of many conditions, none of which seem to apply to this job.
II. More Than One Building or Other Structure
225.30 Number of Supplies.
Where more than one building or other structure is on the same property and under single management, each additional building or other structure that is served by a branch circuit or feeder on the load side of the service disconnecting means shall be supplied by only one feeder or branch circuit unless permitted in 225.30(A) through (E). For the purpose of this section, a multiwire branch circuit shall be considered a single circuit.
In my opinion none of the items in (A) through (E) apply so we are limited to one feeder.
Old 04-17-2010, 12:29 PM   #13
Rewards Points: 3,855
Maybe they're calling it two structures, but you can just coincidently walk between them? Fire doors with closers in the demising wall??
It just seems like job trailers aren't inspected too hard. Around here, they look for a couple rods and #8 to the frame(s), and that's about it.
Old 04-17-2010, 01:27 PM   #14
Rewards Points: 524
Branch circuit....
Does the NEC have a section for Factory built relocatable structures? The CEC outlines trailers as pictured in section 70. I don't have my code book here so not even sure if that section covers said predicament, but would think it would.
By that token they are manufactured so could be a piece of equipment rather then a building?
I can't really see the two trailers as being classed two buildings either, the whole firewall and doors thing.
Old 04-17-2010, 01:35 PM   #15
jwjrw's Avatar
I did them at East Coast Trailer. Now that I think about it 2 were for substation training. We had to manufacture a solenoid to trip the remote start for the generator on those.
The other 6 were construction trailers. I was told 1 was going to Puerto Rico.
Old 04-17-2010, 11:40 PM   #16
Bob,
IMO, A double wide is one structure that happens to get delivered in more
than one section. Of course, one service disconnect would be required.
Frank, Arizona,USA
It's what you learn after you know it all that counts
Benaround is offline   Reply With Quote
Old 04-17-2010, 11:53 PM   #17
Rewards Points: 2,012
Sad ,No Doubt!- but reality all over.
Wide format printers Dnkldorf Business, Marketing, and Sales 9 04-10-2010 03:13 PM
Post too wide bobelectric Site Help and Suggestions 1 03-18-2010 07:56 AM
Double Tap Mike Lamb General Electrical Discussion 13 08-25-2009 06:17 PM
Double Pole Breaker windrider General Electrical Discussion 2 08-06-2009 06:37 PM
Generator - Double Delta? LightGuy48 General Electrical Discussion 3 10-22-2007 10:42 AM